Reading: PLC Based Industrial Conveyor Ladder Logic
Inst Tools > Blog > PLC Tutorials > PLC Based Industrial Conveyor Ladder Logic
Last updated: March 4, 2021 3:25 pm
6 Min Read
This is a PLC Program to start a Belt Conveyor and also make it selectable from where you want to start a conveyor from Local or Remote. Design SCADA graphics also.
Conveyor Ladder LogicProblem Solution:Control & Power Diagram:PLC Inputs and OutputsPLC Program:SCADA Design :Take a look at some screenshotsSCADA ReadySCADA RunSCADA Error
By using PLC and SCADA, prepare a PLC program to start a belt conveyor. Also make it selectable from where you want to start Local or Remote. All the interlocks must be included in the program and also design a SCADA graphics.
PLC Based Industrial Conveyor Logic
Problem Solution:
  • To make a complete logic first, we have prepared a control as well as power diagram of the starter.
  • Then we define the inputs and outputs.
  • We have done the wiring from PLC to Starter and Feedback from Field to PLC.
  • For the Program, first check all signals from the fields are healthy.
  • Then we have prepared a local start/stop logic.
  • For healthy running, check all the interlocks from the fields are ok.
  • If there will be any fault, then we have activated Error signal.
  • After preparing a PLC program we heave design a SCADA in which all the signals are clearly indicated.
Belt Conveyor Electrical Drawing
PLC Program:
Here is the PLC program to start the belt conveyor with interlocks.
OB1:
Conveyor Starter Function Block in PLC
Network 1 :
Ready to START status in PLC
In this Network 1, we are checking whether the belt is ready to start.
This signal will come when all the conditions are healthy as well as safety and power feedback’s are active.
Network 2 :
Local Start Logic in PLC
In the Network 2, When selection of start command is in LOCAL mode then this logic will work.
When start button is pressed from the local operating box Belt_DO bit will be set if Ready_to_Start and No Error will be there.
Network 3 :
Local Stop Logic in PLC
This is the local stop logic, this will only work when the selection command is in LOCAL mode.
When stop button is pressed from the local operating box it will reset the Belt_DO bit.
Network 4 :
Belt Running Feedback and Zero Speed Feedback in PLC Logic
In this Network 4, this logic is required for safety as soon as Belt_DO bit will set and if any case contactor will not operate due to any fault or Zero speed sensor does not detect pulse then after predefined wait time, here we considered it as Run_FB_Time, it will reset the Belt_DO bit and generate Error.
This Error you can acknowledge from the SCADA after resolving the error from the field side.
Network 5 :
Conveyor Belt Trip Logic with Interlock
In this Network 5, All the interlocks are taken in line. If any one of this interlock will become active, then it will reset Belt_DO bit and generate Error.
SCADA Design :
SCADA Design
This is a SCADA screen where operator can operate and visually inspect all the parameter of the conveyor belt.
All the indications are marked just for detailing purpose here.
  • Operator can change the REMOTE/LOCAL mode by just clicking on the LOCAL or REMOTE text.
  • Operator can see the status of READY, ERROR, BSS (Belt Sway Switch), PCS (Pull Chord Switch), ZSS (Zero Speed Switch) as well as LOCAL START and LOCAL STOP button on the operating box.
  • Operator can acknowledge ERROR by just clicking ACK button, just after clearing the error from the field side.
  • Operator can START/STOP the belt conveyor from the ON and OFF button while the selection in REMOTE mode.
SCADA Ready
SCADA Ready
This screenshot (above) shows a online monitor of PLC Program as well as SCADA run time screen. There are a healthy signal from Safety button and Power MCCB, so the conveyor belt are showing healthy ready to start indication.
SCADA Run
SCADA Run
Here we have already given START command from local operating box (as shown in above picture), the belt is showing RUNNING (Green Color in Belt Symbol means it is running smoothly).
There is a healthy ZSS (Zero Speed Switch) signal from the field and there is no ERROR.
SCADA Error
SCADA Error
There is an ERROR bit activated here due to someone is operated PCS (Pull Chord Switch) in the field. So, both ERROR and PCS indication are healthy in SCADA screen as well as we can check in online PLC program as well.
Author : Hiral Patel
Traffic Light Control using PLC
How PLC Reads from Transmitter
PLC Control of 2 Outputs with 1 Input
Facts about PLC Ladder Logic
Contacts and Coils in Ladder Logic
What is Complementary Split Range Control (CSRC)?
Ladder Logic for Stair-Case wiring using Toggle Switches
DC Injection Braking in VFD
Hardwired I/O and Serial I/O – Differences Explained
How to use Masked Move Instruction in PLC
Open User Communication in Siemens Tia Portal – PLC to PLC
  • Kieran Maguire says:
    July 5, 2021 at 9:55 pm
    In the power diagram called “belt conveyor drawing,” why is the MCCB numbered as 120 and 130 for its normally open contacts, and not 128 and 129 as it is on the power diagram? Many thanks.
Mitsubishi Electric GOC Controllers
100 Electrical Circuit Breaker Quiz
LS Electric PLC Program Example: Clothes Washing System
PLC Programming for Tank Heating Control using Heater
How to Upload Siemens PLC Programs?
Elevator PLC Ladder Logic
How to use Master Control Reset (MCR) Instruction in PLC
Example of Automated Guided Vehicle with PLC
Normally closed input actuator as stop button.
Normally-Closed Contacts for Stop Buttons
running two single-phase induction motors sequentially
Control Two Motors in Sequence after Time Delay – Circuit, Operation
4-20mA Loop Power Supply Questions
Sharing data between two PLC systems
Distributed IO Sharing Between PLC Systems – Technical Insights
Yokogawa DCS Tutorials - Configuration of Analog Input (Transmitter)
Yokogawa DCS Tutorials – Configuration of Analog Input (Transmitter)
Transistor Output Wiring
PLC Output Types
PLC Programming Limit Switch
Introduction to SCADA
How to Select the Right Encoder for Your Machine
How to Select the Right Encoder for Your Machine?
Hydrogen Sulfide Accident
The Aghorn Hydrogen Sulfide Accident – H2S Gas
Characteristics of Protective Relay
What is a Protective Relay? Principle, Advantages, Applications
Transmission and Distribution Interview Questions
Measurement and Instrumentation Objective Questions – Part 3
LED Indications on PLC
Getting to Know the LED Indications on GE Make PLC
High-Speed Inputs in PLC
What are High-Speed Inputs in PLC?
Top 50 Electrical Engineering Questions & Answers