Reading: PLC Permissive for Motor Control
Inst Tools > Blog > PLC Tutorials > PLC Permissive for Motor Control
Last updated: March 4, 2021 3:51 pm
PLC Tutorials Practical Questions
2 Comments
2 Min Read
A engineer needs to write a PLC program to control a water pump driven by an electric motor. This water pump will be manually started and stopped by pushbutton switches, and shutdown automatically by any one of several “permissive” switches.
The operating statuses of these switches are listed here:
  • Start pushbutton (normally-open): open when unpressed, closed when pressed
  • Stop pushbutton (normally-open): open when unpressed, closed when pressed
  • Low water level (normally-closed): closed when level is low, open when level is adequate
  • Low oil pressure (normally-open): open when pressure is low, closed when pressure is adequate
  • High vibration (normally-closed): closed when still, open when vibrating
  • Water leak detector (normally-open): open when dry, closed when wet (leak detected)
PLC Permissive Motor Control
The engineer’s first attempt is shown here, but it contains a serious error. Identify and correct this error:
PLC program pushbutton switches
Answer :
The Stop_PB contact instruction should be drawn as normally-closed rather than normally-open as shown in the engineer’s first draft of the PLC program.
The program is designed to shutdown the motor when that pushbutton is pressed (i.e. the Stop_PB contact instruction becomes uncolored (i.e. fails to “conduct” virtual power).
We have been told that the real-world Stop pushbutton switch is NO, which means its contact closes when pressed.
This means pressing the Stop pushbutton causes that bit to be 1, which necessitates an NC contact instruction so that it will un-color under that condition.
PLC Counters Program
Contacts and Coils in PLC
PLC Electric Motor Interlocks
Motor Control Circuit
PLC Pump Permissive
Schneider PLC Example Program for Star-Delta System
Calculate the Thermocouple Output millivolts
How to Export Data from WinCC Runtime Advanced into Excel using VB Script
How to Detect Speed of Conveyor in PLC?
Connecting Faceplate to PLC Project – HMI Tutorial
2 Comments
  • Bruce says:
    April 19, 2018 at 7:09 am
    Why would you show an example of stop being NO and not fail safe. You would never see it wired this way in an individual setting?
  • DIMITRIOS ADAMOS says:
    June 21, 2018 at 8:19 pm
    Hi , i believe that there are two ways that you can program a stop button . this is one way that you mention
    and the other way ,you have stop button NC (hardwired) and you program it as NO in the plc ,fail safe .so there is no wrong in this i believe .great work
208kSubscribersSubscribe
Problem with Sump Tank Level Transmitter
Hydrostatic Level Measurement – Temperature related Density Change Effects
Static and Temp Variables in PLC
Current-to-Pressure Transducer Calibration Table
How to Design an Effective HMI? – Human Machine Interface
Two Hand Press Safety Control Circuit
Siemens PLC Mathematics Instructions
Industrial Networking and Wireless Interview Questions
Sample Schematic Template for Systems Architecture Diagram
Types of Scan Time in a PLC
Programmable Logic Controller (PLC) Scan Time – Types, Theory
Identify which lamp in the following ladder-logic diagram
Identify High Flow Alarm and Low Flow Alarm?
PLC based Drink Dispenser System
PLC Program Upload
How to Upload Siemens PLC Programs?
PLC Program for motor operation based on time cycle
PLC Motor Operation based on Time Cycle Sequence – Program
PLC Program for Automatic Oil and Water Separation Process
Oil and Water Separation Process using PLC Programming
Manual sequential logic in Schneider PLC
Programming Schneider PLC Manual Sequential Machine
Vortex Flow Meter Animation
Common Control Valve Problems
Troubleshooting Common Control Valve Problems
Time Response Analysis
Robotic Control System – Part II
Differential Pressure Transmitter Manifold
Field Instrument Calibration Errors
PLC Program for Trash Compactor
Time Response of Second Order Systems – II
H2S Analyzers Questions & Answers
SCADA Multiple Choice Questions