Reading: Facts About Orifice Flow Meters
Inst Tools > Blog > Flow Measurement > Facts About Orifice Flow Meters
The orifice plate is for flow measurement : an inexpensive yet effective primary sensing element. Study Orifice Flow Meters and Sensors.
Last updated: November 1, 2023 2:12 pm
Flow Measurement
7 Comments
25 Min Read
The orifice plate is for flow measurement: an inexpensive yet effective primary sensing element. The concept is disarmingly simple. Place a restriction in a pipe, then measure the resulting pressure drop (ΔP) across that restriction to infer the flow rate.
Orifice Flow Meters
You may have already seen a diagram such as the following, illustrating how an orifice plate works:
Orifice Flow Meter
Now, the really weird thing about measuring flow this way is that the resulting ΔP signal does not linearly correspond to flow rate. Double the flow rate, and the ΔP quadruples. Triple the flow rate and the ΔP increases by a factor of nine. To express this relationship mathematically:
Orifice Flow Meter Equation
In other words, differential pressure across an orifice plate (ΔP) is proportional to the square of the flow rate (Q2). To be more precise, we may include a coefficient (k) with a precise value that turns the proportionality into an equality:
Orifice Flow Meter Formula
Expressed in graphical form, the function looks like one-half of a parabola:
Orifice Flow Graph
To obtain a linear flow measurement signal from the differential pressure instrument’s output signal, we must “square root” that signal, either with a computer inside the transmitter, with a computer inside the receiving instrument, or a separate computing instrument (a “square root extractor”).
We may see mathematically how this yields a value for flow rate (Q), following from our original equation:
Orifice Flow Equation Solve
Note: Since we get to choose whatever k value we need to make this an equality, we don’t have to keep k inside the radicand, and so you will usually see the equation written as it is shown in the last step with k outside the radicand.
Students are taught that the differential pressure develops as a consequence of energy conservation in the flowing liquid stream. As the liquid enters a constriction, its velocity must increase to account for the same volumetric rate through a reduced area.
This results in kinetic energy increasing, which must be accompanied by a corresponding decrease in potential energy (i.e. pressure) to conserve total fluid energy.
Pressure measurements taken in a venturi pipe confirm this:
Venturi Flow Meter Principle
In all honesty, this did not make sense to me when I heard this (first time when i was a student). My “common sense” told me the fluid pressure would increase as it became crammed into the constriction, not decrease.
Even more, “common sense” told me that whatever pressure was lost through the constriction would never be regained, contrary to the pressure indication of the gauge furthest downstream.
Accepting this principle was an act of faith on my part, putting preconceived notions aside for something new. A leap of faith, however, is not the same as a leap in understanding. I believed what I was told, but I really didn’t understand why it was true.
The problem intensified when my teacher showed a more detailed flow equation. This new equation contained a term for fluid density (ρ):
Orifice Flow Theoretical Formula
What this equation showed us is that orifice plate flow measurement depended on density. If the fluid density changed, our instrument calibration would have to change in order to maintain good accuracy of measurement.
Something disturbed me about this equation, though, so I raised my hand. The subsequent exchange between my teacher and I went something like this:
Me: What about viscosity?
Teacher: What?
Me: Doesn’t fluid viscosity have an effect on flow measurement, just like density?
Teacher: You don’t see a variable for viscosity in the equation, do you?
Me: Well, no, but it’s got to have some effect on flow measurement!
Teacher: How come?
Me: Imagine clean water flowing through a venturi, or through the hole of an orifice plate. At a certain flow rate, a certain amount of ΔP will develop across the orifice.
Now imagine that same orifice flowing an equal rate of liquid honey: approximately the same density as water, but much thicker. Wouldn’t the increased “thickness,” or viscosity, of the honey result in more friction through the orifice, and thus more of a pressure drop than what the water would create?
Teacher: I’m sure viscosity has some effect, but it must be minimal since it isn’t in the equation.
Me: Then why is honey so hard to suck through a straw?
Teacher: Come again?
Me: A straw is a narrow pipe, similar to the throat of a venturi or the hole of an orifice, right? The difference in pressure between the suction in my mouth and the atmosphere is the ΔP across that orifice.
The result is flow through the straw. If viscosity is of such little effect, then why is liquid honey so much harder to suck through a straw than water? The pressure is the same, the density is about the same, then why isn’t the flow rate the same according to the equation you just gave us?
Teacher: In industry, we usually don’t measure fluids as thick as honey, and so it’s safe to ignore viscosity in the flow equation
My teacher’s smokescreen – that thick fluid flow streams were rare in industry – did nothing to alleviate my confusion. Despite my ignorance of the industrial world, I could very easily imagine liquids that were more viscous than water, honey or no honey.
