Inst ToolsInst ToolsInst Tools
  • Courses
  • Automation
    • PLC
    • Control System
    • Safety System
    • Communication
    • Fire & Gas System
  • Instrumentation
    • Design
    • Pressure
    • Temperature
    • Flow
    • Level
    • Vibration
    • Analyzer
    • Control Valve
    • Switch
    • Calibration
    • Erection & Commissioning
  • Interview
    • Instrumentation
    • Electrical
    • Electronics
    • Practical
  • Q&A
    • Instrumentation
    • Control System
    • Electrical
    • Electronics
    • Analog Electronics
    • Digital Electronics
    • Power Electronics
    • Microprocessor
Search
  • Books
  • Software
  • Projects
  • Process
  • Tools
  • Basics
  • Formula
  • Power Plant
  • Root Cause Analysis
  • Electrical Basics
  • Animation
  • Standards
  • 4-20 mA Course
  • Siemens PLC Course
Reading: DP type Flow Transmitter Preventive Maintenance and Calibration
Share
Notification Show More
Font ResizerAa
Inst ToolsInst Tools
Font ResizerAa
  • Courses
  • Design
  • PLC
  • Interview
  • Control System
Search
  • Courses
  • Automation
    • PLC
    • Control System
    • Safety System
    • Communication
    • Fire & Gas System
  • Instrumentation
    • Design
    • Pressure
    • Temperature
    • Flow
    • Level
    • Vibration
    • Analyzer
    • Control Valve
    • Switch
    • Calibration
    • Erection & Commissioning
  • Interview
    • Instrumentation
    • Electrical
    • Electronics
    • Practical
  • Q&A
    • Instrumentation
    • Control System
    • Electrical
    • Electronics
    • Analog Electronics
    • Digital Electronics
    • Power Electronics
    • Microprocessor
Follow US
All rights reserved. Reproduction in whole or in part without written permission is prohibited.
Inst Tools > Blog > Calibration > DP type Flow Transmitter Preventive Maintenance and Calibration

DP type Flow Transmitter Preventive Maintenance and Calibration

In this article, you will learn the DP type flow transmitter preventive maintenance (PM) activity and calibration procedure in the field.

Last updated: February 21, 2023 3:01 pm
Editorial Staff
Calibration Flow Measurement
1 Comment
Share
7 Min Read
SHARE

In this article, you will learn the DP type flow transmitter preventive maintenance (PM) activity and calibration procedure in the field.

Contents
Tools ListDP type Flow Transmitter Preventive MaintenanceFlow Transmitter PM Checklist

Before starting the maintenance activity we have to follow the below steps.

First, you have to take the proper work permit.

Tools List

Gather the required tools and instruments for the PM job.

  • Digital Multimeter
  • Pressure Calibrator
  • HART 375/475 Communicator
  • Other Tools

We must make sure that the required instruments must have valid calibration before using them for our PM job. Make sure the instruments are properly charged (like the HART communicator).

We have to use a calibration sticker at the end of our PM activity. So get one new label, which is shown in the below image.

calibration sticker

We have to use proper PPE for the job. So check all the required PPE available or not before starting the job.

Check the datasheet of the DP type flow transmitter and note down the ranges. Here we need two range values. One is in mmH2O which is the DP range and the second one is the actual flow range which is in m3/hr range (or any other units)

Take out the range of the transmitter from the data sheet of the DP type Flow transmitter. Here you will see two ranges. One is in mmH2O which is the DP range. Another is the m3/hr range which is the output flow range.

DP type Flow Transmitter Preventive Maintenance

DP type Flow Transmitter Calibration
DP Flow transmitter maintenance & calibration in the field
  1. Take appropriate work permit and take necessary approvals.
  2. Bypass the interlock if the DP type Flow transmitter is having any interlocks (Always take a bypass approval from operations and fill the Interlock Bypass Form).
  3. Instrument engineer should check whether the square root function is present in the field transmitter or in the PLC or DCS system.
  4. Verify the flow transmitter tag number. You should always ask the value shown by DP type Flow transmitter on the DCS/SCADA/PLC and confirm the value in field. This is a double confirmation for identifying the proper tag. (optional)
  5. Note down the value shown by DP type Flow transmitter before starting the PM job.
  6. Ask the operation engineer to arrange for the isolation of the DP type Flow transmitter through a process isolation valve (if required).
  7. Open the back cover of the DP type Flow transmitter and check the connections.
  8. Note down all the cable connections. So that it will be easy to restore the connections after completing the PM.
  9. Check the input supply voltage.
  10. Connect HART 375/475 communicator with the DP type Flow transmitter.
  11. Open the equalization valve on the manifold and check the zero reading of the DP type Flow transmitter.
  12. Now properly drain the fluid (for hazardous service close drain is required).
  13. Connect the pressure calibrator or pressure source to the HP tapping point of the flow transmitter.
  14. As per the range of the DP type Flow transmitter datasheet, set the required pressure on the pressure calibrator and feed it to the DP type Flow transmitter.
  15. Now apply respective pressure and note down the output of the transmitter (confirm in field display as well as from control room DCS/SCADA/PLC).
  16. Repeat the above step for different calibration points. The general rule is to apply the input pressure in terms of 0%, 25%, 50%, 75%, and 100%.
  17. We have to do the calibration of DP type flow transmitter in increasing order like from 0% to 100% by applying equivalent pressure values as per the range and also in reverse order from 100% to 0%.
% of RangeDPm3/hrValue on field displayValue on DCS/SCADA/PLC
000  
2512501000  
5025001414  
7537501732  
10050002000  
7537501732  
5025001414  
2512501000  
000  

(Above table filled for DP range of 0 to 5000 mmH2O and flow rate of 0 to 2000 m3/hr)

We have to check for any leakages on the impulse tubes using snoop liquid leak detectors or with any other solution.

