Inst ToolsInst ToolsInst Tools
  • Courses
  • Automation
    • PLC
    • Control System
    • Safety System
    • Communication
    • Fire & Gas System
  • Instrumentation
    • Design
    • Pressure
    • Temperature
    • Flow
    • Level
    • Vibration
    • Analyzer
    • Control Valve
    • Switch
    • Calibration
    • Erection & Commissioning
  • Interview
    • Instrumentation
    • Electrical
    • Electronics
    • Practical
  • Q&A
    • Instrumentation
    • Control System
    • Electrical
    • Electronics
    • Analog Electronics
    • Digital Electronics
    • Power Electronics
    • Microprocessor
  • Request
Search
  • Books
  • Software
  • Projects
  • Process
  • Tools
  • Basics
  • Formula
  • Power Plant
  • Root Cause Analysis
  • Electrical Basics
  • Animation
  • Standards
  • 4-20 mA Course
  • Siemens PLC Course
Reading: Pressure Safety Valve Leak Test Procedure (PSV Testing)
Share
Font ResizerAa
Inst ToolsInst Tools
Font ResizerAa
  • Courses
  • Design
  • PLC
  • Interview
  • Control System
Search
  • Courses
  • Automation
    • PLC
    • Control System
    • Safety System
    • Communication
    • Fire & Gas System
  • Instrumentation
    • Design
    • Pressure
    • Temperature
    • Flow
    • Level
    • Vibration
    • Analyzer
    • Control Valve
    • Switch
    • Calibration
    • Erection & Commissioning
  • Interview
    • Instrumentation
    • Electrical
    • Electronics
    • Practical
  • Q&A
    • Instrumentation
    • Control System
    • Electrical
    • Electronics
    • Analog Electronics
    • Digital Electronics
    • Power Electronics
    • Microprocessor
  • Request
Follow US
All rights reserved. Reproduction in whole or in part without written permission is prohibited.
Inst Tools > Blog > Calibration > Pressure Safety Valve Leak Test Procedure (PSV Testing)

Pressure Safety Valve Leak Test Procedure (PSV Testing)

Learn the pressure safety valve leak test procedure using air, nitrogen, or water. Also includes bench setup, CDTP, and evaluation criteria.

Last updated: June 22, 2025 3:48 pm
Editorial Staff
Calibration Control Valves
No Comments
Share
5 Min Read
SHARE

The pressure safety valve leak test procedure can be carried out using air or nitrogen, or water.

Contents
PSV Leak Test Using Air or NitrogenPSV Leak Test Using WaterUnderstanding the Test SetupWhat is CDTP?What if the Pressure Safety Valve is Under Warranty?

Leak testing a Pressure Safety Valve (PSV) is important to make sure the valve is sealing properly and not leaking when it is supposed to be closed.

There are two common methods to test a PSV:

  1. using air or nitrogen, and
  2. using water.

Here’s how each method works, step by step.

PSV Leak Test Using Air or Nitrogen

Pressure Safety Valve Leak Test Procedure

Step-by-step Process:

1. Place the PSV on a test bench.

Secure the valve on the leak test bench as per standard setup.

2. Find the CDTP (Cold Differential Test Pressure).

This pressure value is usually written on the PSV tag or in its datasheet. If not, you’ll need to calculate it manually (explained in the note at the end).

3. Increase pressure slowly.

Use a needle valve to gradually increase air or nitrogen pressure in the test setup. Go up to 90% of the CDTP, not all the way.

4. Check for leaks.

Attach a clear tube to the valve outlet. Submerge the other end in a container of water. Watch for air bubbles.

5. Evaluate the results.

If the number of bubbles is below the acceptable limit, the valve passes the leak test.

If there are too many bubbles, the valve fails the leak test.

6. If it fails…

Follow the manufacturer’s troubleshooting steps, or contact the valve vendor for help.

PSV Leak Test Using Water

Step-by-step Process:

Set up the PSV on the test bench.

1. Make sure the valve is mounted properly.

2. Identify the CDTP value.

Check the tag plate or datasheet. If it’s not available, calculate it.

3. Fill the PSV with water.

Before starting the test, fill the inside of the valve (the body) with water. This helps detect leaks instantly.

4. Raise the pressure slowly.

Open the water needle valve and increase the pressure carefully up to 90% of CDTP.

5. Observe for leaks.

Check if water is dripping from the outlet.

6. Check the flow rate.

If the water leak is within the allowed limit, the valve passes.

If water is leaking too much, the valve fails.

7. If it fails…

Follow the instructions in the vendor’s manual or contact the supplier.

