Reading: Muting Functions of Safety Control Circuits – PLC Example
Inst Tools > Blog > PLC Tutorials > Muting Functions of Safety Control Circuits – PLC Example
Muting function is used to interrupt the safety PLC light curtain without triggering a safety condition that will probably stop your process.
Last updated: March 6, 2023 3:11 pm
Mahmoud Salama
13 Min Read
In previous articles, we gave examples of some of the most common safety instructions in a safety PLC. In this article, we will talk about another important safety instruction which is the Muting function, and we will give a simple PLC example code.
What is a Muting Function?Muting Function Instruction in TIA PortalDifferent approaches for Muting Function4 Sensors Approach Sequence2 Sensors Approach SequenceSimple PLC exampleProgramming stepsCode simulation:Conclusion
Contents:
  • What are Muting Functions?
  • Muting Function Instruction in TIA Portal
  • Different approaches for muting function
  • 4 sensors approach sequence
  • 2 sensors approach sequence
  • Hardware configurations
  • Programming steps
  • Code simulation
  • Conclusion
A muting function is when a group of sensors (usually 2 or 4 sensors), are used to temporarily disable the safety function of a safety light curtain of a safety sensor when a workpiece or a conveying palette is passing through the guarded area of the safety function.
The challenge facing a muting function is to be able to differentiate between a passing workpiece and a passing worker through the hazard area.
There are two different cases of activating a muting function:
  • A workpiece or a conveying palette is passing through the guarded area of the safety function.
  • Enabling personnel access inside the dangerous areas during the non-dangerous part of the machine cycle. For example, when an operator needs to load/unload the workpiece inside a hazard area.
So, a muting function should only work when a workpiece is passing through the risk area, but if a worker or an operator passes through the risk area, the safety function should be activated and the machine should stop immediately.
See picture 1 for MUT_P or Parallel muting safety function in TIA Portal.
What is a muting function
Picture 1 – MUT_P instruction
As you can see, The MUT_P safety function has a lot of parameters, let’s see what some of them mean:
  • MS_11 and MS_12:  are muting sensor pair 1.
  • MS_21 and MS_22:  are muting sensor pair 2.
  • DISCTIM1: Discrepancy time of sensor pair 1 (0 to 3 s)
  • DISCTIM2: Discrepancy time of sensor pair 2 (0 to 3 s)
  • FREE: this is the signal coming from the light curtain, if TRUE then it means the light curtain is not interrupted.
  • STOP: this is the signal coming from the conveyer system, if TRUE then it means the conveyer system has stopped, the muting function will not be activated if the conveyer is stopped.
  • ENABLE: if set to TRUE, the muting function can be obtained. This can be any condition that you want to have before allowing the muting function to happen, a new palette request from the machine.
  • ACK: used to acknowledge a restart after a failure.
  • MUTING: display the status of the muting function.
  • TIME_MAX: max time of the muting function, this time should be carefully calculated and set, to prevent safety function failures due to, for example, a worker trying to bypass the safety function.
There are many different approaches to muting functions, but the most common are:
  • 4 sensors muting function
  • 2 sensors muting function
In this approach, 4 sensors (MS_11, MS_12, MS_21, and MS_22) are used to provide detection of the moving workpieces or a conveying palette.
Each two sensors facing each other should be installed in such a way that the moving palette will be detected by the two sensors at the same time or within a discrepancy time. And also both of them should be deactivated at the same time.
Also, the 4 sensors should be installed in such a way that sensors MS_21 and MS_22 will get activated before MS_11 and MS_12 are de-activated, to enable continuity of the muting function.
The following steps show the sequence of achieving a muting function without any errors:
  • When both muting sensors MS_11 and MS_12 are activated by the product within DISCTIM1. The muting function will start, provided that Enable signal of the MUT_P safety instruction is TRUE. See picture 2.
  • The muting function will continue to be TRUE even when the light curtain detects the product, (FREE = 0).
muting function starts
Picture 2 – Muting function starts
  • As long as both muting sensors MS_11 and MS_12 continue to be activated, the MUTING function of the instruction causes Q to remain 1 and MUTING to remain 1 (so that the product can pass through the light curtain without causing the machine to stop).  See picture 3.
Safety Light Curtains with muting function
Picture 3 – Muting function continues, even when the light curtain is interrupted.
  • The two muting sensors MS_21 and MS_22 must be activated (within DISCTIM2) before muting sensors MS_11 and MS_12 are switched to inactive. This way the MUT_P instruction retains the muting function. (Q = 1, MUTING = 1). See picture 4.
Light curtain muting examples
Picture 4 – Muting function remains
  • When one of the two muting sensors MS_21 and MS_22 is deactivated the muting function will be terminated (Q = 1, MUTING = 0). See picture 5.
Two muting sensors
Picture 5 – Muting function is terminated.
  • Note that, MS_21 and MS_22 must both be deactivated within DISCTIM2, otherwise if one of them is deactivated and the DISCTIM1 is elapsed before the second one is deactivated, the safety PLC will consider an internal failure in the sensor and will trigger the safety function.
 If reflection light barriers are used as muting sensors, then only 2 sensors MS_11 and MS_12 Can be used for a muting function, the 2 sensors will be arranged diagonally. See picture 6.
