Inst ToolsInst ToolsInst Tools
  • Courses
  • Automation
    • PLC
    • Control System
    • Safety System
    • Communication
    • Fire & Gas System
  • Instrumentation
    • Design
    • Pressure
    • Temperature
    • Flow
    • Level
    • Vibration
    • Analyzer
    • Control Valve
    • Switch
    • Calibration
    • Erection & Commissioning
  • Interview
    • Instrumentation
    • Electrical
    • Electronics
    • Practical
  • Q&A
    • Instrumentation
    • Control System
    • Electrical
    • Electronics
    • Analog Electronics
    • Digital Electronics
    • Power Electronics
    • Microprocessor
  • Request
Search
  • Books
  • Software
  • Projects
  • Process
  • Tools
  • Basics
  • Formula
  • Power Plant
  • Root Cause Analysis
  • Electrical Basics
  • Animation
  • Standards
  • 4-20 mA Course
  • Siemens PLC Course
Reading: Electronic Valve positioners
Share
Font ResizerAa
Inst ToolsInst Tools
Font ResizerAa
  • Courses
  • Design
  • PLC
  • Interview
  • Control System
Search
  • Courses
  • Automation
    • PLC
    • Control System
    • Safety System
    • Communication
    • Fire & Gas System
  • Instrumentation
    • Design
    • Pressure
    • Temperature
    • Flow
    • Level
    • Vibration
    • Analyzer
    • Control Valve
    • Switch
    • Calibration
    • Erection & Commissioning
  • Interview
    • Instrumentation
    • Electrical
    • Electronics
    • Practical
  • Q&A
    • Instrumentation
    • Control System
    • Electrical
    • Electronics
    • Analog Electronics
    • Digital Electronics
    • Power Electronics
    • Microprocessor
  • Request
Follow US
All rights reserved. Reproduction in whole or in part without written permission is prohibited.
Inst Tools > Blog > Control Valves > Electronic Valve positioners

Electronic Valve positioners

Last updated: May 4, 2020 10:17 am
Editorial Staff
Control Valves
No Comments
Share
10 Min Read
SHARE

The purpose of a valve positioner is to ensure the mechanical valve’s position matches the command signal at all times.

Thus, a valve positioner is actually a closed-loop control system in its own right: applying as much or as little pressure to the actuator in order to achieve the commanded valve stem position at all times.

Mechanical valve positioners use levers, cams, and other physical components to achieve this closed-loop control. Electronic valve positioners, such as the Fisher model DVC6000, use an electronic sensor to detect valve stem position, a microprocessor to compare that sensed stem position against the control signal by mathematical subtraction (error = position − signal), then a pneumatic signal converter and relay(s) to send air pressure to the valve actuator.

Electronic Valve positioners

A simplified diagram of a generic electronic valve positioner is shown here:

 

Electronic Valve positioners

As you can see from this diagram, there is a lot going on inside an electronic positioner. We have not just one, but two control algorithms working together to maintain proper valve position:

  • one monitoring and controlling pressure applied to the actuator (compensating for changes in air supply pressure that might otherwise affect the valve’s position) and
  • the other monitoring and controlling stem position itself, sending a cascaded control signal to the pressure control components.

The command signal (sent from the process loop controller, PLC, or other control system) tells the positioner where the valve stem should be positioned. The first controller inside the positioner (PI) calculates how much air pressure at the actuator should be needed to achieve the requested stem position.

The next controller (PID) drives the I/P (current-to-pressure) converter as much as necessary to achieve that pressure.

If anything causes the valve stem to not be at the commanded position, the two controllers inside the positioner work together to force the valve to its proper position.

Not only do electronic valve positioners achieve superior position control when compared to mechanical valve positioners, but their array of sensors and digital communication ability provides a new level of diagnostic data both to maintenance personnel and the supervising control system (if programmed to monitor and act on this data).

Examples of diagnostic data provided by electronic positioners include:

  • Supply air pressure
  • Actuator air pressure
  • Ambient temperature
  • Position and pressure errors
  • Total valve stem travel (like an odometer in an automobile)

Additionally, the microprocessor embedded within an electronic valve positioner is capable of performing self-tests, self-calibrations, and other routine procedures traditionally performed by instrument technicians on mechanical valve positioners.

Having access to such measurements as total valve stem travel even allows an electronic positioner to predictively calculate packing wear-out time, automatically flagging a maintenance alarm notifying operators and/or instrument technicians when the valve’s stem packing will need to be replaced!

A useful capability of some “smart” valve positioners – since they monitor actuator air pressure in addition to stem position – is the ability to maintain a respectable degree of valve control in the event of a stem position sensor failure.

If the microprocessor detects a failed (off-scale) position feedback signal, it may be programmed to continue operating the valve based on pressure alone: adjusting the applied air pressure to the valve actuator according to the pressure/position function it has recorded in the past.

While not strictly functioning as a positioner any more since it cannot sense valve stem position, it may still fulfill its role as a volume booster (compared to the flow capacity of a typical I/P) and give reasonable control over the valve where any other (non-smart) valve positioner would actually make matters worse in the event of losing its stem position feedback.

With any purely mechanical positioner, the control valve will typically “saturate” either fully open or fully closed if the stem position feedback linkage falls off. Not so with the best “smart” positioners!

Perhaps the most significant diagnostic data provided by an electronic positioner is the comparison of actuator pressure versus stem position, usually expressed in the form of a graph.

Actuator pressure is a direct reflection of force applied by the actuator to the valve stem, since the relationship between force and pressure for either a piston or a diaphragm is simply F = PA, where area (A) is constant.

Thus, a comparison of actuator air pressure versus stem position is really an expression of force-versus-position for the valve.