Somewhere, somehow, someone had to be measuring the flow rate of such liquids, and there the effects of viscosity on orifice ΔP must be apparent. Surely my teacher knew this. But then why did the flow equation not have a variable for viscosity in it? How could this parameter be unimportant?
Like most students, though, I could see that arguing would get me nowhere and it was better for my grade to just go along with what the teacher said than to press for answers he couldn’t give. In other words, I swept my doubts under the carpet of “learning” and made a leap of faith.
After that, we studied different types of orifice plates, different types of pressure tap locations, and other inferential primary sensing elements (Pitot tubes, target meters, pipe elbows, etc.). They all worked on Bernoulli’s principle of decreased pressure through a restriction, and they all required square root extraction of the pressure signal to obtain a linearized flow measurement.
In fact, this became the sole criterion for determining whether or not we needed square root extraction on the signal: did the flow measurement originate from a differential pressure instrument? If so, then we needed to “square root” the signal. If not, we didn’t.
A neat and clean distinction, separating ΔP based flow measurements from all the others (magnetic, vortex shedding, Coriolis effect, thermal, etc.). Nice, clean, simple, neat, and only 95% correct, as I was to discover later.
Also Read: Basics of Flow measurement
Fast-forward fifteen years. I was now a teacher in a technical college, teaching Instrumentation to students just like myself a decade and a half ago. It was my first time preparing to teach flow measurement, and so I brushed up on my knowledge on a technical book (Liptak, Bela G) and found a type of flowmeter I had never seen or heard of before: the laminar flowmeter. As I read this section of the book, my jaw hit the floor.
Here was a differential-pressure-based flowmeter that was linear! That is, there was no square root extraction required at all to convert the ΔP measurement into a flow measurement. Furthermore, its operation was based on some weird equation called the Hagen- Poiseuille Law rather than Bernoulli’s Law.
Early in the section’s discussion of this flowmeter, a couple of paragraphs explained the meaning of something called Reynolds number of a flow stream, and how this was critically important to laminar flowmeters. Now, I had heard of Reynolds number before when I worked in industry, but I never knew what it meant.
All I knew is that it had something to do with the selection of flowmeter types: one must know the Reynolds number of a fluid before one could properly select which type of flow-measuring instrument to use in a particular application.
Little did I know that Reynolds number held the key to understanding my “honey-through-a-straw” question of years ago, as well as comprehending (not just believing) how orifice plates actually worked.
Laminar flowmeters were effective only for low Reynolds numbers, typically below 1200.Generally Reynolds numbers for typical orifice-plate flow streams were much greater (10000 or higher). Furthermore, the orifice plate section contained an insightful passage on the technical book which I will now quote here. Italicized words indicate my own emphasis, locating the exact points of my “Aha!” moments:
The basic equations of flow assume that the velocity of flow is uniform across a given cross-section. In practice, flow velocity at any cross section approaches zero in the boundary layer adjacent to the pipe wall, and varies across the diameter.
This flow velocity profile has a significant effect on the relationship between flow velocity and pressure difference developed in a head meter. In 1883, Sir Osborne Reynolds, an English scientist, presented a paper before the Royal Society, proposing a single, dimensionless ratio now known as Reynolds number, as a criterion to describe this phenomenon. This number, Re, is expressed as
Reynolds number
where V is velocity, D is diameter, ρ is density, and μ is absolute viscosity.
Reynolds number expresses the ratio of inertial forces to viscous forces. At a very low Reynolds number, viscous forces predominate, and the inertial forces have little effect. Pressure difference approaches direct proportionality to average flow velocity and to viscosity. At high Reynolds numbers, inertial forces predominate and viscous drag effects become negligible.
What the above paragraph is saying is that for slow-moving, viscous fluids (such as honey in a straw), the forces of friction (fluid “dragging” against the pipe walls) are far greater than the forces of inertia (fluid momentum). This means that the pressure difference required to move such a fluid through a pipe primarily works to overcome the friction of that fluid against the walls of the pipe.
For most industrial flows, where the flow velocities are fast and the fluids have little viscosity (like clean water), flow through an orifice plate is assumed to be frictionless. Thus, the pressure dropped across a constriction is not the result of friction between the fluid and the pipe, but rather it is a consequence of having to accelerate the fluid from a low velocity to a high velocity through the narrow orifice.
My mistake, years ago, was in assuming that water flowing through an orifice generated substantial friction, and that this is what created the ΔP across an orifice plate. This is what my “common sense” told me. In my mind, I imagined the water having to rub past the walls of the pipe, past the face of the orifice plate, and through the constriction of the orifice at a very high speed, in order to make it through to the other side.
I memorized what my teacher told us about energy exchange and how pressure had to drop as velocity increased, but I never really internalized it because I still held to my faulty assumption of friction being the dominant mechanism of pressure drop in an orifice plate.
