Reading: Calculate the Thermocouple’s Measurement Junction Temperature
Inst Tools > Blog > Practical Questions > Calculate the Thermocouple’s Measurement Junction Temperature
Last updated: June 6, 2018 9:47 am
Practical Questions
2 Min Read
Type K thermocouple
A type K thermocouple is inserted into a process, with a digital multimeter connected to its terminals.
The ambient temperature at the DMM’s test lead connections is 84 oF.
Calculate the thermocouple’s measurement junction temperature at the following millivolt measurements (rounding to the nearest degree Fahrenheit):
  • 2.55 mV ; T = ______ deg F
  • 6.21 mV ; T = ______ deg F
  • 10.93 mV ; T = ______ deg F
  • 18.83 mV ; T = ______ deg F
Answer :
All answers based on ITS-90 thermocouple table values:
  • 2.55 mV ; T = 195 deg F
  • 6.21 mV ; T = 357 deg F
  • 10.93 mV ; T = 567 deg F
  • 18.83 mV ; T = 904 deg F
Type J thermocouple
A type J thermocouple is inserted into a process, with a digital multimeter connected to its terminals.
The ambient temperature at the DMM’s test lead connections is 17 oC.
Calculate the thermocouple’s measurement junction temperature at the following millivolt measurements (rounding to the nearest degree Celsius):
  • 5.05 mV ; T = ______ deg F
  • 17.82 mV ; T = ______ deg F
  • 31.44 mV ; T = ______ deg F
  • 40.29 mV ; T = ______ deg F
Answer :
  • 5.05 mV ; T = 112 deg C
  • 17.82 mV ; T = 346 deg C
  • 31.44 mV ; T = 586 deg C
  • 40.29 mV ; T = 732 deg C
Double Block and Bleed Valves Opening or Closing Sequence
Programmable Logic Controller (PLC) Questions and Answers – 13
Practical Process Control System Questions & Answers – 1
Stilling Well in Interface Level Measurement System
Pressure Switch Questions
PLC connected to Three Pushbutton Switches
Calculate the Magnitude of Hydrostatic Pressure
What is the Simple Alternative Vessel Level Indication?
Air Pressure Regulator Questions
Questions on Allen-Bradley MicroLogix 1000 PLC
Determine LRV and URV settings for the Level Transmitter
Liquid Level Switch Control Logic
Distillation Tower Displacer Level Instrument Check
Guided-wave Radar Asset Management Parameters
Manometer Measures Differential Pressure
How Manometer Measures Differential Pressure for Different Fluids?
Explain What these Spool Valve Represent
Explain What these Spool Valve Symbols Represent?
Practical Control Systems Questions & Answers - 2
Practical Process Control System Questions & Answers – 2
Chemical Seal Pressure Transmitter
What is the Purpose of Chemical Seals Pressure Transmitter?
Determine the Problems with the Level Transmitter and Gauge
Determine the Problems with Level Transmitter and Gauge
Signal Strength of Guided-wave Radar Level Instrument
High and Low Ports on Pneumatic DP Transmitter
Identify High and Low Ports on Pneumatic DP Transmitter
Paint Mixing System
Paint Mixing System
PLC Analog I/O Potential Problems
PLC Analog I/O Potential Problems – Troubleshooting & Issues
SCADA and HMI Systems - Differences, Similarities, Purpose
SCADA and HMI Systems – Differences, Similarities, Purpose
flow-meter-accuracy-calculation
Impact of Flow Meter Accuracy
Instrument Mechanic Interview Questions
Top 100 PLC Objective Questions and Answers
Control Valves Pre-Commissioning Checklist
How to Identify Phase, Earth, and Neutral Wires_
How to Identify Phase, Earth, and Neutral Wires?
What is an Actuator - Different Types of Actuators
What is an Actuator? – Different Types of Actuators