Reading: Orifice Flowmeter Rangeability
Inst Tools > Blog > Flow Measurement > Orifice Flowmeter Rangeability
The orifice flow meter only allows 3:1 rangeability to maintain accuracy. It is the most used flow measurement device in oil & gas plants.
Last updated: November 2, 2023 1:13 pm
Flow Measurement
2 Min Read
Orifice, combined with differential pressure transmitter, is the most used flow measurement device in oil & gas plants because of its low cost and its ease of installation and maintenance.
However, the orifice only allows 3:1 rangeability to maintain accuracy. This means, if one wants to measure a maximum flow of 10 MMscfd, then the minimum flow measurement that could be measured is only 3.3 MMscfd.
According to the Bernoulli principle, the relationship between the flow and pressure drop of fluid passing through an orifice is given by the following formulae:
Orifice Formulae
Q = Volumetric flowrate
dP = Measured pressure drop ρ = Density
Ao = Cross-sectional orifice area
Cf = Constant
Hence, flow value could be obtained by measuring pressure drop and the relationship between them is a square root.
Let’s say the orifice is intended for flow measurement of 0-10 MMscfd which is represented by 0-100 inH2O pressure drop (as shown below the curve)
Differential Pressure versus Flow Rate
At a maximum flow of 10 MMscfd, a change of 1% of full flow (0.1 MMscfd) to 9.9 MMscfd will be represented by a change of 2% of DP (from 100 inH2O to 98.01 in H2O).
The following table summarizes the value of flow, its corresponding pressure drop, and its dP change in percentage of full scale for a 1% change of full flow at the specified flow.
The less flow to be measured, the more sensitivity suffers.
Orifice Flow Table
  • Flow Control Loop
  • Flow Meter Interview Questions
  • What is Square Root Extractor?
  • Orifice Plate Flow Requirements
  • Flow Meter Calibration Procedure
What is a Coriolis Flow Meter?
Rotary Abutment Flow Meters Working Principle and Animation
Pressure based Flow Meters
Interview Questions on Flow Measurement
What is a Torbar? – Averaging Pitot Tubes
Lobed Impeller Flow Meters Working Principle
  • Asok Kumar Hait says:
    September 18, 2022 at 2:54 am
    The statement “orifice only allows 3:1 rangeability to maintain accuracy” is not clear. You haven’t explained why you are considering 3:1 rangeability for orifice plate. Also you haven’t explained what is the accuracy for Orifice plate measurement you have considered here.
    You may be knowing that using a multivariable transmitter, the rangeability of orifice plate can be increased to 10:1. Without multivariable orifice by changing the transmitter or by changing the orifice plate itself the rangeability of orifice can be increased substantially. In industry we are doing it frequently.
Reasons to Calibrate Different Types of Flow Meters
Volumetric Flow Calculations
Square-root characteristics of Differential Pressure Flow Meters
Flow Transmitter Rangeability
Oscillating Piston Flow Meters Working Principle
Basics of Orifice Plates
Advantages & Disadvantages of Different Flow Meters
Interferometer Principle
magnetic flow meter parts
What is a Magnetic Flow Meter?
Heat Tracing Problems
Paddle Wheel Flow Meter
Paddle Wheel Flow Meters – Principle, Advantages, Limitations
Circular Chart Recorder
How to Read Circular Chart Recorder for Flow Measurement?
Annubar flow principle
Different Types of Flow Elements
Coriolis Flow Meter Inaccuracy
Coriolis Flow Meter Uncertainty and Inaccuracy
Coriolis Mass Flow Meter Working Animation
Coriolis Meter Explained with Animation
Pressure Transmitter Re-Range Questions
Stability in Frequency Domain
Difference between HART and Foundation Fieldbus
HMI book
HMI Handbook
Compressor Shutdown Jobs
Compressor Shutdown Job – Instrumentation Engineer Duties
Volume Booster Working Principle
Control Valve Volume Booster Working Principle
Instrumentation Engineering Students Test
Process Control Fundamentals