In other words, while I could parrot the doctrine of kinetic and potential energy exchange, I was still thinking in terms of friction, which is a totally different phenomenon. The difference between these two phenomena is the difference between energy exchanged and energy dissipated.
To use an electrical analogy, it is the difference between reactance (X) and resistance (R). Incidentally, many electronics students experience the same confusion when they study reactance, mistakenly thinking it is the same thing as resistance where in reality it is quite different in terms of energy, but that is a subject for another essay!
In a frictionless flow stream, fluid pressure decreases as fluid velocity increases in order to conserve energy. Another way to think of this is that a pressure differential must develop in order to provide the “push” needed to accelerate the fluid from a low speed to a high speed.
Conversely, as the fluid slows back down after having passed through the constriction, a reverse pressure differential must develop in order to provide the “push” needed for that deceleration:
Venturi Flow Theory
A moving mass does not simply slow down on its own! There must be some opposing force to decelerate a mass from a high speed to a low speed. This is where the pressure recovery downstream of the orifice plate comes from.
If the pressure differential across an orifice plate originated primarily from friction, as I mistakenly assumed when I first learned about orifice plates, then there would be no reason for the pressure to ever recover downstream of the constriction. The presence of friction means energy lost, not energy exchanged.
Although both inertia and friction are capable of creating pressure drops, the lasting effects of these two different phenomena are definitely not the same.
There is a quadratic (“square”) relationship between velocity and differential pressure precisely because there is a quadratic relationship between velocity and kinetic energy as all first-quarter physics students learn (Ek = 1/2mv2).
This is why ΔP increases with the square of flow rate (Q2) and why we must “square-root” the ΔP signal to obtain a flow measurement. This is also why fluid density is so important in the orifice-plate flow equation.
The denser a fluid is, the more work will be required to accelerate it through a constriction, resulting in greater ΔP, all other conditions being equal:
This equation is only accurate, however, when fluid friction is negligible: when the viscosity of the fluid is so low and/or its speed is so high that the effects of potential and kinetic energy exchange completely overshadow the effects of friction against the pipe walls and against the orifice plate.
This is indeed the case for most industrial flow applications, and so this is what students first study as they learn how flow is measured. Unfortunately, this is often the only equation two-year Instrumentation students study with regard to flow measurement.
In situations where Reynolds number is low, fluid friction becomes the dominant factor and the standard “orifice plate” equation no longer applies. Here, the ΔP generated by a viscous fluid moving through a pipe really does depend primarily on how “thick” the fluid is.
And, just like electrons moving through a resistor in an electric circuit, the pressure drop across the area of friction is directly proportional to the rate of flow (ΔP ∝ Q for fluids, V ∝ I for electrons).
This is why laminar flowmeters – which work only when Reynolds number is low – yield a nice linear relationship between ΔP and flow rate and therefore do not require square root extraction of the ΔP signal.
These flowmeters do, however, require temperature compensation (and even temperature control in some cases) because flow measurement accuracy depends on fluid viscosity, and fluid viscosity varies according to temperature. The Hagen-Poiseuille equation describing flow rate and differential pressure for laminar flow (low Re) is shown here for comparison:
Where,
Q = Flow rate (gallons per minute)
k = Unit conversion factor = 7.86 ×105
ΔP = Pressure drop (inches of water column)
D = Pipe diameter (inches)
μ = Liquid viscosity (centipoise) – this is a temperature-dependent variable!
L = Length of pipe section (inches)
Note that if the pipe dimensions and fluid viscosity are held constant, the relationship between flow and differential pressure is a direct proportion:
Laminar Flow Meter Equation
In reality, there is no such thing as a frictionless flow (excepting super fluidic cases such as helium II which are well outside the bounds of normal experience), just as there is no such thing as a massless flow (no inertia).
In normal applications there will always be both effects at work. By not considering fluid friction for high Reynolds numbers and not considering fluid density for low Reynolds numbers, engineers draw simplified models of reality which allow us to more easily measure fluid flow.
Orifice Meter Equation
As in so many other areas of study, we exchange accuracy for simplicity, precision for convenience. Problems arise when we forget that we’ve made this Faustian exchange and wander into areas where our simplistic models are no longer reasonable.
Also Read: Important Factors in Flow Measurement
Perhaps the most practical upshot of all this for students of Instrumentation is to realize exactly why and how orifice plates work. Bernoulli’s equation does not include any considerations of friction. To the contrary, we must assume the fluid to be completely frictionless in order for the concept to make sense.
This explains several things:
There is pressure recovery downstream of an orifice: most of the pressure lost at the vena contracta is regained further on downstream as the fluid decelerates to its original (slow) speed.
Permanent pressure drop will occur only where there is energy lost through the constriction, such as in cases where fluid friction is substantial. Where the fluid is frictionless there is no mechanism in an orifice to dissipate energy, and so with no energy lost there must be full pressure recovery as the fluid returns to its original speed.