The sequence of the muting function is obtained according to the following steps:
Two sensors approach sequence
Picture 6 – Muting function with only 2 sensors
  • The muting function will continue to be TRUE even when the light curtain detects the product, (FREE = 0).  As long as MS_11 and MS_12 are still activated by the product. The product can then pass through the light curtain without causing the machine to stop.
  • When one of the two muting sensors MS_11 and MS_12 is deactivated, the muting function will be terminated (Q = 1, MUTING = 0).
  • Note that, MS_11 and MS_12 must both be deactivated within DISCTIM1, otherwise if one of them is deactivated and the DISCTIM1 is elapsed before the second one is deactivated, the safety PLC will consider an internal failure in the sensor and will trigger the safety function.
Simple PLC example
Hardware configurations:
First, let’s define all needed inputs for our simulation. See picture 7.
Simple PLC example Hardware configurations
Picture 7 – Define inputs
Programming steps
Start with adding your MUT_P safety instruction, see picture 1, and then choose Multi-instance DB for your function. See picture 8.
Multi-instance DB of safety function in PLC
Picture 8 – Multi-instance DB of safety function
Next, add your inputs to the MUT_P safety instruction, also define some static outputs and add them to the MUT_P outputs. See picture 9.
Picture 9 – Add your inputs and outputs
The coding part is done, compile your code and start a new simulation.
Code simulation:
First, run your PLC and notice the MUT_P at start-up, see picture 10.
PLC safety instructions at startup
Picture 10 – Safety instructions at startup
From picture 10 you can see that there is a fault in the instruction, because the FREE signal is FALSE, which means the light curtain is interrupted without muting, so a safety condition will be triggered.
Now, set the FREE signal to TRUE (to simulate the light curtain not being interrupted) and acknowledge the safety condition to reset the fault. See picture 11.
Reset the fault in Safety PLC
Picture 11 – Resetting the fault
Now, see pictures 12 to 17 for a complete sequence of the muting function.
Safety Function Light Curtain with Muting
Picture 12 – ENABLE signal is FALSE
Muting function
Pictures 13 – Muting function started
As the product keeps moving, the light curtain will eventually be interrupted, that should happen while MS11 and MS12 are still active, (see picture 3) to keep the muting function triggered. See picture 14.
Conveyor light curtain muting
Picture 14 – Light curtain interrupted the muting function still active
After a while, MS21 and MS22 will also be activated (see picture 4), this should happen while the light curtain is still interrupted by the product and while MS11 and MS12 are still active see picture 15.
Sequential Muting of a Light Curtain
Picture 15 – Muting function is still active
After a while, MS11 and MS12 will be deactivated, but the muting function will still be active because MS21 and MS22 are still activated. See picture 16.
Multifunctional safety light curtain offers muting
Picture 16 – MS11 and MS12 are now deactivated, muting is still active.
When MS21 and MS22 are deactivated, the muting function will be stopped. See picture 17.
muting function in siemens tia portal
Picture 17 – Muting function is now OFF
Note that, if the TIME_MAX of the safety instruction is elapsed before muting one complete safety muting function finished, the PLC will give a fault and the output will stop immediately.
We now finished the simulation and test of a 4 sensors muting function sequence.
Check the PLC software attached to the article and try to see if you can simulate the 2-sensor Muting function sequence.
Download the muting function logic and its project back up in the Siemens Tia Portal.
P.S. password for safety PLC software is 123
Conclusion
The muting function is a very important safety function for when you need to interrupt the safety light curtain without triggering a safety condition that will probably stop your process.
 Again, safety PLC made the implementation of this function very easy due to the already built-in safety instructions that comply with the safety standards. If you would try to implement the same functionality with a normal PLC, you will need a large code to perform the same function as the MUT_P in safety PLCs.
  • Industrial Automation Solution
  • Automation Project Investment
  • PLC Functional Block Diagrams
  • Choose HMI for Your Application
  • Delta PLC in Industrial Automation
PLC Mixing Process with Adjustable Timer and Valve Control
PLC Basics – Manual Control, Closed Loop, ON-OFF with Hysteresis
Example of PLC Programming based on Logic Circuit
Siemens PLC programming: BCD, Integer, Double Integer, Real
PLC Selective Execution of the Application – Example Program
Example of Automated Guided Vehicle with PLC
Identify the Problem in the PLC Program
Types of Expressions in the SCL Language of the Tia Portal
Count the Number of Bottles in Packaging Carton PLC Logic
One Shot Rising and One Shot Falling Instructions in PLC
PLC Program with 2 Toggle Switches and 4 Motors
Shutdown Motors in Timed Operation PLC Program
Siemens Tia Portal Function Block
Function Blocks in PLC (FBs) – What You Need To Know?
CRA Module in Schneider PLC
CRA Module in Schneider PLC – Remote IO Adapter Module
Difference Between Wifi and Industrial Wireless
DCS Vs PLC
DCS versus PLC Architecture
What is Motor Jogging ?
Siemens PLC Write Protection
How to Protect Siemens PLC using Password?
6.6kV HV Induction motor Protection
PLC Retrofitting Project
What is a PLC Retrofitting Project? – Importance, Procedure
Rotating Magnetic Field Quiz
Working of Woodward Governor 505
Overview of Woodward Governor 505
Biosensors Questions & Answers
How to Create DFB in Schneider PLC? – Derived Function Block
PLC SCADA Water Pump
PLC Program for Controlling a Water Pump with 3 Power Sources
Mass Spectrometer Questions & Answers