Reading: XG5000 PLC Programming for Automatic Exhaust Fan
Inst Tools > Blog > PLC Tutorials > XG5000 PLC Programming for Automatic Exhaust Fan
Learn how to control the Automatic Exhaust Fan in Auto and Timer mode using XG5000 PLC programming software.
Last updated: September 22, 2024 11:33 am
This article discusses controlling the Exhaust FAN automatically using a timer in the XG-5000 PLC software.
Automatic Exhaust FanProgram IOXG5000 PLC Programming
The Exhaust FAN PLC program is used to suck up dust in the room. The system can be Run in 2 modes, Auto or Timer. In Auto mode, the Exhaust Fan will turn ON when the dust level in the room exceeds the “Set value” limit.
When the system is Running in Timer mode, the Exhaust Fan will turn ON sequentially. Exhaust Fan will be ON for 5 seconds and will be OFF for 5 seconds.
This PLC program uses 2 buttons and 1 selector switch, the START_SYSTEM (P0000) button is used to Turn ON the system, and the STOP_SYSTEM (P0001) button is used to Turn OFF the system.
Selector Switch MODE_BUTTON (P0002) is used to select the system to Run in Auto or Timer mode.
By default, when the START_SYSTEM (P0000) button is pressed, the system will Run in Auto Mode. The Output OUT_FAN (P0040) will be ON when the value in the memory word PV_TEMPERATURE (M050) is greater than or equal to the memory word SV_TEMPERATURE (M051).
When Selector Switch MODE_BUTTON (P0002) is changed to Timer mode, the Output OUT_FAN (P0040) will be ON for 5 seconds and then OFF repeatedly.
The system will be OFF if the STOP_SYSTEM (P0001) button is Pressed.
Program IO
CommentInput (I)Output (Q)Memory BitsMemory WordTimers
START_SYSTEM_SYSTEMP0000
STOP_SYSTEM_SYSTEMP0001
MODE_BUTTONP0002
OUT_FAN P0040
SYSTEM_ON  M0000
TIMER_MODE  M0001
AUTO_MODE  M0002
TIMER_MODE  M0003
AUTO_MODE  M0005
PV_TEMPERATURE           M050
SV_TEMPERATURE  M051
TIMER_1    T000
TIMER_2    T001
NETWORK 1
In this rung, when the START_SYSTEM (P0000) button is pressed, the memory bit SYSTEM_ON (M0000) will be in the HIGH state. Memory bit SYSTEM_ON (M0000) will remain in the HIGH state even though the START_SYSTEM (P0000) button has been Released because it uses Latching.
If the STOP_SYSTEM (P0001) button is Pressed, the memory bit SYSTEM_ON (M0000) will change to LOW state.
Automatic exhaust fan control
NETWORKS 6
When the NO contact of memory bit SYSTEM_ON (M0000) is HIGH and the NC contact of Selector Switch MODE_BUTTON (P0002) is in the LOW state, the memory bit AUTO_MODE (M0002) will be in the HIGH state.
The memory bit TIMER_MODE (M0001) will be in HIGH state if the NO contact of memory bit SYSTEM_ON (M0000) and the NO contact of Selector Switch MODE_BUTTON (P0002) are in HIGH state.
NETWORKS 14
In this Rung, when the NO contact of memory bit SYSTEM_ON (M0000) is in the HIGH state, the memory bit FAN_TIMER (M0003) will be in the HIGH state. The timer instruction TIMER_1 (T000) will start counting up to 5 seconds and TIMER_2 (T001) will count up to 10 seconds.
When the timer TIMER_1 (T000) finishes counting, the memory bit FAN_TIMER (M0003) will change to a LOW state due to the interlock of the timer TIMER_1 (T000).
When the TIMER_2 (T001) timer finishes counting, the timer TIMER_1 (T000) will be OFF due to the interlock of timer TIMER_2 (T002) and memory bit FAN_TIMER (M0003) will change to a HIGH state again.
PLC programming for exhaust fan
NETWORKS 27
In this Rung, when the NO contact of memory bit SYSTEM_ON (M0000) is in a HIGH state and the value in memory word PV_TEMPERATURE (M050) is greater than or equal to memory word SV_TEMPERATURE (M051), then the memory bit FAN_AUTO (M0004) will be in the HIGH state.
When the value in the memory word PV_TEMPERATURE (M050) is Less than the memory word SV_TEMPERATURE (M051), then the memory bit FAN_AUTO (M0004) will be in LOW state.
NETWORKS 31
The Output OUT_FAN (P0040) will be ON if the NO contact of memory bit FAN_TIMER (M0003) or FAN_AUTO (M0004) is in the HIGH state.
  • Automatic Vacuum Cleaner PLC Programming
  • STAR-DELTA Auto And Manual PLC Program
  • Electric Motor Forward Reverse PLC Logic
  • Product Painting with Omron PLC Program
  • Attendance System Program in Omron PLC
What is Interface Module in Siemens PLC?
PID in Studio 5000
Parking Garage Indicator: PLC Automation System
PLC Program for Washing Machine
#3 PLC Best Practices – Leave Operational Logic in the PLC wherever feasible
PLC based Door Open and Closing System
#10 PLC Best Practices – Assign Register Blocks by Function
PLC Problems Troubleshooting
Flip-Flop PLC Programming: Lights with Adjustable Timers
Process Interlocks and Trips
What is Live Zero in 4-20 mA Current Loop?
Parameters of SRT_DINT instruction
Tia Portal – OB20 Time Delay Interrupt Organization Block
Top PLC Manufacturers
PLC Brands Software Information
Tanks Draining Control in PLC using Functional Block Diagram
Bit Shift Registers PLC Program
PLC Light Sequence Control using Bit Shift Registers
PLC Software Redundancy
Software Redundancy in Siemens PLC – Hardware versus Software
PLC Sequence Programming Ladder Logic
MCQ on PLC (Programmable Logic Controller)
DDE Protocol
What is the DDE Protocol?
valve-actuator
Pneumatic Control Valve Actuators
FPGA vs. CPLD - What are the differences between them
FPGA vs. CPLD – What are the differences between them
CO2 Analzer Working Principle
Infrared Non Dispersive CO2 Analyzer Working Principle
Effect of Lead Wire Resistance on RTD
Advantages and Disadvantages of Pneumatic Instruments
Displacement Sensing Accelerometer
Seismic Displacement Sensing Accelerometer
NFPA Standards (National Fire Protection Association Standards)
Advances in Control System
Adaptive Control