Inst ToolsInst ToolsInst Tools
  • Courses
  • Automation
    • PLC
    • Control System
    • Safety System
    • Communication
    • Fire & Gas System
  • Instrumentation
    • Design
    • Pressure
    • Temperature
    • Flow
    • Level
    • Vibration
    • Analyzer
    • Control Valve
    • Switch
    • Calibration
    • Erection & Commissioning
  • Interview
    • Instrumentation
    • Electrical
    • Electronics
    • Practical
  • Q&A
    • Instrumentation
    • Control System
    • Electrical
    • Electronics
    • Analog Electronics
    • Digital Electronics
    • Power Electronics
    • Microprocessor
  • Request
Search
  • Books
  • Software
  • Projects
  • Process
  • Tools
  • Basics
  • Formula
  • Power Plant
  • Root Cause Analysis
  • Electrical Basics
  • Animation
  • Standards
  • 4-20 mA Course
  • Siemens PLC Course
Reading: Ziegler-Nichols Closed Loop Tuning Procedure
Share
Notification Show More
Font ResizerAa
Inst ToolsInst Tools
Font ResizerAa
  • Courses
  • Design
  • PLC
  • Interview
  • Control System
Search
  • Courses
  • Automation
    • PLC
    • Control System
    • Safety System
    • Communication
    • Fire & Gas System
  • Instrumentation
    • Design
    • Pressure
    • Temperature
    • Flow
    • Level
    • Vibration
    • Analyzer
    • Control Valve
    • Switch
    • Calibration
    • Erection & Commissioning
  • Interview
    • Instrumentation
    • Electrical
    • Electronics
    • Practical
  • Q&A
    • Instrumentation
    • Control System
    • Electrical
    • Electronics
    • Analog Electronics
    • Digital Electronics
    • Power Electronics
    • Microprocessor
  • Request
Follow US
All rights reserved. Reproduction in whole or in part without written permission is prohibited.
Inst Tools > Blog > Control Systems > Ziegler-Nichols Closed Loop Tuning Procedure

Ziegler-Nichols Closed Loop Tuning Procedure

Last updated: August 31, 2019 8:40 pm
Editorial Staff
Control Systems
No Comments
Share
3 Min Read
SHARE

The closed-loop, or “Ultimate” tuning method of Ziegler and Nichols was applied to this process.

Eliminating both integral and derivative control actions from the controller, and experimenting with different gain (proportional) values until self-sustaining oscillations of consistent amplitude (Note) were obtained, gave a gain value of 11, as shown in below figure.

Note : The astute observer will note the presence of some limiting (saturation) in the output waveform, as it attempts to go below zero percent.

Normally, this is unacceptable while determining the ultimate gain of a process, but here it was impossible to make the process oscillate at consistent amplitude without saturating on the output signal.

The gain of this process falls off quite a bit at the ultimate frequency, such that a high controller gain is necessary to sustain oscillations, causing the output waveform to have a large amplitude.

Ziegler-Nichols Closed Loop Tuning

Ziegler-Nichols Closed Loop Tuning Procedure

From the trend, we can see that the ultimate period (Pu) is approximately 7 minutes in length. Following the Ziegler-Nichols recommendations for PID tuning based on these process characteristics:

Ziegler-Nichols Closed Loop Tuning Formula

It should be immediately apparent that these tuning parameters will yield poor control. While the integral and derivative values are close to those predicted by the open-loop (Reaction Rate) method, the gain value calculated here is even larger than what was calculated before.

Since we know proportional action was excessive in the last tuning attempt, and this one recommends an even higher gain value, we can expect our next trial to oscillate even worse.

Applying the PID values of 6.6 (gain), 3.5 minutes per repeat (integral), and 0.875 minute (derivative) gave the following result in automatic mode:

Ziegler-Nichols Loop Tuning

This time the loop stability is a bit worse than with the PID values given by the Ziegler-Nichols open-loop tuning equations, owing mostly to the increased controller gain value of 6.6 (versus 4.5).

Proportional action is still the dominant mode of control here, as revealed by the minimal phase shift between PV and OUT waveforms (ignoring the 180 degrees of shift inherent to the controller’s reverse action).

In all fairness to the Ziegler-Nichols technique, the excessive controller gain value probably resulted more from the saturated output waveform than anything else. This led to more controller gain being necessary to sustain oscillations, leading to an inflated Kp value.

Don't Miss Our Updates
Be the first to get exclusive content straight to your email.
We promise not to spam you. You can unsubscribe at any time.
Invalid email address
You've successfully subscribed !

Continue Reading

Instrumentation Engineer Activities & Documents – Detail Design Phase
How Process Control Loop Works
VFD Commissioning and Testing Procedure (Variable Frequency Drive)
PID Tuning Recommendations based on Process Dynamics
Instrumentation and Control Project Packages – Detail Engineering
What is a Transducer ?
Share This Article
Facebook Whatsapp Whatsapp LinkedIn Copy Link
Share
Leave a Comment

Leave a Reply Cancel reply

Your email address will not be published. Required fields are marked *

Stay Connected

128.3kFollowersLike
69.1kFollowersFollow
210kSubscribersSubscribe
38kFollowersFollow

Categories

Explore More

Analysis of HART communicator and Smart HART Transmitter
Supervisory Control
ICS Control System Security
Top 5 Advantages of Human-Machine Interface (HMI)
Types of Control Systems
Why Use a Current Loop?
Difference between SR Flipflop and RS Flipflop ?
What is DIN rail ?

Keep Learning

Integral controller eliminates offset error

How Integral Controller Reduces offset error ?

PID-Controller-Selection

PID Controller Selection

Explain how this is an example of Ratio Control?

Questions on Ratio Control System

Tips for Reducing the Noise Signals

Tips for Reducing the Noise Signals

4 TO 20 MA ANALOG CURRENT SIGNALS

Basics of 4 to 20 mA analog Signals

energized-to-safe-loop

Energize to Safe Loop philosophy

Distributed Control System Interview Questions

NAMUR OPEN ARCHITECTURE

What is NAMUR OPEN ARCHITECTURE?

Learn More

Electronic Force Balance Pressure Transmitter

Electronic Force Balance Pressure Transmitter

A Large Gate Valve Failed Motorized Operation

A Large Gate Valve’s Failed Motorized Operation

Electrical Machines Questions and Answers

Synchronous Machines Excitation Quiz

Instrument Calibration Questions

Instrument Calibration Questions

Automation in Agriculture

Automation in Farming & Agriculture

Categories of Unshielded Twisted Pair

Network Cabling

PLC Program to Control Level of Two Tanks

PLC Level Control of Two Tanks

Power Electronics Objective Questions

Choppers MCQ

Menu

  • About
  • Privacy Policy
  • Copyright

Quick Links

  • Learn PLC
  • Helping Hand
  • Part Time Job

YouTube Subscribe

Follow US
All rights reserved. Reproduction in whole or in part without written permission is prohibited.
Welcome Back!

Sign in to your account

Username or Email Address
Password

Lost your password?