Inst ToolsInst ToolsInst Tools
  • Courses
  • Automation
    • PLC
    • Control System
    • Safety System
    • Communication
    • Fire & Gas System
  • Instrumentation
    • Design
    • Pressure
    • Temperature
    • Flow
    • Level
    • Vibration
    • Analyzer
    • Control Valve
    • Switch
    • Calibration
    • Erection & Commissioning
  • Interview
    • Instrumentation
    • Electrical
    • Electronics
    • Practical
  • Q&A
    • Instrumentation
    • Control System
    • Electrical
    • Electronics
    • Analog Electronics
    • Digital Electronics
    • Power Electronics
    • Microprocessor
  • Request
Search
  • Books
  • Software
  • Projects
  • Process
  • Tools
  • Basics
  • Formula
  • Power Plant
  • Root Cause Analysis
  • Electrical Basics
  • Animation
  • Standards
  • 4-20 mA Course
  • Siemens PLC Course
Reading: Control Valve Relation between Cv and Kv
Share
Font ResizerAa
Inst ToolsInst Tools
Font ResizerAa
  • Courses
  • Design
  • PLC
  • Interview
  • Control System
Search
  • Courses
  • Automation
    • PLC
    • Control System
    • Safety System
    • Communication
    • Fire & Gas System
  • Instrumentation
    • Design
    • Pressure
    • Temperature
    • Flow
    • Level
    • Vibration
    • Analyzer
    • Control Valve
    • Switch
    • Calibration
    • Erection & Commissioning
  • Interview
    • Instrumentation
    • Electrical
    • Electronics
    • Practical
  • Q&A
    • Instrumentation
    • Control System
    • Electrical
    • Electronics
    • Analog Electronics
    • Digital Electronics
    • Power Electronics
    • Microprocessor
  • Request
Follow US
All rights reserved. Reproduction in whole or in part without written permission is prohibited.
Inst Tools > Blog > Control Valves > Control Valve Relation between Cv and Kv

Control Valve Relation between Cv and Kv

Last updated: September 28, 2022 2:43 pm
R Jagan Mohan Rao
Control Valves
No Comments
Share
5 Min Read
SHARE

Control Valve Relation between Cv and Kv

Control Valve Relation between Cv and Kv

Contents
Control Valve Relation between Cv and KvHow do we get value 1.156 (Conversion Factor) in formula Cv = 1.156Kv or Cv= 1.156×Q×sqrt (G/delta P). Please explain.Answer:Example :

How do we get value 1.156 (Conversion Factor) in formula Cv = 1.156Kv or Cv= 1.156×Q×sqrt (G/delta P). Please explain.

Answer:

For measuring the valve capacity of control valves, the coefficient Cv or its metric equivalent Kv is adopted.

The Valve Coefficient (Cv – in Imperial unit) – the number of US GALLON PER MINUTE of water at 60 °F  that will flow through a valve at specific opening with a pressure drop of 1 psi across the valve.

The flow factor (Kv – in Metric unit) – the amount of water that will flow in m3/hr. with a temperature range 5 to 30 °C and pressure drop of 1 bar.

The relationship between Cv and Kv is

Cv = 1.156 * Kv.    OR

Kv = 0.864 * Cv

The flow rate for a liquid   Q = Cv * Sq. Root of ( ΔP/SG)

 Q = Flow in US GPM.

Cv = Flow Coefficient of control valve

ΔP = Differential pressure

SG = Specific Gravity of fluid (reference against water at 60 °F)

Now we discuss about how we get the conversion factor of 1.156 in the formula, Cv = 1.156Kv

Unit conversions from Imperial to Metric (vice versa)

1 US gpm = 0.227125 m3/hr  and 1 m3/hr = 4.4028812454 US GPM

1 psi = 0.06894757 bar  and 1 bar = 14.503773773 psi

60 deg F = 15.5 deg C

Conversion of units for Cv to Kv

Cv = 1 m3/hr * sqrt (1/1bar)

Cv  =  4.4028812454 US GPM * sqrt (1/14.503773773 psi)

Cv  = 4.4028812454 US GPM * 0.2625786985 *1/psi

Cv = 1.1561 US GPM /psi

Cv = 1.156 Kv

 Conversion of units for Kv to Cv

Kv = 1Us gpm *sqrt (1/1psi)

Kv = 0.227125 m3/hr * sqrt (1/0.06894757 bar)

Kv = 0.2271 * 3.808 * m3/ hr

Kv = 0.864 m3/ hr

Kv = 0.864 Cv

At a particular percentage of opening of valve giving Cv = 1 will pass 1US GPM ( at 60 °F) and a pressure differential of 1 psi upstream and downstream across the valve.

