Write a PLC program that when a start push button (PB) is pressed the motor runs and when released the motor stopped. And if the PB is pressed for more than 3 seconds the motor runs in the latched mode until the stop PB is pressed.
Note the best practice to learn the PLC programming is to start writing the PLC program, take your time before you review the answer.
Inputs & outputs:
I0.0: Start Push Button (Normally open contact)
I0.2: Stop Push Button (Normally closed contact)
Q0.0: Motor
M0.0: marker 01
T1: timer 01
Push button Motor PLC Logic
PLC Program descriptionÂ
When the start PB is pressed for less than 3 seconds, the last branch in the network would energize the motor as long as the PB is pressed.
When the start PB is pressed for more than 3 seconds, the timer T1 would be energized and send a pulse signal to the SR flip flop which would energize the motor in a latched mode.
Whenever the stop PB is pressed, the motor would stop.