Reading: Manually Interpreting Thermocouple Voltages
Inst Tools > Blog > Temperature Measurement > Manually Interpreting Thermocouple Voltages
Last updated: May 27, 2018 4:04 pm
The amount of voltage indicated by a voltmeter connected to a thermocouple is the difference between the voltage produced by the measurement junction (the point where the two dissimilar metals join at the location we desire to sense temperature at) and the voltage produced by the reference junction (the point where the thermocouple wires join to the voltmeter wires):
thermocouple voltages
Vmeter = VJ1 − VJ2
This makes thermocouples inherently differential sensing devices: they generate a measurable voltage in proportion to the difference in temperature between two locations. This inescapable fact of thermocouple circuits complicates the task of interpreting any voltage measurement obtained from a thermocouple. In order to translate a voltage measurement produced by a voltmeter connected to a thermocouple, we must add the voltage produced by the measurement junction (VJ2) to the voltage indicated by the voltmeter to find the voltage being produced by the measurement junction (VJ1). In other words, we manipulate the previous equation into the following form:
VJ1 = VJ2 + Vmeter
We may ascertain the reference junction voltage by placing a thermometer near that junction (where the thermocouple wire attaches to the voltmeter test leads) and referencing a thermocouple table showing temperatures and corresponding voltages for that thermocouple type. Then, we may take the voltage sum for VJ1 and re-reference that same table, finding the temperature value corresponding to the calculated measurement junction voltage. The National Institute of Standards and Technology (NIST) in the United States publishes tables showing junction voltages and temperatures for standardized thermocouple types. While it is possible to mathematically model a thermocouple junction’s voltage in the same way we may model an RTD’s resistance, the functions for thermocouples are less linear than for RTDs, and so tables are greatly preferred for practical use.
Also Check : Thermocouple Tables
To illustrate, suppose we connected a voltmeter to a type K thermocouple and measured 14.30 millivolts. A thermometer situated near the thermocouple wire / voltmeter junction point shows an ambient temperature of 73 degrees Fahrenheit. Referencing a table of voltages for type K thermocouples (in this case, the NIST “ITS-90” reference standard), we see that a type K junction at 73 degrees Fahrenheit corresponds to 0.910 millivolts. Adding this figure to our meter measurement of 14.30 millivolts, we arrive at a sum of 15.21 millivolts for the measurement (“hot”) junction. Going back to the same table of values, we see 15.21 millivolts falls between 701 and 702 degrees Fahrenheit. Linearly interpolating between the table values (15.203 mV at 701 oF and 15.226 mV at 702 oF), we may more precisely determine the measurement junction to be 701.3 degrees Fahrenheit.
The process of manually taking voltage measurements, referencing a table of millivoltage values, performing addition, then re-referencing the same table is rather tedious. Compensation for the reference junction’s inevitable presence in the thermocouple circuit is something we must do, but it is not something that must always be done by a human being. The next subsection discusses ways to automatically compensate for the effect of the reference junction, which is the only practical alternative for continuous thermocouple-based temperature instruments.
Also Check : Thermocouple Calculator
Spiral Bimetallic Thermometer Principle
Thermowell Insertion and Immersion Length
Calculate Temperature Coefficient of RTD
Thermocouple and its Principle
Why 4 wire RTD Measurement Accuracy is better than 2 and 3 wire RTD?
Testing a Thermocouple With a Multimeter
Foundation Fieldbus Temperature Transmitter Configuration
Non-contact Pyrometers Characteristics
Thermocouple Construction
Why we use Wheatstone bridge in RTD?
What is a Thermocouple ?
Thermocouple Questions and Answers
Questions on Thermocouple and Pyrometer
Thermal Imaging Temperature Measurement
RTD Construction
Introduction to RTDs
Temperature Transmitter Formula
Calculate Temperature Transmitter Output
Difference Between RTD, Thermocuples and Thermistors
Difference Between RTD, Thermocouple and Thermistor
Thermocouple Standard
Thermocouple Details
Three Wire RTD Wheatstone bridge Circuit
RTD Wheatstone Bridge Circuits
RTD Calibration
RTD Calibration
Peltier Effect
Peltier Effect Theory
RTD Questions & Answers
RTD Questions and Answers
Emergency ShutDown Valve Working Principle
ESDV : How it Works ?
pH Analyzers Interview Questions Answers
pH Analyzer Interview Questions and Answers
Deluge Valve Operation using Solenoid Valve Animation
Transformer Open Circuit and Short Circuit Test
What is a Memristor
What is a Memristor? Principle, Advantages, Applications
transistor-terminals
Basics of Transistors
Half Wave Diode Rectifier Quiz
Routine Tests of Transformers
Transformer Testing – Routine Tests of Transformers