Inst ToolsInst ToolsInst Tools
  • Courses
  • Automation
    • PLC
    • Control System
    • Safety System
    • Communication
    • Fire & Gas System
  • Instrumentation
    • Design
    • Pressure
    • Temperature
    • Flow
    • Level
    • Vibration
    • Analyzer
    • Control Valve
    • Switch
    • Calibration
    • Erection & Commissioning
  • Interview
    • Instrumentation
    • Electrical
    • Electronics
    • Practical
  • Q&A
    • Instrumentation
    • Control System
    • Electrical
    • Electronics
    • Analog Electronics
    • Digital Electronics
    • Power Electronics
    • Microprocessor
  • Request
Search
  • Books
  • Software
  • Projects
  • Process
  • Tools
  • Basics
  • Formula
  • Power Plant
  • Root Cause Analysis
  • Electrical Basics
  • Animation
  • Standards
  • 4-20 mA Course
  • Siemens PLC Course
Reading: PID Controller Loop Tuning Questions and Answers – Part 1
Share
Font ResizerAa
Inst ToolsInst Tools
Font ResizerAa
  • Courses
  • Design
  • PLC
  • Interview
  • Control System
Search
  • Courses
  • Automation
    • PLC
    • Control System
    • Safety System
    • Communication
    • Fire & Gas System
  • Instrumentation
    • Design
    • Pressure
    • Temperature
    • Flow
    • Level
    • Vibration
    • Analyzer
    • Control Valve
    • Switch
    • Calibration
    • Erection & Commissioning
  • Interview
    • Instrumentation
    • Electrical
    • Electronics
    • Practical
  • Q&A
    • Instrumentation
    • Control System
    • Electrical
    • Electronics
    • Analog Electronics
    • Digital Electronics
    • Power Electronics
    • Microprocessor
  • Request
Follow US
All rights reserved. Reproduction in whole or in part without written permission is prohibited.
Inst Tools > Blog > Control Systems > PID Controller Loop Tuning Questions and Answers – Part 1

PID Controller Loop Tuning Questions and Answers – Part 1

Last updated: March 29, 2019 1:44 pm
Editorial Staff
Control Systems
2 Comments
Share
17 Min Read
SHARE

This article provides PID controller loop tuning conditions for different conditions to analyze Process Variable, Set Point and Controller Output trends.

PID Controller Loop Tuning Questions and Answers

1. Examine this process trend showing the PV, SP, and Output of a loop controller:

PID Controller Loop Tuning

Based on what you see here, determine the following:

  • Whether this is an open-loop or a closed-loop response
  • Whether the controller is (or needs to be) direct-acting or reverse-acting
  • If possible, identify any problems with the field instrumentation
  • If possible, identify any problems with the controller PID tuning
  • Qualitatively identify the kind of PID tuning we will need for robust control

Answer :

This is a closed-loop test, based on the fact the output signal responds dynamically to the changing process variable, as well as to the step-change in setpoint.

This is a reverse-acting controller: the output steps up when the setpoint steps up (implying the output would step down if the process variable stepped up).

There do not appear to be any field instrumentation problems revealed in this trend. A manual-mode (open-loop) test would be more informative in that regard, but it appears as though the process is very quick to respond with no discernable dead time or other lags.

The controller tuning is clearly inappropriate for this process. Note the large offset between PV and SP (i.e. how the process variable never settles at the setpoint value, even though it’s clearly a fast-responding process). This tells us the controller is configured only for proportional action, and this process needs integral! We can also tell this from the 180 Deg phase shift between PV and output during the oscillations: this is the classic response of a reverse-acting proportional-only controller with excessive gain.

Aggressive integral action with a minimum of proportional gain should work very well in this process, which is probably a liquid flow-control process.

