Inst ToolsInst ToolsInst Tools
  • Courses
  • Automation
    • PLC
    • Control System
    • Safety System
    • Communication
    • Fire & Gas System
  • Instrumentation
    • Design
    • Pressure
    • Temperature
    • Flow
    • Level
    • Vibration
    • Analyzer
    • Control Valve
    • Switch
    • Calibration
    • Erection & Commissioning
  • Interview
    • Instrumentation
    • Electrical
    • Electronics
    • Practical
  • Q&A
    • Instrumentation
    • Control System
    • Electrical
    • Electronics
    • Analog Electronics
    • Digital Electronics
    • Power Electronics
    • Microprocessor
  • Request
Search
  • Books
  • Software
  • Projects
  • Process
  • Tools
  • Basics
  • Formula
  • Power Plant
  • Root Cause Analysis
  • Electrical Basics
  • Animation
  • Standards
  • 4-20 mA Course
  • Siemens PLC Course
Reading: How to Calculate mmWC Range of Level Transmitter with Examples?
Share
Font ResizerAa
Inst ToolsInst Tools
Font ResizerAa
  • Courses
  • Design
  • PLC
  • Interview
  • Control System
Search
  • Courses
  • Automation
    • PLC
    • Control System
    • Safety System
    • Communication
    • Fire & Gas System
  • Instrumentation
    • Design
    • Pressure
    • Temperature
    • Flow
    • Level
    • Vibration
    • Analyzer
    • Control Valve
    • Switch
    • Calibration
    • Erection & Commissioning
  • Interview
    • Instrumentation
    • Electrical
    • Electronics
    • Practical
  • Q&A
    • Instrumentation
    • Control System
    • Electrical
    • Electronics
    • Analog Electronics
    • Digital Electronics
    • Power Electronics
    • Microprocessor
  • Request
Follow US
All rights reserved. Reproduction in whole or in part without written permission is prohibited.
Inst Tools > Blog > Level Measurement > How to Calculate mmWC Range of Level Transmitter with Examples?

How to Calculate mmWC Range of Level Transmitter with Examples?

Calculate the inch or mmWC range of the remote seal level transmitter based on the field instrument mounting or installation position.

Last updated: September 28, 2022 2:40 pm
R Jagan Mohan Rao
Level Measurement
8 Comments
Share
5 Min Read
SHARE

How to calculate the inch or mmWC range of the level transmitter and explain with different examples.

Contents
Remote Capillary Level Transmitter Mounted at Zero LevelRemote Capillary Level Transmitter Mounted below Zero LevelRemote Capillary Level Transmitter Mounted Above SealRemote Capillary Level Transmitter Installed between SealsRemote Capillary Level Transmitter Mounted on Closed Tank

We need to configure the Lower Range Value (LRV) and Upper Range Value (URV) for the level transmitters after installation in the field. The formula to calculate the LRV (4mA) and URV (20mA) will always change based on the transmitter mounting or installation position.

The below example shows the different types of level transmitters installation.

Remote Capillary Level Transmitter Mounted at Zero Level

Remote capillary Level Transmitter mounted at zero level

  • dH = Vertical distance from the transmitter to high-pressure seal
  • dL = Vertical distance from the transmitter to low-pressure seal
  • Lmax = the maximum level of the process above the high-pressure seal and typically the 20 mA lower range value
  • Lmin = the minimum level of the process above the high-pressure seal and typically the 4 mA lower range value
  • SGf = specific gravity of fill fluid
  • SGp = specific gravity of process fluid

Tank span = Lmax *SGp – Lmin *SGp

Tank span = (108 in.* 0.75) – (0 in.* 0.75) = 81 inH2O

4 mA = Lmin *SGp + dH *SGf

4 mA = (0 in. 0.75) + (0 in.* 0.934) = 0 inH2O

20 mA = Lmax* SGp + dH * SGf

20 mA = (108 in.* 0.75) + (0 in.* 0.934) = 81 inH2O

Span = 81 inH2O (81 to 0 inH2O)

Note: Both installations would have the same calculated range points.

