An electronic  temperature transmitter is ranged  50 to 140 degrees  Fahrenheit and  has  a 4-20 mA output  signal.   Calculate  the  current output  by this  transmitter if the  measured  temperature is 79 degrees Fahrenheit.
Temperature Transmitter Formula
We are solving this problem using standard 4-20mA conversion Formula. Click here for formula
First, we will set up a linear equation describing  this temperature transmitter’s function:
Temperature Transmitter Graph
Calculating and substituting the slope (m)  value for this equation, using the full rise-over-run  of the linear function:
Transmitter span
The y-intercept value will be different  for this example than it was for previous examples,  since the measurement range is not zero-based.  However, the procedure  for finding this value is the same– plug any corresponding  x and  y values into the equation and  solve for b.  In this case, I will use the values of 4 mA for y and 50 o F for x:
Temperature Transmitter formula conversion
We may apply the same alternative method of solution to this problem as we did for the flowmeter example:   first  converting  the process  variable  into  a  simple  “per  unit” ratio  or  percentage  of measurement range,  then using  that percentage to calculate current in milliamps.
The  “tricky” aspect  of this example is the fact the temperature measurement range does not begin at zero.
Converting  79 deg F  into  a  percentage  of a  50-140 deg F  range  requires  that we first  subtract the live-zero value, then divide by the span:
Temperature Transmitter calculation
Again,  we arrive  at the exact  same figure for transmitter output current:  9.16 milliamps  at a measured temperature of 79 o F.
The  choice to calculate  transmitter current  by first  setting  up  a “customized”  linear  equation for the transmitter in question  or by  converting  the measured  value  into  a percentage  and  using a “standard” linear  equation for current is arbitrary.
Either method  will produce  accurate results, although it could be argued that the “customized equation” approach may save time if many different current values must be calculated.
We can also solve the problem using direct formula. Click here for formula
Articles You May Like :
PLC Example with Switches
Flow Meter Turndown Ratio
Fieldbus Transmitter Calibration
Relationship of Temperature Scales
Formula – 4-20ma from percentage
What is a Four-wire RTD ?
Bridge Circuit Construction
How to Convert Cable Size from AWG to Inches
How Does an Infrared Thermometer Work?
Temperature Gauges and Elements : Detailed Specifications
What is RTD Sensitivity ?
Turbine Flow Meter Coefficient and Scaling Factor
How to Select Right Thermocouple & Thermowell ?
Non-contact Pyrometers Characteristics
Basics of Thermocouples and RTD
Temperature Sensor Accessories
4-20mA Graphical Calculations
Temperature Sensor calibration procedure
Thermocouple Reference junction compensation
Difficulties with Thermocouples for Temperature Measurement
Thermocouples Burnout detection
3 Wire RTD Connections
RTD Sensor Connections
Formula for 4-20mA from 3-15PSI
Formula to Calculate 3-15psi from 4-20mA Current
Calibration of Pyrometers using Black Body
RTD Accuracy
What is RTD Accuracy ?
Temperature Controller Problem
Process variable to 4-20mA Conversion
Formula to Calculate 4-20 mA from Process Variable
Annunciator Panel
What is a Annunciator Panel?
Tuning Fork Level Switch principle
Synchronous Machines Excitation Quiz
Structured Text PLC Programming for Two-Tanks Level Control
Structured Text PLC Programming for Two-Tanks Level Application
Turbine to Gearbox Alignment Drifts Caused Pump Transfers Problems
SCR Class B Resonant-Pulse Commutation
Thyristor Commutation Techniques – Types, Working Principles
Flare KOD
Flare Knockout Drums Working Animation