Reading: Current to Pressure (I/P) Converter Calibration Procedure
Inst Tools > Blog > Calibration > Current to Pressure (I/P) Converter Calibration Procedure
Last updated: October 4, 2019 12:27 pm
Calibration
4 Comments
2 Min Read
A “current to pressure” converter (I/P) converts an analog signal\ (4 to 20 mA) to a proportional linear pneumatic output (3 to 15 psig).
Its purpose is to translate the analog output from a control system into a precise, repeatable pressure value to control pneumatic actuators/operators, pneumatic valves, dampers, vanes, etc.
Principle :
Its force balance principle is a coil suspended in a magnetic field on a flexible mount.
At the lower end of the coil is a flapper valve that operates against a precision ground nozzle to create a backpressure on the servo diaphragm of a booster relay.
The input current flows in the coil and produces a force between the coil and the flapper valve, which controls the servo pressure and the output pressure.
Also Read :  Current to Pressure (I/P) Converter Theory
Calibration :
Required Apparatus:
1. Air Filter Regulator
2. I/P Converter
3. Master Pressure gauge (For Measurement of I/P Output pressure)
4. mA Source (to feed mA to I/P Converter)
Calibration Setup :
Current to Pressure Converter Calibration Procedure
Calibration Procedure :
  1. Inlet air supply to be set at 20 psi in AFR
  2. Feed 4mA from source to I/P converter
  3. Observe master pressure gauge , it should show 3psi
  4. If it is not showing (3psi) adjust I/P ZERO up to obtain the 3psi
  5. Feed 20mA from source to I/P converter
  6. Observe master pressure gauge , it should show 15 psi
  7. If it is not showing 15 psi- adjust I/P SPAN up to obtain the 15 psi
  8. After completion of above procedure again feed 4mA-observe 3psi 20mA-observe 15psi
  9. Up to achieve the correct output from I/P converter repeat the step 2 to 7.
After calibration following to be done:
  1. All the readings to be entered in calibration report.
  2. Calibration sticker to be adhesived.
Uncertainty Calculations of Pressure Calibration
Calibration of Pyrometers using Black Body
How to Commission WirelessHART Transmitter With Gateway
Prover Tank Calibration and Mass Flow Meter Verification Procedure
pH Analyzer Calibration and Troubleshooting
Pressure Transmitter Calibration at the bench
4 Comments
  • Salah says:
    March 22, 2018 at 7:02 am
    Very clear and simple explanation, perfect, thank you
  • Yuriy says:
    May 4, 2018 at 11:53 pm
    I don’t understand why 4mA corresponds to 3 psi?Could you help me?!
    • yo says:
      August 18, 2023 at 9:58 pm
      same reason why you don’t use 0mA. if the pressure drops below 3PSI, the line is probably disconnected of you have a bad leak.
      3psi is the minimum, below that you have a problem.
  • OFAGBE Eric GODWIN says:
    September 3, 2019 at 4:18 pm
    Those are the standard lower limits of calibration for current and pressure respectively in instrumentation. Same way the upper limits are 20mA and 15psig. So as the topic is trying to explain conversion from one signal to the other, there is need to understand how each corresponds to the other
Magnehelic Gauge Calibration
DeadWeight Tester Questions
DP Level Transmitter with Zero Suppression Calibration
Difference between Repeatability and Reproducibility
Transmitter Calibration Procedure
Turbidity Sensor Calibration Procedure
Calibration MCQ – Terminology and Glossary Questions
Ultrasonic Level Transmitter Principle, Limitations, Calibration and configuration
Sand Probe Functional Testing
Closed-tank-DP-Level-Transmitter-with-cleaning-leg-Calibration
DP Diaphragm Capillary Seal Level instrument
DP Diaphragm Capillary Seal Level instrument Calibration Procedure
Instrumentation Engineer’s Calibration Mistakes
Comparison of Accuracy and Precision
Difference between Accuracy and Precision
Solenoid Valve Functional Testing
As-found and As-left Calibration
As-found and As-left Documentation during Calibration
HART Transmitter Calibration
How are HART instruments Calibrated?
What is a Core Type Transformer
Difference Between Core and Shell Transformers
PLC Program using Counters
PLC Counters Program
PLC-Complete-Training-Package
Free PLC Training Software Download
Simple RL Circuit
Impedance in RL Circuits
HART Communication Tutorial 2
Tube Fitting Parts
Procedure for Crimping the Connector
Digital Instrument Example
Digital Measuring Instruments – Types, Functions, Advantages, Disadvantages
Gearbox within week Failing Journal Bearing upset Plant Operations