Note: Silicone 200 has a specific gravity of 0.934.

Remote Capillary Level Transmitter Mounted below Zero Level

Remote Capillary Level Transmitter Mounted below the Zero Level

Tank span = Lmax* SGp – Lmin * SGp

Tan span = (108 in.* 0.75) – (0 in*. 0.75) = 81 inH2O

4 mA = Lmin *SGp + (dH* SGf)

4 mA = (0 in.* 0.75) + (60 in.* 0.934) = 56.04 inH2O

20 mA = Lmax *SGp + (dH *SGf)

20 mA = (108 in* 0.75) + (56.04* inH2O) = 137.04 inH2O

Span = 81 inH2O (137.04 to 56.04 inH2O)

Note: Silicone 200 has a specific gravity of 0.934.

Remote Capillary Level Transmitter Mounted Above Seal

Remote Capillary Level Transmitter Mounted Above the Top Seal

Tank span = Lmax SGp – Lmin SGp

Tank span = (108 in. 0.75) = 81 inH2O

4 mA = Lmin * SGp +(dH * SGf)

4 mA = (0 in * 0.75) + (–120 in *. 0.934) = –112.08 inH2O

20 mA = Lmax * SGp + (dH* SGf)

20 mA = (108 in * 0.75) + (–120 in.* 0.934) = –31.08 inH2O

Span = 81 inH2O (–112.08 to –31.08 inH2O)

Note The height of the transmitter (Hd Sg) should not be greater than approximately 394 inH2O (14.2 PSI) not to exceed the 0.5 PSIA sensor limits of a coplanar DP or GP.

Remote Capillary Level Transmitter Installed between Seals

Remote capillary transmitter installed between the seals.

Tank span = Lmax SG

Tank span = 108 in. 0.75 = 81 inH2O

4 mA = Lmin *SGp – (dL* SGF) +(dH * SGf)

4 mA = (0 in. 0.75) – (60 in.* 0.934) + (– 60 in.* 0.934) = –112.08 inH2O

20 mA = Lmax * SGp – (dL * SGf) +(dH SGf)

20 mA = (108 in. 0.75) – (60 in. 0.934) + (–60 in. 0.934) = –31.08 inH2O

Span = 81 inH2O (–112.08 to –31.08 inH2O) 

Note: Silicone 200 has a specific gravity of 0.934.

Remote Capillary Level Transmitter Mounted on Closed Tank

Remote capillary transmitter mounted on Closed Tank

Tank span = Lmax *SGp – Lmin *SGp

Tank span = (108 in.* 0.75) = 81 inH2O

4 mA = Lmin *SGp – (dL*SGf)

4 mA = (0 in.* 0.75) – (120 in.* 0.934) = –112.08 inH2O

20 mA = Lmax *SGp – (dL* SGf)

20 mA = (108 in.* 0.75) – (120 in.* 0.934) = –31.08 inH2O

Span = 81 inH2O (–112.08 to –31.08 inH2O)

Note: Silicone 200 has a specific gravity of 0.934.

Source: manual-rosemount-dp-level-transmitters

Read Next:

  • Formulas to calculate mA from PV
  • Types of Tank Gauging
  • Percentage to Process Variable Conversion
  • Rotary Level Switch Principle
  • DP Level Transmitter Problems
Don't Miss Our Updates
Be the first to get exclusive content straight to your email.
We promise not to spam you. You can unsubscribe at any time.
Invalid email address
You've successfully subscribed !

Continue Reading

Level Measurement with Wet leg and Installed Below Tapping Point
Sight Glass Level Measurement Principle
How a Level Switch Works
What is a Bridle?
Tilt Level Switch Working Principle
What is Dip Tape Level Measurement?
Share This Article
Facebook Whatsapp Whatsapp LinkedIn Copy Link
Share
8 Comments
  • DB says:
    December 28, 2019 at 11:55 pm

    Why does Tank span = (180 in.* 0.75) – (0 in*. 0.75) = 81 inH2O? as far as I can tell, 180*0.75 = 135? What’s going on here that am I missing?