2. Examine this process trend showing the PV, SP, and Output of a loop controller:

PID Controller Graph

Based on what you see here, determine the following:

  • Whether this is an open-loop or a closed-loop response
  • Whether the controller is (or needs to be) direct-acting or reverse-acting
  • If possible, identify any problems with the field instrumentation
  • If possible, identify any problems with the controller PID tuning
  • Qualitatively identify the kind of PID tuning we will need for robust control

Answer :

This is a closed-loop (automatic-mode) response, seeing how the output reacts to the changes in setpoint and process variable.

The control action here is definitely reverse. We can tell this by examining the output’s immediate down-step as the setpoint is decreased, as well as the output’s decrease as the process variable rises later on.

The control system’s initial response to the large setpoint changes looks very good. No problems, either with the field instruments or the controller itself, are evident from this portion of the trend recording. However, something strange happens around the “75” time index, where the process variable begins to rise and the controller output falls to zero in response. It would appear that something has happened to cause the process variable to rise uncontrollably, and the controller is helpless to correct the situation.

We may speculate as to the cause of this uncontrollable situation, but there is not enough information to make a definitive judgment. One possible cause is a large load change in the process that overwhelms the controller. Another possible cause is a final control element failure, going to the 100% condition as if the controller signal had increased to saturation.

3. Examine this process trend showing the PV, SP, and Output of a loop controller:

PID Loop Tuning

Based on what you see here, determine the following:

  • Whether this is an open-loop or a closed-loop response
  • Whether the controller is (or needs to be) direct-acting or reverse-acting
  • If possible, identify any problems with the field instrumentation
  • If possible, identify any problems with the controller PID tuning
  • Qualitatively identify the kind of PID tuning we will need for robust control

Answer :

This is a closed-loop test, based on the fact the output signal responds dynamically to the changing process variable, as well as to the step-change in setpoint.

This is a reverse-acting controller: the output steps up when the setpoint steps up (implying the output would step down if the process variable stepped up).

There do not appear to be any field instrumentation problems revealed in this trend. A manual-mode (open-loop) test would be more informative in that regard, but it appears as though the process is very quick to respond with no discernable dead time or other lags.

The controller tuning is too heavy on proportional action. We can tell this from the phase shift between PV and output during the oscillations, which is nearly 180o . Excessive integral action would shift the phase of the output wave further to the right (i.e. so that each peak of the output waveform coincided with the zero-crossing of the PV waveform, or very nearly). The fact that the inverse peaks of the PV and output waves are very nearly aligned tells us that excessive gain (proportional action) is the culprit here. Another clue is the magnification of noise we see in the output trend compared to the PV trend – only proportional action or derivative action can cause this, and since we see no sign of excessive derivative action (e.g. output wave leading the PV wave), we can safely say the problem is too much gain.

The process response time (dead time, lag time) seems to be very short, which is a good thing for process control. We can tell, however, that this is an integrating process by the way it was able to achieve a new SP value with the old output value. This means it will exhibit some overshoot with SP changes if there is any integral action. We may have to do most of the control through proportional action (albeit much less gain than we are using now!), with just enough integral action to handle load changes.

4. Examine this process trend showing the PV, SP, and Output of a loop controller:

PID Controller Graph - 2

Based on what you see here, determine the following:

  • Whether this is an open-loop or a closed-loop response
  • Whether the controller is (or needs to be) direct-acting or reverse-acting
  • If possible, identify any problems with the field instrumentation
  • If possible, identify any problems with the controller PID tuning
  • Qualitatively identify the kind of PID tuning we will need for robust control

Answer :

This is an open-loop (manual-mode) response, seeing how the output is being moved up and down in step-change fashion which suggests a human operator making changes in manual. The process variable, by comparison, is responding in a smooth-changing manner to those output step-changes.

The process variable is increasing as the output signal is made to increase. This tells us the control action in automatic mode will need to be reverse. Put in other terms, if we know the process variable is driven by the output signal in direct fashion (i.e. increasing the output makes the process variable increase, and vice-versa), then we know the controller is going to have to do the opposite to regulate this process. For example, if the process variable happens to increase due to a load change, the controller’s output will need to decrease in order to drive that process variable back down where it belongs.