This so-called valve signature is incredibly useful in identifying and correcting such problems as excessive packing friction, valve trim interference, and plug/seat fit problems.

A screenshot showing a “valve signature” (taken from an Emerson software product called ValveLink, as part of their AMS suite) appears here, showing the behavior of an air-to-open Fisher E-body globe valve:

actuator pressure versus stem position

Two plots of actuator pressure versus stem position are shown in this graph, one red and one blue.

The red graph shows the valve’s response in the opening direction where additional pressure is required to overcome packing friction as the valve moves open (up).

The blue graph shows the valve as it closes, less pressure applied to the diaphragm now to allow the spring’s compression to overcome packing friction as the valve moves closed (down) to its resting state.

The sharp turns at each end of this graph show where the valve stem reaches its end positions and cannot move farther despite further changes in actuator pressure.

Each plot is roughly linear in accordance with Hooke’s Law describing the behavior of the valve spring, where the force applied to a spring is directly proportional to the displacement (compression) of that spring: F = kx.

Any departure from a single linear plot indicates some other force(s) besides spring compression and pneumatic force acting on the valve stem.

This is why we see two plots vertically offset from each other: packing friction is another force acting on the valve stem in addition to spring compression and the force exerted by air pressure on the actuator diaphragm.

The relatively small magnitude of this offset as well as its consistency indicates that packing friction in this valve is “healthy.” The more packing friction this valve experiences, the more vertically-offset the two plots will be.

The sharp down-turn at the left-hand end of the graph where the valve plug contacts the seat is called the seating profile.

Located at the end of the plot where the valve closes off, the seating profile holds much useful information about the physical condition of the plug and seat.

As these trim parts wear in a control valve, the shape of the seating profile changes accordingly. Irregular seating profiles may diagnose seat erosion, galling, or a number of other maladies.

By zooming in on the lower-left end of the valve signature graph, the seating profile may be examined in fine detail.

A seating profile taken of a Fisher E-body globe valve in pristine condition appears here:

Control Valve seating profile

If the maintenance staff of a particular facility are diligent enough to record the valve signatures of its control valves after assembly or rebuild, the “original” signature of any particular control valve may be compared against the signature of the same control valve taken at any later date, allowing qualitative determinations of wear without having to disassemble the valves for inspection.

Interestingly, this relationship of actuator pressure (force) to stem position is also available in the electronic positioners used with some modern electrically-actuated valves.

In the case of an electric actuator, force applied to the valve stem directly relates to motor current, which is easily measured and interpreted by the electronic positioner.

Thus, even with a different actuator technology, the same kind of diagnostic data may be presented in graphical form for the purpose of more easily diagnosing valve problems.

These diagnostics apply even to open/close motor-operated valves not used for throttling service, and are especially useful on gate, plug, and ball-type shut-off valves where seat engagement is substantial for tight shut-off.

Articles You May Like :

Pneumatic Instrumentation

What is Valve Packing ?

Inherent vs Installed Characteristics

Pneumatic Amplifying Relays

Diaphragm Valves Construction

Don't Miss Our Updates
Be the first to get exclusive content straight to your email.
We promise not to spam you. You can unsubscribe at any time.
Invalid email address
You've successfully subscribed !

Continue Reading

Purpose of 100% and 30% Feed Control Valves in a Power Plant
How to Reduce the Control Valve Noise?
Control Valve Interview Questions and Answers
Functional Testing of Control Valve Positioners
Control Valve Volume Booster Working Principle
Classification of Control Valves
Share This Article
Facebook Whatsapp Whatsapp LinkedIn Copy Link
Share
Leave a Comment

Leave a Reply Cancel reply

Your email address will not be published. Required fields are marked *

Stay Connected

128.3kFollowersLike
69.1kFollowersFollow
210kSubscribersSubscribe
38kFollowersFollow

Categories

Explore More

Direct Lift Diaphragm Solenoid Valve Principle
Current to Pressure (I/P) Converter Principle
What is Gate Valve ?
Solving Control Valve Hunting: Instrument Troubleshooting
Bellows Seal Valve Working Principle
What is Ball Valve ?
Self Actuated Pressure Control Valve Functional Testing
What is Cavitation? What are the Causes?

Keep Learning

Lift check valves

What is Lift Check Valve ?

control valve sequencing

Control Valve Sequence Methods

Y Body Globe Valve

Globe Valve Body Design

Valve Basics

Basics of Control Valves

Air Filter Regulator Working Principle Animation

Control Valves Quiz

Interactive Control Valve Parts Quiz: Drag & Drop Challenge

Procedure for the Repair of Control Valve

Basic Steps and Procedure for the Repair of Control Valve

Control Valve pressure recovery

What is Control Valve Flashing ?

Learn More

reactor vessel

Practical Process Control System Questions & Answers – 5

Process Control Terms

143 Process Control Terms and Glossary – Questions Answers

PID Simulator

PID Simulator Download

Optical Level Switch Principle

Optical Level Switch Working Principle

Instrumentation Basics - Range Conversion Formula and Examples

Instrumentation Basics – Range Conversion Formula and Examples

Level Sensor Pressure vessel mounting

Level Instruments Design Rules

Statement List (STL) to Find Highest Value in the Data Block

Statement List (STL) to Find Highest Value

Differential Pressure Sensor for Filtration Monitoring

Differential Pressure Sensor for Filtration Monitoring

Menu

  • About
  • Privacy Policy
  • Copyright

Quick Links

  • Learn PLC
  • Helping Hand
  • Part Time Job

YouTube Subscribe

Follow US
All rights reserved. Reproduction in whole or in part without written permission is prohibited.
Welcome Back!

Sign in to your account

Username or Email Address
Password

Lost your password?