Reading: DP Flow Transmitter Re-Ranging Calculation
Inst Tools > Blog > Flow Measurement > DP Flow Transmitter Re-Ranging Calculation
DP Flow Transmitter Re-Ranging Calculation is used to find the DP Flow transmitter revised flow with Existing DP, Existing Flow & New DP.
Last updated: October 31, 2023 10:51 am
Flow Measurement Instrumentation Tools
16 Comments
2 Min Read
DP Flow Transmitter Re-Range: This tool is used to calculate the DP Flow transmitter revised flow with the following inputs: Existing DP, Existing Flow, and revised DP.
This tool is primarily used for orifice-based flow meters. Also useful for flow transmitters that work on Differential Pressure applications.
Generally, we calibrate our transmitter as per the datasheet of the orifice. But sometimes the measured DP of the transmitter will be out of range or more than the maximum scale of DP, so we have to re-range the DP flow transmitter.
For these applications, we use the below-mentioned formula to calculate the maximum flow of the transmitter.
This calculation tool is used to calculate the revised flow range of a DP Flow transmitter.
The formula for calculating the DP Flow Transmitter Re-Range value.
DP Flow Transmitter Re-Ranging calculation Formula
Where,
Existing DP    = DP value as per orifice datasheet
Existing Flow  =  Flow value as per orifice datasheet
Revised DP    =  Actual DP value in the field
Revised Flow  =  Calculated transmitter flow max range.
Note:
1. The Existing DP and revised DP must be in the same units like bar, mbar, mmh20, etc.
2. The Existing Flow and revised Flow must be in the same units like m3/hr, t/hr, etc.
Also See: Instrumentation Calculator
  • What is a Pitot Tube?
  • Pitot Tube Working Principle
  • Different Types of Flow Elements
  • Annubar Flow Meter Principle
  • Types of Flow Meters
Prover Tank Calibration and Mass Flow Meter Verification Procedure
Basics of Flow Measurement
Multiphase Flow Meter Calibration Procedure
Mass Flow Calculations
Level Measurement with Wet leg and Installed Below Tapping Point
What is a Paddle Wheel Flow Meter?
16 Comments
  • Jitin D says:
    April 21, 2015 at 11:04 am
    I am instrument guy and i am very rarely found tools related to instrumentation. I am very happy to see these type of tools. Please update more with complex calculations like density measurement, Interface measurement, USM flow calculations etc.
  • Rambai says:
    April 26, 2015 at 6:31 pm
    I Just loved your site dude :love:
  • rahim says:
    November 29, 2015 at 7:32 pm
    Hi. We have a flowmeters with instrument range 0 to 500 mbar and calib. Range 0 to 250 mbar for normal flow =10000kg/h but we need 10311 kg/h so we have to recalibrate it .please help me how i do it .i mean 0~250mbar should change to 0~? Many thanks
    • rahim1356 says:
      December 1, 2015 at 5:08 am
      You should just change your scale !
      Reading dp flow ,so long as your devices within the capability of the pressure device , everything is ok.
      For mentioned ranges above is your remedy but for large differences you need to know your device limitation.
  • ravi singh says:
    November 30, 2015 at 12:05 pm
    dear sir
    i have one orifice plate concentric type and id is 25 mm.but i do not calculate Dp range please guide in LRV & URV range. how to calculate……….
  • rahim1356 says:
    December 1, 2015 at 5:02 am
    Be careful this is for 4~20 ma not for fieldbus .
    • S Bharadwaj Reddy says:
      December 1, 2015 at 6:52 am
      Dear Rahim, Thank you for the suggestions.
    • Hadi says:
      November 20, 2017 at 5:00 am
      What’s the right way to re-range DP fieldbus “FF” transmitter?
  • Raju says:
    December 23, 2015 at 5:32 am
    Sir,
    I Need Suggestion on Flow. Orifice D/P To Connected DP Transmitter With Sq.root Op.
    Indicator also Need Sq.root Input or Linier In put.
    Pls Explain sir.
    Regards
    Raju
  • GANDHI says:
    May 16, 2016 at 5:41 am
    What is the minimum static working pressure
  • Suresh badiger says:
    January 1, 2017 at 1:22 pm
    Sir I’m instrumentation Engg I have do transmitter in condensate water line as per data sheet 1500 mmwc I puted urv range in transmitter but I’m not getting full flow as per pump discharge 110 m/3 hr only I’m getting 49 m3/hr so please suggest
  • jdp says:
    June 3, 2019 at 11:39 am
    if we re range the value… does the square root graph also change ?
  • Saddam hussain says:
    March 5, 2020 at 8:04 pm
    Respected sir,
    Pls give me solution. How to we calculate nm3/hr flow for different case. Like air, gas. Please give one note with example.
  • Le Huy Dat says:
    July 16, 2021 at 11:16 pm
    you can to chang for calibration range from 0 to 265 MPA with enering range from 0 to 10311.
  • Cyrus says:
    June 19, 2022 at 8:02 pm
    Good day to all.
    I hope any one can help me elighten about Flow Transmitters. Why is it Flow transmitter has 2 ranges? Example process variable range from 0 to 2500 mmH2O and the other range (engineering range) is 0 to 160 t/h.
  • GP says:
    August 21, 2024 at 4:32 pm
    We are plaining in-house calibration flow meters. would you please give me simple technique. How to set up and calibration step by step.
Swirl Flow Meters Working Principle
DP type Flow Transmitter Preventive Maintenance and Calibration
Hot Wire Anemometer Principle and Types
Basic Working Principle of Vortex Flowmeter
Thermal Mass Flow Meter – Principle, Advantages, Applications
Transit Time Flow Meter Principle
Transmitter Current Conversion Tool
How does an Orifice Measures Flow?
Coriolis mass flowmeter Density Measurement
How Coriolis Mass Flow Meter Measure Density?
Comparison of Venturi and Orifice flow meterComparison of Venturi and Orifice flow meter
Flow Element Symbol
What is a Flow Element? – Types, Comparison of Flow Elements
Bernoulli's Principle and Flow Meters
Oval Gear Flow Meter Principle
Oval Gear Flow Meters – Principle, Advantages, Animation
Target Meter Principle
Target Flow Meter – Working Principle, Advantages, Disadvantages
Servo Operated Electro Magnetic Flowmeter Objective Questions
Electro-Magnetic Flow meter Objective Questions
Namur Digital Input Card
What is Namur Digital Input Card?
Pressure Gauge Datasheet Preparation
How to Prepare Pressure Gauge Datasheet ?
Piping Schematic for Two Solenoid Valves Double Acting
Different Types of Control Valve Actuators
Synchronous Machines Power Factor Control Questions
Control valve positioner calculation
Calculate Control Valve Stem Position
How to Solve Cable Tray Sagging
How to Solve Cable Tray Sagging ?
gas chromatograph principle
Online Gas Chromatograph Principle
DCS Quiz
DCS Quiz