Inst ToolsInst ToolsInst Tools
  • Courses
  • Automation
    • PLC
    • Control System
    • Safety System
    • Communication
    • Fire & Gas System
  • Instrumentation
    • Design
    • Pressure
    • Temperature
    • Flow
    • Level
    • Vibration
    • Analyzer
    • Control Valve
    • Switch
    • Calibration
    • Erection & Commissioning
  • Interview
    • Instrumentation
    • Electrical
    • Electronics
    • Practical
  • Q&A
    • Instrumentation
    • Control System
    • Electrical
    • Electronics
    • Analog Electronics
    • Digital Electronics
    • Power Electronics
    • Microprocessor
  • Request
Search
  • Books
  • Software
  • Projects
  • Process
  • Tools
  • Basics
  • Formula
  • Power Plant
  • Root Cause Analysis
  • Electrical Basics
  • Animation
  • Standards
  • 4-20 mA Course
  • Siemens PLC Course
Reading: Types of Fire and Gas Detectors
Share
Font ResizerAa
Inst ToolsInst Tools
Font ResizerAa
  • Courses
  • Design
  • PLC
  • Interview
  • Control System
Search
  • Courses
  • Automation
    • PLC
    • Control System
    • Safety System
    • Communication
    • Fire & Gas System
  • Instrumentation
    • Design
    • Pressure
    • Temperature
    • Flow
    • Level
    • Vibration
    • Analyzer
    • Control Valve
    • Switch
    • Calibration
    • Erection & Commissioning
  • Interview
    • Instrumentation
    • Electrical
    • Electronics
    • Practical
  • Q&A
    • Instrumentation
    • Control System
    • Electrical
    • Electronics
    • Analog Electronics
    • Digital Electronics
    • Power Electronics
    • Microprocessor
  • Request
Follow US
All rights reserved. Reproduction in whole or in part without written permission is prohibited.
Inst Tools > Blog > Fire & Gas System > Types of Fire and Gas Detectors

Types of Fire and Gas Detectors

Last updated: March 18, 2019 7:43 pm
Editorial Staff
Fire & Gas System
No Comments
Share
8 Min Read
SHARE

Fire and Gas System or portion of a combination system that consists of components and circuits arranged to monitor and annunciate the status of fire or presence of gas alarm or supervisory signal-initiating devices and to initiate the appropriate response to those signals.

Fire and Gas System

I. Gas Detectors

Gas Detectors are broadly divided into 2 types:

a. Flammable Gas Detectors:

Detects the percentage by volume of flammable gas in air in terms of LFL and UFL

b. Toxic Gas Detectors:

Detects the concentration in ppm of Toxic gas in terms of TLV

1. Flammable Gas Detectors:

The three types of Flammable gas detectors are:

a. Catalytic Gas Detectors

b. Infrared Gas Detectors

c. Open Path (Line of Sight) Gas Detectors

a. Catalytic (Pellistor) Gas Detectors:

Working Principle: Catalytic gas detectors determine gas concentration through oxidization which results in heat, and this is sensed by a bridge circuit.

It follows that catalytic gas detectors under-read in the low oxygen atmospheres which exist with gas rich releases.

Set Point: Catalytic detectors have a typical recommended minimum alarm setting of 20 % LFL and 60 % LFL to indicate low and high level of gas

b. Infrared Gas Detectors:

Working Principle: Infrared Gas Detectors make use of the property of Hydrocarbons and other gases to absorb infra-red energy at certain wavelengths but not others.

For HCs the absorption peak occurs around 3.4 µm. A reference measurement is normally made close to the measurement wavelength that is not absorbed by expected gases.

The ratio from the two measurements gives the gas concentration free from variations in signal intensity and detection sensitivity.

Set Point: Infra-red detectors have a typical recommended minimum alarm setting of 20 % LFL and 60 % LFL to indicate low and high level of gas

c. Open Path (Line of Sight) Gas Detectors:

Working Principle: Open path gas detectors make use of properties of gases to absorb infrared energy at certain wavelengths but not others.

This property coupled with high energy sources enables open path detectors to sense gas over relatively long distances.

Set Point: Set Point: Open path detectors have a typical recommended minimum alarm setting of 0.5 LFL m (50 % LFL extended for one meter)

2. Toxic Gas Detectors

Major 2 categories are available:

  • Detectors for gases which create an immediate health hazard (eg. H2S, CO, HF, HCl, Cl2)
  • Detectors for gases that create a health hazard on long term exposure (eg. Vinyl Chloride, Benzene, Toluene etc.)

H2S detectors:

The two types of H2S detectors available are:

a. Electro-chemical cell type:

This type is based on an electro-chemical cell, developed to react exclusively to H2S.

As a result of chemical reaction of the cell organic electrolyte with H2S, an electric current is generated, which is proportional to the H2S concentration in the sample gas.

b. Semi-conductor (MOS) type:

Working principle: The semi-conductor type is based on the adsorption of H2S molecules on the surface of a solid-state semi-conductor crystal which causes a change in electrical resistance of the electrical circuit of which the semi-conductor forms the part.

Set Point: H2S detectors have a typical recommended minimum alarm setting of 5 ppm. If second stage alarm is used, 10 ppm shall be used.Semi-conductor (MOS) type

II. Fire Detectors

Fire Detectors are broadly divided into 3 types:

1. Smoke Detectors

  • Ionisation
  • Photo-Electric

2. Heat Detectors

3. Flame Detectors

1. Smoke Detectors:

There are two types of smoke as mentioned above

a. Ionisation Smoke Detector

Detection Principle:

These Detectors have an ionisation chamber with a 8 particle radiator consisting an Americium-241 foil at its centre and it ionises the air inside the chamber.

