Reading: PLC Program for Automatic Liquid Mixing Application
Inst Tools > Blog > Guest Articles > PLC Program for Automatic Liquid Mixing Application
Create a PLC Program for Automatic Liquid Mixing Application using ladder logic programming. Study about mixing process using PLC ladder diagram.
Last updated: November 3, 2023 10:34 am
Guest Articles PLC Tutorials
4 Comments
Create a PLC Program for Automatic Liquid Mixing Application using ladder logic programming. Study about mixing process using a PLC ladder diagram.
Liquid Mixing ApplicationDiagramProblem SolutionList of PLC inputs outputsPLC Ladder Diagram for Automatic Liquid Mixing ApplicationPLC Program ExplainedRuntime Test Cases
Problem Description
In many industries, there are lots of mixing system used for solutions mixing. Some plants use complete automation or semi-automation.
In a manual system, there are so many disadvantages such as lack of Accuracy, Time delay problems, loss of liquids, Time consumption, etc.
Here we are discussing the semi-automatic application of a mixing system.
Diagram
Problem Solution
For this example, we use PLC programming and for that we use Siemens S7-1200 PLC.
For easy explanation, we can consider simple example of mixing system as shown above.
In this application pure unmixed solution can be prepared by the operator using switches S1 and S2. And mixed solution or material can be prepared by the operator using switch S3.
Operator observes the level of the tank and he can discharge the liquid inside tank by operating valve V5.
Also the agitator motor M will be  in running while tank is being filled. We will provide interlock system so operator cannot operate both switches at same time.
V1, V3 and V5 are manual valves which is not connected to the PLC.
V2 and V4 are electronically operated valves which can be controlled by PLC.
Digital Inputs
There are three switches S1, S2 & S3
  • S1 : I0.0
  • S2 : I0.1
  • S3 : I0.3
Digital Outputs
We have two valves V2 & V4. one Agitator Motor M1
  • V2 : Q0.0
  • V4 : Q0.1
  • M1 : Q0.2
PLC Automatic Mixing
  • For this application, we used S7-1200 PLC and TIA portal software for programming.
  • In Network 1, we have taken NO contact of S1 (I0.0) and NC contact of S2 (I0.1) and S3 (I0.2) in series. By activating switch S1 operator can START the valve V2 for solution 1 (Liquid 1 ).
  • In Network 2, we have taken NO contact of S2 (I0.1) and NC contact of S1 (I0.0) and S3 (I0.2) in series. By activating switch S2 (I0.1) operator can START the valve V4 (Q0.1) for solution 2 (Liquid 2).
  • For both Networks 1 & 2,  A parallel connection we have taken, NO contact of S3 (I0.2) and in series with  NC contact of S1 (I0.0) and S2 (I0.1).
  • Because of the above parallel connection, operator can operate both valves by activating switch S3 (I0.2) for mixed solution (Liquid 1 & Liquid 2)
  • As per our condition, agitator M1 (Q0.2) should be activated automatically while tank is being filled. So we have taken NO contact of V2 (Q0.1) and in parallel NO contact of V4 (Q0.1) so agitator will be activated automatically by operating any switch.
Runtime Test Cases
Mixing PLC Logic
Note : The above PLC Logic provided for basic idea about application of PLC in Liquid Mixing Application. The Logic is limited and not complete application.
Author : Bhavesh
  • Continuous Filling PLC Operation
  • Ladder logic program to GE PLC
  • PLC Program Backup procedure
  • Conveyor Motor PLC Logic
  • PLC System Troubleshoot
PLC Program for Fish Feeding System
SFC Language in PLC Programming
Configuration of Input and Output Tags in Siemens Scada and PLC
4 Comments
  • shams afroz says:
    April 10, 2020 at 4:49 am
    Tons of teaching information for free,
    Thank you so much I am a program Learner.
    I have a MicroLogix 1100 processor with basic 10 inputs and 6 outputs. Will add some more IO’s.
    Planning to teach electricians and electrical engineers.
    Again Thanks
  • SHAMS says:
    April 10, 2020 at 7:54 pm
    THERE ARE 3 INPUTS 2 OUTPUTS. PLEASE CHECK THE ADDRESS OF COIL Q 0/2 INSTEAD Q 0/3 IN NETWORK #3
  • tun win says:
    December 8, 2021 at 1:59 pm
    I have never seen any diagram. Why
  • Mahalakshmi G says:
    June 25, 2024 at 1:28 pm
    give some information about hmi design
How to Upload Siemens PLC Programs?
How a PLC do the Scaling for a Sensor ?
Statement List (STL) to Find Highest Value
100 Electrical Circuit Breaker Quiz
Architecture of Allen Bradley PLC
PLC Analog I/O Potential Problems – Troubleshooting & Issues
PLC Programming for Pumping and Draining System
Basics of Ladder Diagram in PLC Programming
Auto Sugar Bag Filling Station
Opposite Acting Control Valves Application
PLC Ladder Logic for Opposite Acting Control Valves Application
Loop Diagram
In this article, we will learn the difference between Machine Expert Basic and Machine Expert software in Schneider PLC.
Difference between Machine Expert Basic and Machine Expert – Schneider PLC
PLC Documents
PLC System Documentation
Basics of Sinking and Sourcing
Midline output instruction
What is Midline Instruction in Siemens PLC?
Yokogawa DCS Tutorials - Configuration of Analog Input (Transmitter)
Yokogawa DCS Tutorials – Configuration of Analog Input (Transmitter)
Calculate voltage across RTD
Resistance Temperature Detector (RTD) Questions – 2
Contact less Tachometer
Types of Tachometers – Mechanical and Electrical Tachometers
Smart DP transmitter Formula
Smart DP Transmitter Flow Meter Calculations
Use of Temperature Transmitters instead of Direct Wiring
Thermocouple cold junction compensation
Why Thermocouple Reference Junction Compensation Required ?
Electric Circuits Objective Questions – Set 9
Difference between Absolute, Gauge and Differential Pressure Transmitters
Chlorine dioxide measurement principle
Chlorine dioxide Analyzer Principle