Reading: Readings Mismatch between Field & Control Room ? Why
Inst Tools > Blog > Control Systems > Readings Mismatch between Field & Control Room ? Why
Last updated: March 4, 2021 3:56 pm
Control Systems Instrumentation Design PLC Tutorials
20 Comments
10 Min Read
Instrumentation maintenance engineer often hears about process value mismatch from field transmitter display reading and control room DCS/PLC reading.
Generally we see the readings mismatch between field & DCS happens due to the improper configuration either at transmitter or in control room (DCS/PLC).
For example : Operations team informed that a temperature transmitter shows 112 Deg C reading in the field local display and 89.6 Deg C in the control room HMI/SCADA. Then Instrumentation engineer checked & found that Field Transmitter configured range is 0 to 250 Deg C whereas in DCS the configured range is 0 to 200 Deg C. Because of this improper configuration, we have mismatch in readings between field & control room.
Note : use Online Inst Calculator to do conversions like pv to mA or similar
Fine, Now lets assume that the configurations are properly done in field transmitter and in DCS but still we are getting some difference in readings between field & DCS. What happens ?
This may happens because of 4-20mA loop current drop also. In this article i am discussing about the impact of loop current drop in Field & Control room readings.
The 4-20mA loop current drop may happens due to the following :
  1. Little bit High Main cable / Branch cable resistance : Theoretically there will be NO current drop in the loop but sometimes (practically on different rare situations) there will be small amount of current drop can be seen due to cable problems like high resistance, insulation damage, noise, emf etc.
  2. Range Mismatch
  3. Ground Loops
  4. Improper Transmitter Analog output card calibration/configuration
  5. DCS/PLC Analog Input card Resolution ( Very low Possibility of this error )
  6. DCS/PLC Analog input card channel calibration (Very low Possibility of this error )
  7. Loose connections in the loop
  8. Rusted components or terminals
Above listed are the some possibilities for 4-20mA loop current drop.
Theoretically loop current will be same in the total loop but we sometimes found a very small amount of loop current drop. Now the question ” is there any impact of this loop current drop on process variable readings ? ” we will discuss below.
Now another question also will come into your mind that How to check the 4-20mA Loop current Drop is there or not ? or loop current drop is the problem or any other things are causing the reading mismatch between field & control room ?
First thing to do is measure the existing loop current. connect a multimeter in series with the loop and note the loop current value, for example say multimeter displays 5.99mA. Good, we got the loop current reading but it is the right value ? Lets check.
Well, you NO need to use any formulas or calculations to calculate the Actual Transmitter Output current with respect to present PV, LRV & URV values. ( we can also find out the actual loop current by using process variable to 4-20mA conversion formula also).
Simply connect your HART communicator to the transmitter and check Analog Output Current reading in HART display, say it shows 6.00mA. Please remember that if there is loop current drop also, this HART display shows correct reading as this value directly coming from transmitter processor/cpu.
Even if transmitter inbuilt digital to analog card not working properly also the HART Display shows the correct reading in most cases as it taking the value from transmitter processor/cpu and not from transmitter D/A card.
Now we got these readings :
  • HART display shows 6.00 mA
  • Multimeter shows 5.99 mA
The difference between Actual reading (HART Display) and Present reading (multimeter) is 0.01mA. Now a quick question comes into your mind : What is the impact of this very small amount of 4-20mA loop current drop ? is this important to consider or negligible ? we will see with examples below.
Example 1 :
A Pressure transmitter having a range of 0 to 10 kg/cm2 installed in a pipeline. The present value indicating by the transmitter display/ local display reading is 1.25 kg/cm2 and 1.24375 kg/cm2 displaying in Control room. Why there is a difference and What happens ?
we will apply above discussed parameters here i.e. some pressure is there in the pipeline and HART display shows 6mA and multimeter connected in the loop showing 5.99mA.
Also note that HART local display shows process variable reading based on 6mA or transmitter processor/cpu value, so the local display shows 1.25 kg/cm2 ( calculate equivalent process variable from 6mA).
Consider there is a small amount of loop current drop ( assume 0.01mA), so multimeter shows 5.99mA, so DCS/PLC Analog input card also receives 5.99mA instead of 6mA. when you convert 5.99mA to equivalent process variable, the control room shows 1.24375 kg/cm2, if you apply round number, the SCADA graphics shows 1.244 kg/cm2.
Now the difference between field reading and control room reading is 0.006 kg/cm2. Percentage of error is 0.06%.
if you consider one decimal number then field reading is 1.2 and control reading also 1.2, so both are same, fine. Percentage of error is 0 %. Looks good.
same way if you consider two decimal numbers then field reading is 1.25 and control room reading is 1.24, so there will be error of 0.01 kg/cm2. Percentage of error is 0.1%.
Again consider three decimal numbers then field reading is 1.250 kg/cm2 and control reading is 1.244, so there will be error of 0.006 kg/cm2. Percentage of error is 0.06%.
