How to Calculate Process Variable from 4-20mA current loop output of a field transmitter. Check the formula to find out Process variable (PV).
Â
Formula :
First Calculate equivalent Percentage from 4-20mA signal
Percentage = ( X * 6.25 ) – 25
Then calculate equivalent Process variable from percentage
Process Variable =  [ ( Percentage * ( URV – LRV ) /100 ) ] + LRV
Where,
X is 4-20mA signal
LRV is Lower Range Value
URV is Upper Range Value
Example :
A Temperature transmitter with a range of 0 to 250 deg C and its output is 15.5 mA. Calculate equivalent temperature value.
Lower Range Value, LRV = 0
Upper Range Value, URV = 250
Output Current in range of 4-20mA, X = 15.5 mA
Percentage = ( X * 6.25 ) – 25 = (15.5 * 6.25) – 25 = 71.875 %
Process Variable = [ { Percentage * ( URV – LRV ) } / 100 ] + LRV
Process Variable = [ ( 71.875 * 250 ) / 100 ] + 0 = 179.6875
Also you can use online Instrumentation Calculator for Automatic calculations. Click Here.
Articles You May Like :
Control System Setpoints & Alarms
Can you help please. This week I installed a vibration sensor with a 4-20mA output. At the data logger I burdened the loop with a 100 ohm precision resistor. Unfortunately the logger was setup for a 500 ohm resistor. The range should have been 0-20 mm/sec for .4 to 2v. Instead, because of the wrong resistor, the range was -5 to 0. Could you tell me please how to re-scale -5-0 to 0-20 ?
thank u sir for detail information
I don’t really know what 6.25 and 25 figures in the first formula.
But the easiest way is:
1) to subtract 4 from 15.5.
4-15.5= 11.5
2) Then divide 11.5 by 16 “Span” and multiply by 100.
(11.5\16)*100= 71.875%
Simple to remember and to do.
Same your formula in this article
25= 4/16 in your procedure
6.25 = 100/16 in your procedure
(X*6.25)-25 is simplest form of ur procedure