Inst ToolsInst ToolsInst Tools
  • Courses
  • Automation
    • PLC
    • Control System
    • Safety System
    • Communication
    • Fire & Gas System
  • Instrumentation
    • Design
    • Pressure
    • Temperature
    • Flow
    • Level
    • Vibration
    • Analyzer
    • Control Valve
    • Switch
    • Calibration
    • Erection & Commissioning
  • Interview
    • Instrumentation
    • Electrical
    • Electronics
    • Practical
  • Q&A
    • Instrumentation
    • Control System
    • Electrical
    • Electronics
    • Analog Electronics
    • Digital Electronics
    • Power Electronics
    • Microprocessor
  • Request
Search
  • Books
  • Software
  • Projects
  • Process
  • Tools
  • Basics
  • Formula
  • Power Plant
  • Root Cause Analysis
  • Electrical Basics
  • Animation
  • Standards
  • 4-20 mA Course
  • Siemens PLC Course
Reading: Importance of Temperature in Remote Seal Pressure Transmitter
Share
Notification Show More
Font ResizerAa
Inst ToolsInst Tools
Font ResizerAa
  • Courses
  • Design
  • PLC
  • Interview
  • Control System
Search
  • Courses
  • Automation
    • PLC
    • Control System
    • Safety System
    • Communication
    • Fire & Gas System
  • Instrumentation
    • Design
    • Pressure
    • Temperature
    • Flow
    • Level
    • Vibration
    • Analyzer
    • Control Valve
    • Switch
    • Calibration
    • Erection & Commissioning
  • Interview
    • Instrumentation
    • Electrical
    • Electronics
    • Practical
  • Q&A
    • Instrumentation
    • Control System
    • Electrical
    • Electronics
    • Analog Electronics
    • Digital Electronics
    • Power Electronics
    • Microprocessor
  • Request
Follow US
All rights reserved. Reproduction in whole or in part without written permission is prohibited.
Inst Tools > Blog > Practical Questions > Importance of Temperature in Remote Seal Pressure Transmitter

Importance of Temperature in Remote Seal Pressure Transmitter

Last updated: June 16, 2020 5:24 pm
Editorial Staff
Practical Questions
2 Comments
Share
3 Min Read
SHARE

Why is temperature an important factor in pressure transmitters equipped with remote seals (sometimes called “chemical” seals)? Specifically, what temperature condition(s) could cause a differential pressure instrument with remote seals to experience measurement errors?

Also, describe what would happen to a pressure instrument equipped with remote seals if ever a leak developed in one of the capillary tubes.

Remote Seal Pressure Transmitter Temperature

Remote Seal Pressure Transmitter Temperature

Image Credits: reotemp

 

Increased temperature causes the fill liquid in the capillary tube to expand, thus creating a pressure at the transmitter’s sensing element independent of the process fluid pressure being measured.

If the seal-equipped transmitter is differential in nature, and the temperatures of both seal units and capillary tubes are equal, then any temperature-induced pressures will cancel out at the transmitter, and there will be no problem.

However, if the temperature of one seal or capillary is greater than the other, there will be a differential pressure induced by temperature that the transmitter will detect and interpret as process fluid differential pressure.

Remote seal/capillary systems must be completely gas-free (nothing but liquid inside) in order to work. If even a small air or other gas bubble works its way in to the fill fluid between the remote seal diaphragm and the instrument sensing element, the fill fluid will be compressible, meaning that the seal diaphragm will displace a greater volume of fill fluid than the instrument’s sensing element. Thus, the instrument may not “see” the entire amount of process pressure change applied to the seal diaphragm, and its measurement accuracy will be compromised.

In summary, leaks in a remote seal system have very detrimental effects on instrument accuracy. If ever such a system develops a leak, the whole instrument must be replaced. Even if you could patch the leak, you would have to “pack” the seal unit, capillary tubing, and transmitter pressure housing with new fill liquid under a strong vacuum to “pull” any dissolved gas bubbles out of the liquid. Needless to say, the facilities required for such an operation are typically not available in a plant instrument shop, thus rendering the instrument unrepairable by you.

Share your answers with us through below comments section.

Read Next:

  • DP Transmitter with 5 Way Manifold
  • Filled-bulb Temperature Sensor
  • DP Transmitter Auto Calibration
  • Manometer Measurement Accuracy
  • Pressure Gauge Selection

Credits: Tony R. Kuphaldt

Don't Miss Our Updates
Be the first to get exclusive content straight to your email.
We promise not to spam you. You can unsubscribe at any time.
Invalid email address
You've successfully subscribed !

