This article is about a pulse generation PLC program using Siemens TIA PORTAL.
Inputs and OutputsPulse Generation using TimerDescription
In industries, we use special audio and visual indications to notify the operators about the alarms and trips of the process. Different types of indications are flashing LED, beacons with different tones, etc.
We can set the rate of pulses from slow to fast as per our requirement by changing the timing of the timers. Here we will be discussing the pulse generation using timer instruction in Siemens PLC.
Below I have explained the PLC program for pulse generation.
Inputs and Outputs
  • Inputs: START(I0.0), STOP (I0.1)
  • Outputs: LED_INDICATION (Q0.0)
  • Timers: T0 & T1
  • Memory Bit: M0.0
Pulse Generation using TimerPulse Generation using Timer in Siemens PLC
Description
When you press the start button (%I0.0), then the flip-flop (M0.0) energizes then it will pass the signal through NC contact of timer (T2) then timer 1 will energize.
Here I have used S_Pulse timer which will run in our case for 2 seconds after 2 seconds timer will energize.
We can change the timing of the timer to change the flashing rate as per our requirement.
If Timer 1 is not energized then first NOT instruction will energize the Timer 2 allowing output to turn ON for 2 seconds.
Both the timers will run for 2 seconds simultaneously allowing LED to turn ON and OFF for every 2 seconds thus flashing the LED.
Author: Suhel Patel
  • Troubleshoot PLC Program
  • Protect PLC using Password
  • PLC Maths Instructions
  • JUMP Instruction in PLC
  • Siemens S7 1200 PLC
  • One-Shot Rising PLC Logic
Configuration of Siemens VFD Using TIA Portal Start drive
Difference between Power Cables and Signal Cables
Unknown Do’s Need to Know as a PLC Programmer
3 Comments
  • Kumar says:
    April 5, 2020 at 11:48 am
    Hi,
    What is the need of two timers?
  • Suhel says:
    April 5, 2020 at 1:03 pm
    To generate the pulses, 1 timer stay ON for 2 sec, so another timer will remain OFF for 2 sec. thus generating pulse for that interval
  • Praveen Kumar B H says:
    July 3, 2023 at 5:42 am
    Let me correct if my and is wrong…. I think of one timer is enough for pulse generation of every two Seconds once… I will explain, after sr flipflop take contact of timer 1 NC CONTACT., when we press start sr FF will energized and start timer. 2 second after timer output goes to led to blink and timer contact which we taken on After flipflop.,it change from nc to open and again change to NC then again timer start and 2sec after led blink and this operation is continuously running….
Components of SCADA
Difference between Motion Controller and PLC
Set the S5 Timer Value by a Memory Word
Programmable Logic Controller (PLC) Scan Time – Types, Theory
Fixed PLC
traffic light plc program
Sourcing output module in PLC
Which Connection is Best for PLC? – Sinking or Sourcing
Siemens PLC
Five Types of PLC Programming languages
Parking Garage Indicator PLC Automation
Parking Garage Indicator: PLC Automation System
CODESYS HMI Interface
Extended Timer Logic in PLC
Cyclic Interrupts TIA Portal
Configuring and Usage of Cyclic Interrupts TIA Portal (OB 30+)
Non-variable reducing valves
What is Reducing Valve ?
Basics of Motion Controllers
What is Photoionization Detector (PID)
What is Photoionization Detector (PID)?
Tube Fitting Parts
Procedure for Crimping the Connector
Equivalent Circuit of Transformer
Modbus
Modbus : History, Structure, Modes, Addressing, Functions
Malfunctioning Inlet Check Valves
Dead Time and Reclaim Time
What is Auto Reclosing?