The PID controller plays a major role in controlling the process parameters in process industries. It consists of Proportional term, Integral term and Derivative term which combinedly reduces the transient error and steady state error. In steady state condition, i.e when the error tends to zero the output of PID is equal to the integral term of PID.
If the error = 0
then
PID = Kc * error + Ki(previous integral + error) + Kd(error – last)
= 0 + Ki (previous integral + error) + 0
= Ki (previous integral + error)
by the above analysis it is proved that the output of PID controller at the steady state is equal to integral term which acts as reset component of the controller. This illustrates the importance of integral controller in PID controller. With the advantage of reset rate of controller and minimizing the error to zero at steady state, there is major drawback in the integral term i.e wind-up of integral component.
Integral wind-up:
Integral windup is the process of accumulating the integral component beyond the saturation limits of final control element. The formula for integral component in PID is
Integral component = (Ts/Ti) * error
Where Ts = time cycle
Ti = Integral time constant or reset rate
If the set point raises suddenly or the actual value drops suddenly then there will be large error between the set-point and actual value. This error causes the integral component to accumulate with the time period to bring back the actual value near to the set-point. As a result the controller output may exceeds the saturation limits of final control element. The integral component still may accumulate beyond the saturation limits of the final control element because of error. Whatever the integral value the final element or actuator cannot open/close beyond its saturation value. This concept is explained by the following example
Consider a PI control is placed for controlling the liquid level in the controller which controls the inlet flow to the tank by adjusting the inlet valve position. Now if the set-point is raised by the operator from control room then the PI controller calculates the new actuator position according to the error. The integral component of the PI controller which adds the reset rate will accumulates according specified time cycles. If the output of PI controller is 120 % to the adjuster which is the above saturation limit of the actuator because actuator cannot open beyond 100 % position. In full position of valve also still if the error is existing will further increases the integral component value.
At this time if the set-point is lowed by the operator, the controller cannot close the valve to reduce the flow because high accumulation of integral value. Once the integral component reaches its normal value with negative error accumulation than only the PI output will drive the actuator in close direction. This integral accumulation beyond the saturation limits of the final control element is called integral windup which gives a poor response of controller under dynamic conditions.
Example
Consider an above example of PI controller used to control the control the liquid level in the tank.
Initial set-point of of liquid level = 50%
output PI controller(steady state) = Promotional term + integral term
= 0 + 60
= 60
Valve position (linear ) = 60 (0-100)
Now if the operator has raised the set-point to 90% suddenly then according to the error the PI controller increases the output to open the valve to allow more liquid flow.
output PI controller = Promotional term + integral term
= 20 + 80
= 100
The valve is fully opened then also if the liquid level does not reach to its set-point which leads an input error for PI controller.
= 10 + 140
= 150
Even the output of PI controller is 150 the Valve can open up to 100 % open only. i.e that is called the high saturation limit of valve. If the error is still not reduced the integral component will go on accumulate to limit the error. Let us assume the integral component has accumulated up to 180.
Now if the operator has reduced the set-point to 50% then the error of liquid level is -40 %. Then if the proportional gain is 0.5 then
= -20 + 170
= 150
Valve position is = 100 (high saturation limit)
Again the output of PI controller will be less than 100 to close the valve when the integral component reaches to less than 100. This results a poor control of liquid level. To eliminate this integral accumulation beyond saturation limits of final control element the anti-windup technique should be used in design of controller.
Also Read: PID Controller Bumpless Transfer
Excellent Article. Easy Explanation. Thanks
nicelly explained the concept