Understanding the Test Setup

In the air/nitrogen method, leaks show up as bubbles in a water container.

In the water method, leaks show up as visible water drops from the outlet flange.

What is CDTP?

CDTP stands for Cold Differential Test Pressure. It is the pressure used during testing and is usually lower than the actual PSV set pressure used in the plant.

    This is because:

    At high temperatures, the spring inside the valve can become weaker.

    Sometimes, the valve outlet in real applications has constant back pressure, but during testing, it is exposed to atmospheric pressure.

    So, to test accurately, we adjust the set pressure using this formula:

    CDTP = (Set Pressure – Constant Back Pressure) × Temperature Correction Factor

    The correction factor is usually given as a percentage. Always consult the PSV manufacturer to get the correct value.

    What if the Pressure Safety Valve is Under Warranty?

    Before doing any repairs or adjustments, check if the PSV is still under the manufacturer’s warranty.

    If it’s still covered, you are only allowed to test the valve.

    If it fails the test, do not repair it yourself. Report it to the manufacturer to keep the warranty valid.

    Disclaimer:

    This leak test guide is meant for educational purposes only.

    Do not use this as your plant’s standard procedure.

    Always follow:

    • The official PSV vendor instructions
    • Your company’s standard operating procedures
    • Local legal and safety regulations

    Read Next:

    • Instrumentation Inspection Report
    • Pressure Transmitter Calibration at the bench
    • Instrument Technician Interview Questions
    • DIN Valve Connectors – Definition, Types
    • Safety Relief Valve Quiz: Test Your Knowledge
    Don't Miss Our Updates
    Be the first to get exclusive content straight to your email.
    We promise not to spam you. You can unsubscribe at any time.
    Invalid email address
    You've successfully subscribed !

    Continue Reading

    Pressure Switch Calibration Procedure
    Solenoid Valve Problems and Solutions
    Instruments Calibration Procedures
    Pneumatic Training Course – Download PDF
    Why we Require Dual SOV on a Control Valve?
    Breather Valve Working Principle
    Share This Article
    Facebook Whatsapp Whatsapp LinkedIn Copy Link
    Share
    Leave a Comment

    Leave a Reply Cancel reply

    Your email address will not be published. Required fields are marked *

    Stay Connected

    128.3kFollowersLike
    69.1kFollowersFollow
    210kSubscribersSubscribe
    38kFollowersFollow

    Categories

    Explore More

    Solving Control Valve Hunting: Instrument Troubleshooting
    Impulse Line Pressure Testing Procedure
    Stability and Uniformity of Temperature Bath
    Current to Pressure (I/P) Converter Principle
    Different Types of Temperature Calibrators
    As-found and As-left Documentation during Calibration
    Magnetostrictive Level Transmitter Calibration Procedure
    Fundamentals of Valves and their Types

    Keep Learning

    Air Pressure Regulator cut-away diagram

    Air Pressure Regulator Questions

    SMART Control Valve Positioner

    Electronic Valve positioners

    Hydraulic Actuator

    Types of Valve Actuators

    What is Directional Control Valve (DCV)?

    What is Directional Control Valve (DCV)?

    Control Valve Selection Guide

    Control Valve Selection Guide

    Turbidity Sensor Calibration Procedure

    Turbidity Sensor Calibration Procedure

    Shut down valve

    What is Shutdown Valve?

    Direct Lift Diaphragm Normally Open Solenoid Valve

    Direct Lift Diaphragm Solenoid Valve Principle

    Learn More

    Thermocouple Wiring Diagram

    Basics of Thermocouples and RTD

    PLC Cooking Timer Example for Kitchen Automation

    PLC Cooking Timer Example for Kitchen Automation

    Heating and Welding Objective Questions

    Heating and Welding Objective Questions

    Beta ratio ( β )

    Important Factors in Flow Measurement

    DC Motor Connections

    DC Motor Connections

    Head Mount Temperature Transmitter

    What is a Head Mount Temperature Transmitter? – Advantages

    pH Analyzer Calibration and Troubleshooting

    pH Analyzer Calibration and Troubleshooting

    Level Sensors MCQ

    Level Sensors MCQ – Industrial Instrumentation

    Menu

    • About
    • Privacy Policy
    • Copyright

    Quick Links

    • Learn PLC
    • Helping Hand
    • Part Time Job

    YouTube Subscribe

    Follow US
    All rights reserved. Reproduction in whole or in part without written permission is prohibited.
    Welcome Back!

    Sign in to your account

    Username or Email Address
    Password

    Lost your password?