    Reply
  • Almahadi says:
    January 10, 2020 at 2:57 pm

    This is very Good and practically Hope I find a lot of engineering that can this tools help them

    Reply
  • Rathete says:
    April 30, 2020 at 5:19 am

    I’m in Concord with the initial commentor,My line of understanding that calculation,is blurry,won’t some light be shed?.I’m talking about what DN is commenting about

    Reply
  • giby says:
    June 10, 2020 at 4:00 am

    i think the Lmax is 108 not 180..

    Reply
  • Kamesh.b says:
    November 26, 2020 at 11:42 am

    Not thinking
    Here in the examples all 180 are ,misplaced actually it was 108

    And in 3rd example dh & dl are also wrong position according to theory

    May this calculation will be correct by author

    Reply
  • R. JAGAN MOHAN RAO says:
    November 28, 2020 at 7:11 pm

    I thank everyone for their comments on the mistakes. Corrections have been done and updated in the article. I also thank Mr. Bharadwaj Reddy Garu for bringing various comments to my notice.

    Reply
  • jamal alsaad says:
    March 14, 2021 at 10:56 pm

    I need to know the minimum pipe size in high side used to measure fuel tank level in order not to cause Blockage due to rust dirty in fuel

    Reply
  • Franklin says:
    December 14, 2021 at 3:05 pm

    Please why use of silicon 200 specific gravity

    Reply

Leave a Reply Cancel reply

Your email address will not be published. Required fields are marked *

Stay Connected

128.3kFollowersLike
69.1kFollowersFollow
210kSubscribersSubscribe
38kFollowersFollow

Categories

Explore More

Overview of Tank Gauging Technologies
Level Indicators Working Principle
Paddle Wheel Level Switch Principle
Displacer (buoyancy) Level Transmitter Principle, Limitations, Design, Installation & Calibration
Probe Type GWR Level Transmitter Working Animation
Identify Characteristics of Level Measurement Technologies
Displacer Level Measurement Calculations
Ultrasonic Level Measurement

Keep Learning

Closed Tank DP Level Transmitter

How to Find LRV and URV of Closed Tank DP Level Transmitter

Ultrasonic Transmitters vs. Guided Wave Radar Transmitters

Ultrasonic Transmitters vs Guided Wave Radar for Level Measurement

Stilling wells

Stilling Wells for Level Measurement

Bubbler Level Measurement Animation

Bubbler Level Measurement Animation

Closed Tank Level Measurement using DP Transmitter

Closed Tank Level Measurement using DP Transmitters

Applications of Tilting Level Switch

How Tilt Level Switch Works ?

Surface Detector Level Measurement System

Surface Detector Level Gauges (Plumb-bob)

Closed Tank Remote Seal Level Transmitter calculation

Remote Seal Transmitters Ranging Calculation

Learn More

Use of Isolators and Barriers in Electrical Panel

Use of Isolators and Barriers in Electrical Panel

Allen-Bradley MicroLogix controller

Programmable Logic Controller (PLC) Questions and Answers – 15

water treatment station

What is a Vent Filter? – Water Treatment Plant

Quality Control Inspector Questions

Quality Control Inspector Interview Questions and Answers

level-transmitter-calibration-procedure

Level Transmitter Calibration Procedure

Pneumatic Control Mechanisms Objective Questions

Pneumatic Control Mechanisms Objective Questions

Three-Phase Wye Wiring System

4-Wire, Three-Phase Wye Wiring System

Pressure Transmitter Troubleshooting Tips

Pressure Transmitter Troubleshooting Tips

Menu

  • About
  • Privacy Policy
  • Copyright

Quick Links

  • Learn PLC
  • Helping Hand
  • Part Time Job

YouTube Subscribe

Follow US
All rights reserved. Reproduction in whole or in part without written permission is prohibited.
Welcome Back!

Sign in to your account

Username or Email Address
Password

Lost your password?