Reading: Closed Tank Remote Seal Capillary type DP Transmitter
Inst Tools > Blog > Formulas > Closed Tank Remote Seal Capillary type DP Transmitter
Last updated: April 19, 2019 4:15 pm
Formulas Level Measurement Pressure Measurement
4 Comments
A remote seal capillary type dp transmitter which is mounted on a closed tank. distance between both flanges is 1835 mm and density of fluid in tank is 1.15, transmitter is mounted below the high side flange. please give the calculation of URV and LRV values.
Answer
You need to know the capillary fill fluid specific gravity to make the calculation.
Calculating LRV and URV for dual remote seals on a closed tank
Assuming
  • the minimum level is 4mA
  • the maximum level is 20mA
  • high side port is at the bottom tap
  • low side port is at the top tap
The ranging of a remote seal transmitter is not guesswork, it is an arithmetic (multiplication and subtraction) calculation requiring four or five values that are specific to the application:
  • specific gravity (SG) of remote seal fill fluid (SGf value)
  • specific gravity of the process liquid (SGp value)
  • Elevation distance between taps, the lower seal (high side) and upper seal (low side) (d value)
  • distance between bottom tap and maximum level height (what 20mA represents) (b value)
  • distance between bottom tap and minimum level (what 4mA represents) (a value)
It does not matter whether the transmitter is at, below or above the bottom tap when dual remote seals are used. The LRV and URV are the same for all three conditions.
Refer to the illustration:
LRV = (SGp * a) – (SGf * d)
URV = (SGp * b) – (SGf * d)
In many cases, the lower level (4mA) is where the bottom tap is, so value a = zero.
When a = 0, then (SGp * 0) = 0.
Hence, LRV = 0 – (SGf * d), which results in a negative value.
That’s correct. Do not be surprised if the LRV is a negative value. It frequently is negative, as well as the URV.
Remote seal transmitters assembled and filled by the manufacturer will have a part number that includes a code for the fill fluid and usually the tag will show the fill fluid too.
Commonly used capillary fill fluid specific gravities range from 0.26 for glycerin to 1.97 for Halocarbon. Guessing at the fill fluid can lead to large and significant errors. Determine the actual fill fluid.
Example: Dual remote seals on closed tank
a = 0 (bottom tap is minimum level point)
b = 108 inches (maximum liquid level)
d = 120 inches (elevation distance between the high and low taps)
SGp = tank fluid SG = 0.95
SGf = fill fluid SG = 0.934
1) Calculate the LRV
At min level (empty), there is 0 process liquid pressure on the high side, so SGp = 0.
A = 0, so (SGp * a) = 0″
The fill fluid exerts a pressure of (SGf * d) or (0.923 * 120″) on the low side
(SGf * d) = 0.934 * 120″ = 112.08″
LRV = 0″ – 112.08″ = -112.08″
LRV = -112.08
2) Calculate the URV
At the maximum fluid level, there is a pressure of (SGp * b), or (0.95 * 108″) on the high side.
(SGp * b) = 0.95 * 108″ = 102.6″
102.6″ – 112.08″ = – 9.48″
URV = -9.48
3) Transmitter’s range
LRV = 4mA = -112.80″ w.c.
URV = 20mA = -9.48″ w.c.
The transmitter’s range is -112.08″ to -9.48″ w.c., a span of 102.6″ w.c., which is the head pressure of 108″ of liquid with a SG of 0.95.
Articles You May Like :
Remote Seals Configuration
Guided Wave Radar Level Sensor
RF Admittance Level Transmitter
Capacitive Level Switch Principle
Level Troll working principle
Differential Pressure Gauge Principle
Effect of Temperature & Pressure on Level Measurement
Level Gauge Interface & Temperature Problems
How can we use a DP Flow Transmitter for Level Measurement
Closed tank DP Level Transmitter with wet leg Zero elevation Calibration
4 Comments
  • Azfar Yusof says:
    May 3, 2016 at 3:01 pm
    Hai there, what happen if the transmitter located higher than top tapping (low tapping)? Can you explain the calculation?
    • Gourav Sourav says:
      January 27, 2024 at 4:58 pm
  • Jigar Rana says:
    December 19, 2017 at 6:21 am
    sir, how can we define the Distance of maximum liquid level (B)?
    • Jigar Rana says:
      December 19, 2017 at 6:27 am
      Hello sir, how can i define the minimum level (a) , maximum level (b) and also at which point i have to take Hish side and low side tapping.
      Give me reply sir As soon as Possible
Standard 4 to 20 mA Conversion Formula
Relationship between Temperature Scales
Point Level Detection Working Principle
Fine Wire Strain Gauge Principle
Float Type Level Indicator Principle
Probe Type GWR Level Transmitter Working Animation
Purpose of Stop in a Pressure Measuring Instrument
Pressure Transmitter Parts
Differential Pressure Transmitter Working Principle
Comparison of Pressure Instruments - Industrial Instrumentation
Comparison of Pressure Instruments – Industrial Instrumentation
How is pressure drop calculated through a valve?
How is Pressure Drop Calculated through a Valve ?
Ultrasonic Level Switch Working Animation
Ultrasonic Level Switch Working Principle
Closed tank DP Level Transmitter with wet leg elevation zero remote mount Calibration
level gauge
Basics of Sight Glass Level Gauge
Well Manometer Principle
Formula for Linear mA to Square root mA conversion
AC Generator Nameplate Ratings
working-of-pnp-transistor
Working of NPN Transistor
What is a Line Choke or Reactor in a VFD
What is a Line Choke or Reactor in a VFD?
4-wire RTD Bridge Circuit
Why we use Wheatstone bridge in RTD?
Understanding Protection Relays
Understanding Protection Relays – 50, 50N, 51, 51N
RTD-standards
How to calculate the tolerance of a RTD sensor
Historical Scada graph
Configuration of InTouch Scada Trends
Calculate Power in Parallel RL Circuit