Pressure tap location makes a difference: to ensure that the downstream tap is actually sensing the pressure at a point where the fluid is moving significantly faster than upstream (the “vena contracta”), and not just anywhere downstream of the orifice. If the pressure drop were due to friction alone, it would be permanent and the downstream tap location would not be as critical.
Standard orifice plates have knife-edges on their upstream sides: to minimize contact area (friction points) with the high-speed flow.
Care must be taken to ensure Reynolds number is high enough to permit the use of an orifice plate: if not, the linear Q/ΔP relationship for viscous flow will assert itself along with the quadratic potential/kinetic energy relationship, causing the overall Q/ΔP relationship to be polynomial rather than purely quadratic, and thereby corrupting the measurement accuracy.
Sufficient upstream pipe length is needed to condition flow for orifice plate measurement, not to make it “laminar” as is popularly (and wrongly) believed, but to allow natural turbulence to “flatten” the flow profile for uniform velocity. Laminar flow is something that only happens when viscous forces overshadow inertial forces (e.g. flow at low Reynolds numbers), and is totally different from the fully developed turbulent flow that orifice plates need for accurate measurement.
In a more general sense, the lesson we should learn here is that blind faith is no substitute for understanding, and that a sense of confusion or disagreement during the learning process is a sign of one or more misconceptions in need of correction. If you find yourself disagreeing with what you are being taught, either you are making a mistake and/or your teacher is.
Pursuing your questions to their logical end is the key to discovery, while making a leap of faith (simply believing what you are told) is an act of avoidance: escaping the discomfort of confusion and uncertainty at the expense of a deeper learning experience. This is an exchange no student should ever feel they must make.
Author : Tony R. Kuphaldt – Creative Commons Attribution 4.0 License
  • Types of Flow Meters
  • Variable Area Flow Meter
  • Coriolis Mass Flow meter
  • Instrumentation Questions
  • Industrial Automation Questions
What is the Purpose of Orifice Plate Drain Hole and Vent Hole?
What is a Turbine Flow Meter?
Hot Wire Anemometer Principle and Types
What is a Thermal Flow Meter?
Coriolis Flowmeter Advantages and Limitations
7 Comments
  • Jee says:
    December 14, 2017 at 6:20 pm
    Fantastic explanation thank you so much
  • Prasanth says:
    September 11, 2018 at 9:01 pm
    Please clarify how the pressure pattern will be for reverse flow across classic Venturi and normal orifice.
  • yassine says:
    October 7, 2018 at 1:47 am
    Hello,
    when using smart differential pressure transmitter, do we need to calculate the coefficent K to display the flow at the scada?
  • Ahammed shibili y says:
    June 14, 2019 at 9:56 pm
    Thanks for the info
  • Nuri Ghanem says:
    July 26, 2019 at 5:43 pm
    Hello …. Please I want to know how level transmitter measure level in boiler drum? (Mathematical equation for diff – pressure is required ) .
  • GOWARDHAN KISHANLAL AGRAWAL says:
    December 25, 2019 at 5:00 pm
    Absolute class knowledge
  • Lakhvinder says:
    September 7, 2022 at 4:52 pm
    I appreciate the explanation of the concept of pressure drop across a restriction.
Piston Flow Meters Working Principle with Animation
Phase Watcher Multiphase Flow Meter (MPFM) Procedure
Thermal Dispersion Flow Switch Working Principle
Pressure based Flow Meters
Reasons to Calibrate Different Types of Flow Meters
Square-Root in DCS or Flow Transmitter?
Rotameter Working Principle and Animation
What is Differential Pressure Flow Meter?
multiphase-flowmeter-working-principle
What are Multiphase Flow Meters? – Working Principle, Advantages
Weigh feeders Principle
What is a Weigh Feeder?
L2F insertion-style flowmeter
Optical Flow Meter Principle
Orifice Flow Meter With DP Transmitter
What is an Orifice Meter?
Orifice Taps
Orifice Plate Tapping – Orifice Plate Taps
Magnetic Flow Meter Corrosion Effects
Impulse line - Purpose & Tapping Point Location
Impulse Line – Purpose & Tapping Point Location
Flow Standards
Flow Standards
Card Failures in Automation Panels
Automation Panel Electronic Cards Failure investigation
STL Programming - SET, RESET, ASSIGN
STL Programming – SET, RESET, ASSIGN
What is Rapid Spanning Tree Protocol
What is Rapid Spanning Tree Protocol? – RSTP Network
Control Valve in PlantPAx Project
Configuration of Control Valve in Studio 5000
Electrical Machines MCQ Series 4
What is a Current Transformer
What is a Current Transformer?
Installation of a Control Valve
How to Install a Control Valve?
Differences between No-load Supply Current and Load Current