An electric voltage is applied to the needle electrode and as a result, a known current flows through the detection chamber when the detector is in its normal state. In the event of fire, minute aerosol particles (soot particles, combustion gases etc.) attach themselves to the ionised particles.

This increases the resistance in the chamber and consequently reduces the current flow within the detection chamber. This change is registered by Detector’s electronics and a fire signal is sent to the Control Panel.

Ionisation Smoke Detector

b. Photoelectric (Optical) Smoke Detector

Detection Principle:

The sensor consists of a transmitter LED and a receiver photo-diode. These two devices are installed at a specific angle to one another and separator by a screen, so that light from the LED cannot impinge directly on the receiver diode.

The transmitter LED emits infrared light into the detection chamber. In the event of a fire, visible combustion products enter into the chamber and some of the light emitted by the LED is scattered by the particles so that it impinges on the receiver diode.

This naturally increases the signal level generated by the receiver, which is registered by the detector electronics, which in turn trigger the alarm signal.

Photoelectric (Optical) Smoke Detector Principle

2. Heat Detectors:

Heat or Thermal Detectors register the increase in temperature caused by a Fire.

a. Fixed Temperature

It triggers automatically when a preset ambient temperature is reached.

b. Rate of Rise

In addition to present trigger temperature, the rate-of rise detectors also evaluate the speed of temperature increase. If the temperature rises faster than the pre-set amount within a specific period, a rate-of-rise detector will trigger an alarm even if the set point trigger temperature has not actually been reached.

c. Rate Compensated

It responds when the temperature of the air surrounding the device reaches a predetermined level, regardless of the rate of temperature rise.

3. Flame Detectors

  • Flame detectors are typically used in open areas outdoors, but can also be used indoors
  • Used to protect high risk areas such as oil rigs, fuel stores, petro-chemical plants, hangers etc
  • They work by analysing the energy emissions from a fire (UV or IR) not the combustion products such as smoke and heat
  • Hot objects (engines / exhausts / heaters) are potential false alarm sources, including the Sun
  • Need to distinguish between emissions from a real fire and a false alarm source
  • High value detectors covering large areas

The different types of Flame detector are:

  • Ultra Violet detectors
  • Single Channel IR detectors
  • Combined UV and Single channel IR
  • Dual Channel IR flame detectors
  • Triple Channel IR flame detectors
  • CCTV flame detection
Don't Miss Our Updates
Be the first to get exclusive content straight to your email.
We promise not to spam you. You can unsubscribe at any time.
Invalid email address
You've successfully subscribed !

Continue Reading

Fire Alarm System Commissioning Procedure
Gas Detectors Standards
Carbon Monoxide Gas Sensor Principle
Factors for Setting Alarm Levels on Toxic Gas Detectors
How to identify location of Fire Detectors
Overview of Fire/Smoke/Flame/Heat/Gas Detectors
Share This Article
Facebook Whatsapp Whatsapp LinkedIn Copy Link
Share
Leave a Comment

Leave a Reply Cancel reply

Your email address will not be published. Required fields are marked *

Stay Connected

128.3kFollowersLike
69.1kFollowersFollow
210kSubscribersSubscribe
38kFollowersFollow

Categories

Explore More

Which Gases Can a Multi-Gas Detector Detect?
Why Fire and Gas Detectors are 3-Wire types instead of 2 Wire?
Fire Water Spray Systems Principle
Infrared Hydrocarbon Gas Detector Calibration Procedure
Fire and Safety
Active and Passive Fire Protection
Heat Detector Testing Procedure
What are Fire Branches?

Keep Learning

Deluge Valve Operation using Solenoid Valve Animation

Deluge Valve Operation

Rate of Rise Thermal Detectors Working Principle

Rate of Rise Thermal Detectors Working Principle

Gases LEL and UEL

What is Lower Explosive Limit & Upper Explosive Limit ?

Manual Call Point Testing Procedure

Manual Call Point Testing Procedure

What is Photoionization Detector (PID)

What is Photoionization Detector (PID)?

foam fire protection system

Basics of Foam Fire Fighting System

Rate Compensated Heat Detectors Working Principle

Rate Compensated Heat Detectors Working Principle

Fire Hydrant System

Basics of Fire Fighting Hydrant Systems

Learn More

Fiber Optic Measurement Techniques

Fiber Optic Measurement Multiple Choice Questions (MCQ)

Scaling Sensor Output to Engineering Units

Scaling Sensor Output to Engineering Units

How to Blink Lights in Ladder Logic

How to Blink Lights in Ladder Logic?

3-way globe valve

What is Mixing or Diverting Valve ?

full-wave-bridge-rectifier-with-voltage-regulator

Basics of Voltage Regulators

Transformers Interview Questions & Answers

Transformers Interview Questions & Answers

Digital Electronics Objective Questions

Digital Electronics Objective Questions

Superheated Steam Temperature Control System

Superheated Steam Temperature Control System

Menu

  • About
  • Privacy Policy
  • Copyright

Quick Links

  • Learn PLC
  • Helping Hand
  • Part Time Job

YouTube Subscribe

Follow US
All rights reserved. Reproduction in whole or in part without written permission is prohibited.
Welcome Back!

Sign in to your account

Username or Email Address
Password

Lost your password?