We can tell there is definitely a significant amount of hysteresis in the final control element because the process variable fails to respond to the last (smallest) step-change in controller output. This, incidentally, is a good way to test for hysteresis: step the output up and down in progressively smaller increments until no response is seen in the process variable. It is at that point you may interpret that last output step-change as the amount of hysteresis in the final control element. In this case, that quantity appears to be about 5%.

Since this is an open-loop test we cannot tell how well the controller is tuned. However, we can discern from the response of the process variable to output step-changes that this is a self-regulating process with little dead time and first-order lag characteristics, which means it should respond well to fairly aggressive proportional action and will also require integral action to avoid offset.

5. Examine this process trend showing the PV, SP, and Output of a loop controller:

How to Do PID Loop Tuning

Based on what you see here, determine the following:

  • Whether this is an open-loop or a closed-loop response
  • Whether the controller is (or needs to be) direct-acting or reverse-acting
  • If possible, identify any problems with the field instrumentation
  • If possible, identify any problems with the controller PID tuning
  • Qualitatively identify the kind of PID tuning we will need for robust control

Answer :

This is a closed-loop test, based on the fact the output signal responds dynamically to the changing process variable, as well as to the step-change in setpoint.

This is a reverse-acting controller: the output steps up when the setpoint steps up (implying the output would step down if the process variable stepped up).

This process does exhibit some dead time as well as lag time, which explains the setpoint overshoot. A field check of the control element (valve) might be good to do, so see that it is not sticking and causing dead time.

The controller tuning actually looks pretty good here. The only problem is the slight overshoot of setpoint, which may or may not be significant depending on the specific process and the needs of operations personnel. If this overshoot is deemed excessive, we might wish to turn down the proportional action (gain), based on the fact the PV and output waves seem to hit their respective peaks at nearly the same time (characteristic of proportional-dominant action).

Given the existence of dead time and lag time together, we must be careful not to use too much proportional action lest the loop oscillate. Derivative action could be very useful in taming the effects of lag time.

6. Examine this process trend showing the PV, SP, and Output of a loop controller:

PID Loop Tuning - 1

Based on what you see here, determine the following:

  • Whether this is an open-loop or a closed-loop response
  • Whether the controller is (or needs to be) direct-acting or reverse-acting
  • If possible, identify any problems with the field instrumentation
  • If possible, identify any problems with the controller PID tuning
  • Qualitatively identify the kind of PID tuning we will need for robust control

Answer :

This is a closed-loop test, based on the fact the output signal responds dynamically to the changing process variable, as well as to the step-change in setpoint.

This is a reverse-acting controller: the output steps up when the setpoint steps up (implying the output would step down if the process variable stepped up).

There do not appear to be any field instrumentation problems revealed in this trend. A manual-mode (open-loop) test would be more informative in that regard, and it appears as though the process possesses a multiple-order lag, but the time scale of this lag seems modest. It might not be a bad idea to look around for sources of lag time (e.g. thermowell mass, improperly inserted temperature probe), just to see if the response time might be improved a bit. Another possibility explaining the lag time would be a transmitter (or controller input block) configured with too much filtering (damping), adding a single-order lag to whatever lag(s) the process itself already possesses.

The controller tuning is clearly inappropriate for this process, and should be much more aggressive than it is right now. Note how the PV is taking a long time to reach the new SP, and how the controller output is ramping down at a very leisurely pace.

This process appears to be self-regulating, and so we know we must have some integral action in the controller. The existence of multiple-order lag makes this loop a good candidate for moderate derivative action.

7. Examine this process trend showing the PV, SP, and Output of a loop controller:

PID Loop Tuning - 2

Based on what you see here, determine the following:

  • Whether this is an open-loop or a closed-loop response
  • Whether the controller is (or needs to be) direct-acting or reverse-acting
  • If possible, identify any problems with the field instrumentation
  • If possible, identify any problems with the controller PID tuning
  • Qualitatively identify the kind of PID tuning we will need for robust control

Answer :

This is a closed-loop test, based on the fact the output signal responds dynamically to the changing process variable, as well as to the step-change in setpoint.

