Reading: PLC Configuration of Profinet I/O System
Inst Tools > Blog > PLC Tutorials > PLC Configuration of Profinet I/O System
Last updated: March 4, 2021 2:45 pm
3 Min Read
Write the procedure for the Profinet PLC Configuration of the I/O system. Configure the hardware system for the profinet system.
Profinet PLC ConfigurationConfiguration:-
In this example, we will configure the profinet system on profinet master PLC. Here we consider CPU 416-3 PN/DP as a profinet master system. Profinet IM module can be configured on the profinet master bus.
All profinet devices use TCP/IP protocol so they need an IP address when operated on Ethernet. The IP address generally created by the software and assigned to the I/O devices.
The IP address of all I/O devices has the same subnet mask. For example purpose, we configured here one master system and two profinet I/O system.
Configuration:-
First, select the hardware system by right-clicking on the window as shown in the figure.
Click on SIMATIC 400 station from the list.
SIMATIC 400 station
After selecting the station take CPU 416-3 PN/DP from the hardware catalog for the profinet master system.
Once the hardware is created, add a profinet master bus on the PLC.
Add profinet IO system by clicking right click on PN-IO as shown in figure 3.
Profinet master system is created as shown in figure 4, When PN-IO is clicked.
Profinet PN IO
Select IM151-3 PN from the hardware catalog as shown in figure 5.
SIMATIC Hardware Catalogue
Drag and drop the IM module from the hardware catalog on the profinet IO master bus as shown in figure 6.
SIMATIC IO Master Bus
As shown in the figure we can add more IM modules on the bus.
IM module in Simatic Software
The IP address can be changed from the following configuration window.
Click on the IM module to change or see the IP address.
IP Address Change in Simatic
Note:- This example is only for explanation purposes only. This is the simple profinet IO system configuration, we can use this concept in other examples also.
Author: Bhavesh
Networking Interview Questions
SCADA Functions & Tools
Modbus Working Principle
HART Protocol Operation
PLC Hardware Configuration
PLC System Site Acceptance Test (SAT)
Comparator in PLC Programming
Site Commissioning Steps for PLC Programmers
How to Save a PLC Project to a Micro Memory Card?
Safety PLC Coding Practices – Programming Recommendations
  • ummed singh chouhan says:
    September 26, 2019 at 8:55 am
    sir, if you have GE PLC example please send me how to assign profinet configuration .
System Cabinet Health Checks – PLC and DCS Industrial Automation
Playground Swing Logic Exercise Program in PLC
Types of Interlocks
Yokogawa DCS and SIS System Architecture
CRA Module in Schneider PLC – Remote IO Adapter Module
Ladder Logic Example of Two Motors Interlinked with another Motor
Search tank in Intouch Scada
Tank Filling and Emptying using Intouch Scada Script
How a PLC communicates with Transmitters
How PLC Reads the Data from Field Transmitters
PLC datasheet
How to Read the PLC Datasheet? – Important Notes About PLC
Omron PLC increment and decrement
Increment & Decrement Instructions in CX-Programmer (OMRON)
How Engineers Effectively do Problem-solve and Troubleshoot
SCADA Interview Questions
PLC Ladder Logic for Demultiplexer
1 to 8 Demultiplexer PLC ladder diagram
Shaft and Coupling Bore Tapers Repair Caused Frequent Shutdowns
What is a Thermostat
Thermostat – Types, Working Principle, Advantages, Applications
A Question on Steam Drum Water Level Measurement
Surface Detector Level Measurement System
Surface Detector Level Gauges (Plumb-bob)
Hydraulic Actuator Principle
What is a Hydraulic Actuator ?
PLC Ladder Logic Questions and Answers
Function Block Program Simulation