Lets see the comparison without rounding of number in control room : Field reading is 1.25 kg/cm2 and control room reading is 1.24375 kg/cm2, so there will be error of 0.00625 kg/cm2. Percentage of error is 0.0625%.
Finally our error percentage varying from 0 % to 0.0625 % ( 0 to 0.00625 kg/cm2 in terms of process value ) depending on number of decimals of the transmitter & DCS readings. In this example, Everyone says that it is OK with the readings as there is no much difference with the readings ( considering transmitter loop is non-critical ).
Lets see the same situation with another example
Example 2 :
A Flare flow meter having a range of 0 to 1,50,000 kg/hr. we will apply above discussed parameters here i.e. HART display shows 6mA and multimeter showing 5.99mA.
HART Display @ 6mA Shows 18750 kg/hr
Process value Multimeter in loop measures 5.99mA, When we calculate equivalent process value then we have 18656.25 kg/hr
Now the difference between field reading and control room reading is 93.75 kg/hr. approx Percentage of error is 0.06%. Here percentage of error remains same but there is a considerable amount of loss in process value. The main reason for this is due to higher span range of transmitter. Well in this case, we cannot neglect the small amount of loop current drop.
Remember that there will be no impact of loop current drop in field transmitter display (considering transmitter has inbuilt display) as it getting the value from internal transmitter processor/cpu and definitely there will be impact in control room reading.
Also if you connect a external loop power indicator in series with the loop then this loop power indicator reading also effected as same as control room because loop power indicator & control room have same input i.e. 5.99mA as per our example.
we considered 0.01mA loop current drop and seen the two examples & their impact on process reading in field & control room. Now take a small assignment yourself and Consider 0.05mA & 0.1mA loop current drop and observe the impact on process variable readings in field & control room.
I hope you also faced the readings mismatch between field & control room related problems.
Lets share with us what was the problem & how you solved it.
Share via comments…
Happy learning & sharing @ InstrumentationTools.com
  • Flow Transmitter Readings mismatch with DCS
  • What is Process Control ?
  • Example of Feedback System
  • Process Control High Level Alarm Fault Analysis
  • Control Room Design Guidelines
PLC Pump Permissive Interlocks
Structured Text PLC Programming for Automatic Gate Control
PLC Pump Control: 10 seconds ON & 20 seconds OFF
How to Minimize Water Vapor in Instrument Air Lines?
Functional Design Specifications for DCS and SIS Projects – FDS Document
20 Comments
  • stone yuiyui says:
    January 29, 2017 at 5:19 am
    thanks very helpfull
  • P.KRISHNA RAO says:
    January 29, 2017 at 1:08 pm
    Thank you Sir.
  • Gowtham says:
    January 29, 2017 at 2:13 pm
    Good, information sir .
    Dear sir
    I’m e&i graduated actually now I’m working in paint shop in One automotive engineering company in graduated engineer trainee After I got experience can I go for our core Field like process automation Plz clear my doubt awaiting
  • Sinergxp says:
    January 29, 2017 at 3:22 pm
    Very instructive!
  • Jonas Berge says:
    February 1, 2017 at 3:23 pm
    If current recieved in the DCS end is less than it should be it is usually due to high resistance saturating the current, or additional current due to a ground loop
    This, and other problems you mentioned for 4-20 mA (and other analog signals) can be avoided by using real-time digital communication instead, such as FOUNDATION fieldbus.
  • Louis Reeves says:
    February 1, 2017 at 4:01 pm
    To Jonas point about ground loops, this is most common with 4 wire type transmitters where the power source is 110 vac and the output is 4-20 mA.
    I have seen loops with greater than 100 mA output to DCS/PLC as a result of ground loops.
  • Chris George says:
    February 1, 2017 at 5:25 pm
    I agree with Jonas. With FOUNDATION fieldbus the process variable reported by the transmitter is exactly the same as the process variable read at the control room EVERY cycle, even to 6-decimal precision. We don’t need that kind of precision but it just proves what you read is what you get.
    For existing installations, I get it. 4-20mA is everywhere and I appreciate articles like this that educate how to deal with the idiosyncrasies of each technology, but for new installations it continues to baffle me why users don’t choose digital field networks over 4-20mA to avoid these shortcomings.
    • Praveen Toshniwal says:
      February 20, 2017 at 5:28 pm
      Problem with using digital communication is absence of standardisation. Once you have selected a particular technology you are tied in.
  • Alex Tennant says:
    February 20, 2017 at 1:47 am
    This happens all too often but the different ranges of the DCS/PLC versus the field instrument is only one of the possible causes. One common range difference is a DCS/PLC set to 0-20 ma when the transmitter is outputting 4-20 ma.
    The most common reason for a discrepancy between field device and DCS/PLC is a different ground potential at the transmitter then at the DCS/PLC, most of the time the ground is floating at the transmitter and the ground is always at the DCS/PLC end of the loop. More common in self powered instruments where an isolator is sometimes used to interrupt ground loop.