DP type Flow Transmitter Preventive Maintenance
  1. If the DP type Flow transmitter generates the output with an error less than the maximum permissible error, then both are ok. If the transmitter is having errors more than the maximum permissible error, then calibrate the transmitter. And after calibration, recheck all the values.
  2. Restore all the original connections. Take transmitter in line.
  3. Close the cover of the DP type Flow transmitter and apply monsoon tape or silastic whichever is applicable.
  4. After connections, match the values with the values which were taken before the job and ask the operation engineer that is it correct or not (Because values change if the process is ongoing). If found not ok, then recheck the connections.
  5. Apply a calibration sticker on the DP type Flow transmitter with the appropriate calibration due date.
  6. Clean the DP type Flow transmitter.
  7. Restore the interlocks and also ask the operation engineer to put the control loop again in auto mode if taken in manual mode.
  8. Close the work permit.
  9. Fill up the calibration record for the DP type flow transmitter.

Flow Transmitter PM Checklist

PM checklist to be filled:

  1. Tag number of Instrument
  2. Order Number
  3. Permit Number
  4. Range of Instrument
  5. Square root functionality found in (Field or System)
  6. Date of Calibration
  7. Value before doing Job
  8. Value after doing Job
  9. Transmitter Make & Model number
  10. Test and Calibration Instrument used
  11. Test Result
  12. Technicians involved in Job
  13. Engineers involved in Job

Read Next:

  • Flow Standards
  • Turbine Flow Meter Verification
  • Practical Calibration Standard
  • Digital Control Valve Principle
  • Temperature Bath Calibration
Don't Miss Our Updates
Be the first to get exclusive content straight to your email.
We promise not to spam you. You can unsubscribe at any time.
Invalid email address
You've successfully subscribed !

Continue Reading

Error sources creating uncertainty in Calibration
Smart Transmitters LRV & URV
Basics of Venturi Flow Meter
Flow Transmitter Rangeability
Calibration of Gas Detectors
Basics of Flow Measurement
Share This Article
Facebook Whatsapp Whatsapp LinkedIn Copy Link
Share
1 Comment
  • V.Jagdish Prakash says:
    June 4, 2022 at 5:29 pm

    Good to always check out the P&ID to get a feel of what the Instrument is doing there in the process;

    1. Alarms and shutdown functions need to be taken care of reference to the C&E chart.
    2. If it is in a control loop, the controller needs to be taken into manual control.

    The above needs to be discussed with the operations and ONLY IF they agree do you need to prepare a PTW.
    Or else all the time is wasted that day.

    Usually, the above study is done the previous day when planning for the next day’s jobs.

    Reply

Leave a Reply Cancel reply

Your email address will not be published. Required fields are marked *

Stay Connected

128.3kFollowersLike
69.1kFollowersFollow
210kSubscribersSubscribe
38kFollowersFollow

Categories

Explore More

What is an Insertion Flow Meter? – Types, Principle, Advantages
DP Diaphragm Capillary Seal Level instrument Calibration Procedure
What is a Weigh Feeder?
What is a Paddle Wheel Flow Meter?
Flow Switch : What is it? – Applications
Ultrasonic Flow Meters Animation
Pressure Safety Valve Leak Test Procedure (PSV Testing)
All About Turbine Meters

Keep Learning

Differential Pressure (DP) Flow Meters Range Calculation Methods

Differential Pressure (DP) Flow Meters Range Calculation Methods

Difference between Calibration and Ranging

Difference between Calibration and Ranging

Coriolis Mass Flowmeter Principle

Coriolis Mass Flow Sensor Theory

How to Calibrate Load Cells

How to Calibrate Load Cells in Weighing Applications?

calibration potentiometer for simulating the millivoltage output

Temperature Standards

What is a K Factor

Flow Meter K-factor and Calculations

How to Test a Pressure Gauge

How to Test a Pressure Gauge

difference between invasive and non-invasive and intrusive and non-intrusive

Difference between Invasive, Non-invasive, Intrusive & Non-intrusive

Learn More

Steam Letdown Station Problems

Steam Letdown Station Problems and their Solutions

Circuit Control Devices Multiple Choice Questions

Circuit Control Devices Multiple Choice Questions & Answers

Siemens Industrial Laptop (Simatic Field PG)

Connect to the Siemens S7 PLC

PLC Program for 2 Push buttons to Control 1 Output

PLC Program for 2 Push buttons to Control 1 Output

Control System

The need for automatic controls

Circuit Diagram of Displacement Transducer

What is a Displacement Transducer? – Types and Advantages

Vortex flow meter Bluff Body

Types of Vortex Flow Meter Sensors

kirchhoffs-voltage-law

What is Kirchhoff’s Voltage Law

Menu

  • About
  • Privacy Policy
  • Copyright

Quick Links

  • Learn PLC
  • Helping Hand
  • Part Time Job

YouTube Subscribe

Follow US
All rights reserved. Reproduction in whole or in part without written permission is prohibited.
Welcome Back!

Sign in to your account

Username or Email Address
Password

Lost your password?