A engineer needs to write a PLC program to control a water pump driven by an electric motor. This water pump will be manually started and stopped by pushbutton switches, and shut down automatically by any one of several “permissive” switches.
The operating statuses of these switches are listed here:
  • Start pushbutton (normally-open): open when unpressed, closed when pressed
  • Stop pushbutton (normally-closed): closed when unpressed, open when pressed
  • Low water level (normally-closed): closed when level is low, open when level is adequate
  • Low oil pressure (normally-open): open when pressure is low, closed when pressure is adequate
  • High vibration (normally-closed): closed when still, open when vibrating
  • Water leak detector (normally-open): open when dry, closed when wet (leak detected)
The engineer’s first attempt is shown here, but it contains a serious error. Identify and correct this error:
Answer :
The Vib_high contact instruction should be drawn as normally-closed rather than normally-open as shown in the engineer’s first draft of the PLC program.
The program is designed to shut down the motor if ever the Shutdown bit goes to a 1 state. This means the motor will shut down if any of the permissive contact instructions become colored (i.e. “conductive” to virtual power).
We have been told that the realworld vibration switch is NC, which means its contact opens when vibration is excessive. This means high vibration causes that bit to be 0, which necessitates an NC contact instruction so that it will color under that condition.
More PLC Questions :
PLC Programming Questions & Answers – 1
PLC Programming Questions & Answers – 2
PLC Programming Questions & Answers – 3
PLC Programming Questions & Answers – 4
PLC Programming Questions & Answers – 5
PLC Programming Questions & Answers – 6
PLC Programming Questions & Answers – 7
PLC Ladder Logic Example based on Set Coil and Reset Coil
200+ Quiz on Electrical Meters, Measurement, and Troubleshooting
Step-by-Step Guide to Choose Right Fuse for a Panel
What is Siemens TDC? – Siemens Control System
What is NOR Flash Memory in PLC?
  • Bruce says:
    April 12, 2018 at 6:41 am
    The low water level is not fail safe the way you have it set up
Augmented Reality and Virtual Reality in Industrial Automation
Programmable Logic Controller (PLC) Questions and Answers – 7
Guided-wave Radar Asset Management Parameters
How to do Scaling for Analog Input in RSLogix 500?
Pressure Transmitter using Potentiometer and Diaphragm
PLC Input Output Modules
Functions of SCADA
Electronic Pressure Sensor with Bourdon Tube and LVDT
Why 4-20 mA Current Signal is used instead of Voltage Signal
Why Baud Rate is Important in Modbus Network
Industrial Gas Detection Systems
PLC based Gas Detection System using Ladder Logic Project
Foxboro pneumatic instruments
Pneumatic Force Balance Instrument
Repeat Until Statement in SCL Language
Siemens S7-200 PLC Ladder Logic
Programmable Logic Controller (PLC) Questions and Answers – 10
SCADA in Cloud
Cloud-Based SCADA Projects – Try Free Demo Account
Real-time and historical SCADA Trends
What are Trends in SCADA?
Yokogawa differential pressure transmitter
Basics of Differential Pressure Transmitters
Vortex Flow GIF
Working Principle of Vortex Flow Meter
X-Ray Spectroscopy Questions & Answers
Temperature Switch Working
Basics of Temperature Switch
DC Machines Circuit Model Objective Questions
Solenoid-Valve-Manual-Reset-function
Solenoid Valve with Manual Reset Working Principle
Differential Pressure Transmitter Zero Suppression
Basics of DP Transmitter Suppression and Elevation
Coal Hopper
Coal Based Fuel Feeding System for Boiler