Continue Reading

Draw a ladder logic circuit for the electric motor of an air compressor ?
Question on Remote Seal with Capillary Tubing Transmitter
Calculate Process Temperature using a Thermocouple
Resistance Temperature Detector (RTD) Questions – 2
What Effect on Hydrostatic Level Transmitter if Liquid Density Changes?
Pressure Gauge with Block and Bleed Valves
Share This Article
Facebook Whatsapp Whatsapp LinkedIn Copy Link
Share
2 Comments
  • Gutri says:
    September 26, 2020 at 9:34 am

    Good and brief article. I would like to add some point.

    DS always add error and certain additional response time to the DP/Pressure Transmitter. DPT/PT nowadays have at least 0.04% – 0.075% of span accuracy and response time at 100 msecond less. Many End User will spark after dicussed the critical effect of DS onto the whole close system DS+DPT or DS+PT in regard of error and response time.

    A.Temperature effect will create error in terms of pressure because of liquid expansion. How much the expansion will depend on the selection of liquid ( liquid characteristic ) and the volumetric inside the tubing . And off course the installation effect on site. How the cappilary position to day light on the tanks,is it balance between high pressure side and low pressure side.It should take as a note of one temperature effect concern too.

    B.There is another concern beside temperature effect namely response time.How fast the liquid seal transfer the pressure from diaphragm seal onto the transmitter.

    This wlll depend on the viscosity of the liquid selection and again volumetric inside the tubing. Viscosity will be resistance factor to transfer the pressure).

    Liquid selection will be depend on application : cryogenic ,medium temperature,high temperature,food related. Each application have specific suitable liquid.

    Volumetric selection will be depend on pressure range will it be low range,high pressure ( e.g low pressure need less volume inside tubing to make it be able to move liquid ) and to make it more complicated to select the correct surface area of diaphragm seal ( low range pressure,need big surface of diaphragm seal to feel the pressure)

    At the end all of above concern will be presented as

    Temperature effect( pressure error) VS response time ( msecond).

    1.Less temperature effect ( 0.1% pressure error at least ) will have slowest response time ( > 1 sec )

    2.Fastest response time ( 1% pressure error )

    These 2 have inverse relation.

    We will choose the optimize value for those of 2.

    There is the challenge and the expertise of certain Diaphragm Seal Manufaturers.

    Sincerely yours,

    Gutri F

    Reply
  • sivchidambaram says:
    April 22, 2022 at 4:34 pm

    For process operating temperature -42 deg C, whether diaphragm seal or impulse tubing is preferred?

    Reply

Leave a Reply Cancel reply

Your email address will not be published. Required fields are marked *

Stay Connected

128.3kFollowersLike
69.1kFollowersFollow
210kSubscribersSubscribe
38kFollowersFollow

Categories

Explore More

Electronic Pressure Sensor with Bourdon Tube and LVDT
Programmable Logic Controller (PLC) Questions and Answers – 11
Thermocouple Terminal block Questions
A Series of False Pressure Alarms
Baffle Nozzle Assembly Sensitive Mechanism
Hydrostatic Pressure of a vertical column of Acetic Acid
Calculate Amount of Weight Indicated by the Scale
Pneumatic Relay Questions

Keep Learning

Two Differential Pressure Transmitters

Pressure Level Transmitter Problems

Resistance Temperature Detector (RTD) Questions

Resistance Temperature Detector (RTD) Questions – 1

Calculate Hydraulic Pressure of a Drum

Calculate Hydraulic Pressure of a Process Vessel

PLC program pushbutton switches

PLC Permissive for Motor Control

Pneumatic Transmitter

Questions on Pneumatic Transmitter and Repeater

Ladder Diagram circuit

PLC Practice Questions

Practical Control Systems Questions & Answers

Practical Process Control System Questions & Answers – 1

Calculate Total Hydrostatic Pressure at Bottom of Vessel

Calculate Total Hydrostatic Pressure at Bottom of Vessel

Learn More

HART Communication Tutorial 2

HART Communication Tutorial Part 5

Power Electronics Objective Questions

Single Phase Voltage Source Inverter MCQ

Power Electronics Objective Questions

GTO Objective Questions and Answers

Level Measurement in Liquids

Point Level Detection Working Principle

Digital Electronics Multiple Choice Questions

Random Access Memory Objective Questions – Part 2

Valve stem travel

Control Valves Mechanical Friction Problems

Current and Voltage analogy

Current and Voltage Principle Animation

Weigh Feeder Drive

Failing Weigh Feeders and Mechanical Variable Speed Drives (VSD)

Menu

  • About
  • Privacy Policy
  • Copyright

Quick Links

  • Learn PLC
  • Helping Hand
  • Part Time Job

YouTube Subscribe

Follow US
All rights reserved. Reproduction in whole or in part without written permission is prohibited.
Welcome Back!

Sign in to your account

Username or Email Address
Password

Lost your password?