  • arkiaMark Reich says:
    February 22, 2017 at 5:30 am
    If correct calibration has been done, there is also the possible difference of resolution of the analog input, the accuracy of the instrument, and the resolution of the scaling. These all have the possibility of adding to the error of control room reading compared to the field instrument.
  • faizal raazy says:
    March 1, 2017 at 5:30 pm
    Thanks a lot for the assistance ,, usefull ,no words
  • Mohd Shamsad says:
    April 6, 2017 at 11:08 am
    Dear sir.
    Thank you so much for this article. This is very useful article.
    Sir could build the instrumentationtools calculation application for iPhone.
  • Kesava says:
    August 5, 2017 at 5:24 am
    It is very useful for every instrumentation guys thank you very much.
  • James E Powell says:
    June 27, 2018 at 2:32 am
    Great article! Thank you for writing it.
    It reminds me of an article that I wrote 3 years ago. It is still posted on Profinews called ‘Is PROFIBUS more accurate then 4-20 mA’. I have just posted two video’s that you might find interesting on my youtube channel (Comms guy) about the problem with 4-20 mA.
  • Infant sujan says:
    August 19, 2019 at 10:31 pm
    Dear sir
    In field mass flow meter showing 0 kg/hr
    But in dcs it is showing 20 kg/hr
    My range is 0 to 6500 kg/hr
    When feed ma from source
    For 4 ma it is showing 20 kg hr
    At 3.8 ma oly it is showing 0 kg/hr
    When it is 4.1 ma it is showing 40 kg/hr which is correct wit my range..
    Why for 4 ma I am getting 20 kg/hr
    • S Bharadwaj Reddy says:
      August 20, 2019 at 11:00 am
      Hi,
      It is difficult to guess the issue. Hope DCS configuration is correct.
      Also when feeding 4mA from field, measure the loop current with multimeter to cross-check, if it shows 4mA then it is fine otherwise check it.
      As you are getting the issue when feeding milli amperes, so you can leave the field and concentrate on DCS.
      Feed the mA in the barrier and check again, if issue solves then problem with the cables like ground loops, mutual induction, high resistance, voltage drop etc.
      If you have issue with the above step, then check DCS configuration again, change barrier or AI channel and check gain.
      There will be many factors. i am sharing the general issues.
      Share your solution with us after solving it.
  • Girish Prasad Behera says:
    August 20, 2019 at 10:35 am
    Dear Sir,
    I have installed a new turbidity analyzer (ROSE MOUNT 1056) and calibrated in standard mode with 20 NTU solution.
    But i am getting some difference value when it is in process..
    when i am taking inlet treated water sample and check turbidity in portable meter it gives the 2.75,ntu but when the 1056 is in online it gives 3.85ntu,
    why this difference is coming.. please suggest me what i can do?
  • Nazar says:
    February 17, 2020 at 10:41 pm
    Thank you for remind me to the old memories. I started to memorising back the one that i done before. Thank you and had a wonderful day.
  • Keepwell Zuzumbe says:
    September 21, 2020 at 5:06 pm
    i am not sure about the way you calculate your percentage error , why do you multiply the difference direct with 100. Why not use the difference divided by the expected value and you then multiply by 100?
  • Akshay says:
    September 23, 2020 at 7:21 am
    There’s a big mismatch in the the readings of control room and pressure transmitter the control room is showing -1.9 nm3/hr and the transmitter is showing 350 nm3/hr
Network Operating System
PLC Program for Paint Spraying
Difference between DCS, PLC, and RTU ?
PLC Counters Program
#9 PLC Best Practices – Validate indirections
Field Instruments Selection Aid
Remote Connectivity to Industrial Automation Systems
Stripping tower unit
Pumping System in Industrial Automation
Basic Pumping System Application Used in Industrial Automation
PLC offline data of a project are compared
Compare Two Offline PLC Projects
Inter Discipline Check (IDC)
What is Inter Discipline Check (IDC)?
PLC project for traffic signals automation
Complete PLC Project: Traffic Light Auto and Manual Automation
Ziegler-Nichols closed-loop Tuning
Ziegler-Nichols Closed-Loop Method (Ultimate Gain)
Pressure Gauge Problems
Omron PLC painting program
Product Painting PLC Program using Omron CX-Programmer
FactoryTalk View Studio Site Edition Pop-Up Confirm Action
How to Automatically Close Pop-up in FactoryTalk View Studio?
Comparison of Control Loops - Open, Closed, Cascade, Feedforward, Ratio
Comparison of Control Loops – Open, Closed, Cascade, Feedforward, Ratio
Star to Delta Conversion
Star to Delta and Delta to Star Conversion Formula
Quick Exhaust Valve (QEV)
Quick Exhaust and Air Operated Valves in Instrumentation Circuit
HVAC Refrigeration Cycle
Components of Electrical Motor
What is Electrical Slip Ring? Principle, Types, Advantages, Applications
Unstable & Drifting Values of Differential Pressure Transmitter
Unstable & Drifting Values of Differential Pressure Transmitter Problem
Level Gauges Questions and Answers
Level Gauges Objective Questions and Answers – Instrumentation