This is a reverse-acting controller: the output ramps up whenever the PV is below SP, and the output ramps down whenever the PV is above SP.

This loop definitely has hysteresis in the final control element (e.g. sticky valve), because this trend is a classic slip-stick cycle in a self-regulating process: the PV exhibits a square-wave shape while the output ramps up and down like a sawtooth wave.

There probably isn’t anything wrong with the controller’s tuning, and no tuning adjustments will fundamentally address the problem of valve stiction.

The process appears to be self-regulating with a fast response time (note how quickly the PV settles at a new value following each “slip” of the control valve), which means it should control very well with aggressive integral action. However, final control element hysteresis is the bane of integral action, as it causes repeated reset windup as we see here.

Credits :  by Tony R. Kuphaldt

Don't Miss Our Updates
Be the first to get exclusive content straight to your email.
We promise not to spam you. You can unsubscribe at any time.
Invalid email address
You've successfully subscribed !

Continue Reading

Tuning a Liquid Level Process Control Loop
Types of Industrial Control Systems
Basics of Alarms and Trips
Add On Instructions Programming – Analog Input Devices in Studio 5000
What is Integral Wind Up ?
DCS Commissioning Steps
Share This Article
Facebook Whatsapp Whatsapp LinkedIn Copy Link
Share
2 Comments
  • Fauzi says:
    April 11, 2018 at 8:53 pm

    Good knowledge..
    Thanks

    Reply
  • zekarias says:
    October 25, 2022 at 5:52 pm

    Good presentation
    thanks

    Reply

Leave a Reply Cancel reply

Your email address will not be published. Required fields are marked *

Stay Connected

128.3kFollowersLike
69.1kFollowersFollow
210kSubscribersSubscribe
38kFollowersFollow

Categories

Explore More

Proportional-only Offset
Difference between Availability, Reliability & SIL
Ziegler-Nichols Closed Loop Tuning Procedure
Installing and Using Modern Industrial Joystick Controls
Inductive Coupling Effects
What is a Control Loop ?
Basics for CAN Bus Protocol – Controller Area Network
Industrial Automation Mobile Apps

Keep Learning

Typical process control loop

How Process Control Loop Works

Node-RED in PLC Automation

Node-RED in PLC Industrial Automation

Types of Wireless Technologies in Industrial Automation

Types of Wireless Technologies in Industrial Automation

Field Instruments Questions and Answers

Control Room and Field Instruments Questions and Answers

Instrumentation During the Detail Design Phase

Instrumentation Engineer Activities & Documents – Detail Design Phase

Quantitative PID tuning procedures

Quantitative PID tuning procedures

ICS Control System

ICS Control System Security

Transducer

What is a Transducer ?

Learn More

4-20mA Loop Power Supply Questions

4-20mA Loop Power Supply Questions and Answers

Span of Pressure Gauge

How to Decrease Span of Pressure Gauge?

Latching and Unlatching in PLC Programming for Beginners

Latching and Unlatching in PLC Programming Example

Ladder Rung with Two Outputs

PLC Multiple Outputs Configuration

Electrical Machines Questions and Answers

Three Phase Induction Motor Power Factor Control

Fire and Gas System

Types of Fire and Gas Detectors

Dual Solenoid Valve on Control Valve

Why we Require Dual SOV on a Control Valve?

Electronics & Instrumentation Engineering Interview Questions For Freshers

Electronics & Instrumentation Engineering Interview Questions For Freshers

Menu

  • About
  • Privacy Policy
  • Copyright

Quick Links

  • Learn PLC
  • Helping Hand
  • Part Time Job

YouTube Subscribe

Follow US
All rights reserved. Reproduction in whole or in part without written permission is prohibited.
Welcome Back!

Sign in to your account

Username or Email Address
Password

Lost your password?