For the same pressure conditions, if we increase the valve opening to create Cv = 10, It will pass 10 US GPM provided 1 psi pressure drop across the valve (remains same).

Q = 1/1.156 Cv * Sq. Root of ( Δ P/SG)

Q = 0.865 Cv * Sq. Root of ( Δ P/SG)

Q = Flow in m3/hr.,

Δ P = 1 bar,

SG = 1 for water at 15°C (Equivalent of 60°C Imperial units)

In metric units, the same valve with Cv = 1 pass 0.864 m3/hr. (at 15 °C) with a delta P of 1 bar across the valve.

 Summary :

For any specific valve opening with an equivalent pressure drop and equivalent temperature, by applying multiplication factor we get equal flows in both Imperial and metric units.

Example :

Simple Example of conversion factor between two different mass units is:

1 Kg = 2.2 * Pounds

In a simple balance consisting two pans – 1 Kg of Weight in one pan and in second pan need to put 2.2 Times Pound weight, then only two pans stay equal in a simple balance. (Under same environmental conditions)

Kg = Kilogram is a Metric unit

Pound is Imperial unit.

10 Kg = 2.2 * 10 Pounds = 22 Pounds.

100 Kg = 2.2 * 100 Pounds = 220 Pounds

Same is the relation between Cv and Kv.

Read Next:

  • Swing Check Valves
  • Control Valve Characteristics
  • Thermostatic valves Principle
  • Different Valve Types
  • Valves Leakage Classification
Don't Miss Our Updates
Be the first to get exclusive content straight to your email.
We promise not to spam you. You can unsubscribe at any time.
Invalid email address
You've successfully subscribed !

Continue Reading

Erratic Stroking Control Valves Delaying the Shutdown Plant Restart
Control Valve Positioner Working Principle
Solenoid Valve’s Energized or De-energized State ?
Types of Control Valves Noise
Air Cylinder Consumption Calculation for Control Valves
How to Do Maintenance of Control Valve Which is Stuck in Field?
Share This Article
Facebook Whatsapp Whatsapp LinkedIn Copy Link
Share
Leave a Comment

Leave a Reply Cancel reply

Your email address will not be published. Required fields are marked *

Stay Connected

128.3kFollowersLike
69.1kFollowersFollow
210kSubscribersSubscribe
38kFollowersFollow

Categories

Explore More

Quick Exhaust and Air Operated Valves in Instrumentation Circuit
Spring and Diaphragm Pneumatic Actuators
When to choose Full Bore Valve or Reduced Bore Valve ?
Problem with Choked Control Valve with Whisper Trim Cage
Classification of Control Valves
Common Terms Used in Control Valves
Types of Pneumatic Actuators Animation
What is Instrument Air Manifold ?

Keep Learning

valve trim

Valve Actuator Bench Set

Typical schematic of Butterfly valve

Automated Block Valve (ABV)

Needle Valve Schematic

How Needle Valve Works ?

Inspection of Control Valves

Inspection and Test Requirement of Control Valves

What is a Hydraulic Valve

What is a Hydraulic Valve? and their Types

Internal Parts of Globe Valve

How to Choose a Control Valve?

Blowdown Valve (BDV) and Shutdown Valve (SDV)

Difference between Blowdown Valve (BDV) and Shutdown Valve (SDV) ?

Opposite Acting Valves

What is Split Range Control Loop ?

Learn More

Single Position Calibration of Temperature Bath

Single Position Calibration of Temperature Bath

Sampling Circuits Objective Questions

Sampling Circuits Objective Questions

Sensors Used in Automotive Vehicles

Different Types of Sensors used in Automotive Vehicles

control valve sequencing

Control Valve Sequence Methods

Process Control Instrumentation Objective Questions

Process Control & Instrumentation Objective Questions – Set 5

Electrical Power Distribution

Electrical Power Distribution

Thermocouple cold junction compensation

Why Thermocouple Reference Junction Compensation Required ?

Automatic Car Door Simulation

Automatic Door Operation PLC Programming and Simulation

Menu

  • About
  • Privacy Policy
  • Copyright

Quick Links

  • Learn PLC
  • Helping Hand
  • Part Time Job

YouTube Subscribe

Follow US
All rights reserved. Reproduction in whole or in part without written permission is prohibited.
Welcome Back!

Sign in to your account

Username or Email Address
Password

Lost your password?