In this post, we will cover the basic topics on how to follow standard earthing practices used for a PLC control panel.
We all are familiar with the term earthing in an electrical circuit. Our day-to-day life involves the use of electrical equipments around us and every such equipment has the facility of earthing in it.
In the world of industrial automation, the PLC control panel that we use has the feature of earthing provided in it.
So, here, we will understand what the exact meaning of earthing is and how it must be properly implemented in a PLC control panel.
Every equipment used in a control panel (low power or high power) generates some electrical leakage current or noise during operation.
When it interferes with other equipments around it, it causes abrupt operation and creates disturbances in the circuit. They do not provide the required output & pose threats of electric shocks during fault conditions.
During such conditions, a very high current flows through the circuit and there are chances that it will not flow to it’s designated path, but instead flow through metallic body of machines or panels.
When any person comes in contact with this path, he will be prone to electrical shock. These leakage currents thus pose a threat to the nearby environment. So, it is necessary to divert these currents to some other path. This is done by earthing.
Earthing is the means of passing electrical energy directly to the earth (earth pit) with the help of some non-current carrying part of the equipment or connecting neutral of the supply system to ground.
The leakage or fault current passes to the earth which has zero potential. This nullifies it’s action and protects the nearby environment from damage.
Earthing is checked by measuring the value of ground resistance. It should ideally be between 0-5 ohms. This resistance must be measured periodically to maintain a safe surrounding.
Now, let us focus on the types of earthing and practices generally used for PLC control panel. Look at the below image.
Ideally, let us consider that there are three components in the panel – PLC, SMPS and VFD. The green lines indicate earthing lines. Each equipment has it’s earthing point incorporated in it.
A wire is routed from those corresponding points to the earthing busbar (shown in a green rectangle).
Types of Earthing
There are three types of earthing done in the control/instrumentation panel:
- Safety Earth / Electrical Earth / Power Earth
- Instrument Earth / Electronic Earth
- Intrinsic Safety Earth for IS circuit.
![Proper Earthing Practices Used for PLC Control Panel](https://instrumentationtools.com/wp-content/uploads/2021/04/Proper-Earthing-Practices-Used-for-PLC-Control-Panel.png)
Electrical Earthing
Power Earthing (also called electrical earthing) is provided to devices that are of high power and generate a large amount of leakage current. Here, the VFD has been given power earthing. The cable used is of a larger size.
The panel body has also been given power earthing by touching a point from the body to the busbar. The panel body is given electrical earthing as all the equipment is attached to it and chances are also that the noise from main incomer power supply will also flow through it.
Instrument Earthing
Instrument Earthing is provided to devices that are of low power and generate a low amount of leakage current. Here, the PLC and SMPS have been given instrument earthing. The cable used is of a smaller size.
Intrinsic Safety Earthing
Intrinsic Safety (IS) Earthing is used for intrinsic safe devices. They are devices that generate a certain amount of thermal and electrical energy which can cause fire or explosion in hazardous areas.
Now, it is to be remembered that all the different earth busbars inside the panel must be isolated from each other and there should not be any connection between them.
This will ensure proper routing of leakage current to its designated earth pits; and thus ensuring a safe working environment. The final conducting cables from the corresponding busbars should be routed to the corresponding earth pits.
Good Practices of Earthing
There are some important points to remember for a good practice.
- Earth is basically zero potential. But due to neutral connection (from main incomer supply), a small amount of earth to neutral voltage is present. It must not exceed more than 2V. A larger voltage than this indicates that the earthing provided to the panel is not proper and must be rectified at the pit end, along with proper tracing of all the earthing cables from individual control panels and whether they are routed properly or not.
- An automation panel will obviously have analog / digital instruments and field wiring. They generally use single pair / multi-pair cables with shields. The shield part is to be cut and connected with the earth.
- Ensure continuity of all the earth cables up to the earth busbar and then up to earth pits.
- All the field instruments body should also be properly earthed.
- Avoid the formation of the ground loop inside the electrical panel as ground loop current will have an effect on the performance of field instruments.
- Proper designing of busbars along with a proper selection of cables used for earthing is the main criteria for a safe environment.
Author: Viral Nagda
HI
can we connect Armor of IS cables to the electrical earth.
THKS FOR YOUR REPLY
No, You must have separate earth for IS cables.