Inst ToolsInst ToolsInst Tools
  • Courses
  • Automation
    • PLC
    • Control System
    • Safety System
    • Communication
    • Fire & Gas System
  • Instrumentation
    • Design
    • Pressure
    • Temperature
    • Flow
    • Level
    • Vibration
    • Analyzer
    • Control Valve
    • Switch
    • Calibration
    • Erection & Commissioning
  • Interview
    • Instrumentation
    • Electrical
    • Electronics
    • Practical
  • Q&A
    • Instrumentation
    • Control System
    • Electrical
    • Electronics
    • Analog Electronics
    • Digital Electronics
    • Power Electronics
    • Microprocessor
  • Request
Search
  • Books
  • Software
  • Projects
  • Process
  • Tools
  • Basics
  • Formula
  • Power Plant
  • Root Cause Analysis
  • Electrical Basics
  • Animation
  • Standards
  • 4-20 mA Course
  • Siemens PLC Course
Reading: Control Valve Cv calculation
Share
Font ResizerAa
Inst ToolsInst Tools
Font ResizerAa
  • Courses
  • Design
  • PLC
  • Interview
  • Control System
Search
  • Courses
  • Automation
    • PLC
    • Control System
    • Safety System
    • Communication
    • Fire & Gas System
  • Instrumentation
    • Design
    • Pressure
    • Temperature
    • Flow
    • Level
    • Vibration
    • Analyzer
    • Control Valve
    • Switch
    • Calibration
    • Erection & Commissioning
  • Interview
    • Instrumentation
    • Electrical
    • Electronics
    • Practical
  • Q&A
    • Instrumentation
    • Control System
    • Electrical
    • Electronics
    • Analog Electronics
    • Digital Electronics
    • Power Electronics
    • Microprocessor
  • Request
Follow US
All rights reserved. Reproduction in whole or in part without written permission is prohibited.
Inst Tools > Blog > Control Valves > Control Valve Cv calculation

Control Valve Cv calculation

Last updated: May 24, 2019 7:31 pm
Editorial Staff
Control Valves Formulas
9 Comments
Share
6 Min Read
SHARE

In deciding the size of the control valve that (Port Size) we need to calculate the Cv value of the process (Calculated Cv) by calculating Cv has educated more than 50 years, which is involved in. such as the Renault number (Reynolds number), flow rate (Flow), the Shock (Choking), the involved joints in pipes (Fitting) and the other by the values ​​of these.

Contents
Cv value calculationA) Simple Cv Value Formula: Case of the LiquidB) imple Cv Value Formula: Case of the GasC) Simple Cv Value Formula: Case of the Steam (Vapor)

This reference standard IEC 60534-2-1: 1998 (International Electro technical Commission), which is standard valve manufacturer mainly quoted. The coefficient Cv IEC standards are highly complex.

I recommend using the control valve manufacturer has provided. However, to be considered under the verification e Cv easier we have a simple formula Cv value can be calculated following them.

Cv value calculation

A) Simple Cv Value Formula: Case of the Liquid

Control Valve Cv Value Formula for Liquid

Q L : Flow rate (m3 / H).

△ P : Differential pressure (kg / cm 2 )

G L : Specific Gravity (Water = 1)

B) imple Cv Value Formula: Case of the Gas

I) Non-choked flow   ΔP <P1 / 2

CV Value Formula for Gas & Non Choked Flow

Q G  :  Flow rate (M 3 / H @ 15 o C , 1atm.)

△ P :   Differential pressure (kg / cm 2 )

G G :   Specific Gravity (Air = 1)

T :  Temperature ( o C)

P M :  (P1 P2) / 2

II) choked flow ΔP ≥ P1 / 2

CV Value Formula for Gas & Choked Flow

Q G   :  Flow rate (M 3 / H @ 15 o C, 1atm.)

P 1    :   Inlet pressure (kgf / cm 2 , ABS)

G G   :   Specific Gravity (Air = 1)

T  :  Temperature ( o C)

C) Simple Cv Value Formula: Case of the Steam (Vapor)

I) Saturation Vapor: Non-choked flow   ΔP <P1 / 2

CV Value Formula for Steam & Saturation Vapour Non choked flow

Q s  :   Flow rate (kg / H)

Y    :    Vapor Correction factor (Water Vapor = 19.4)

△ P :   Differential pressure (kg / cm 2 )

P M:   (P1 P2) / 2

II) Vapor Saturation: choked flow ΔP ≥ P1 / 2

CV Value Formula for Steam & Saturation Vapour choked flow

Q s :  Flow rate (kg / H)

Y   :   Vapor Correction factor (Water Vapor = 19.4)

P 1 :   Inlet pressure (kgf / cm 2 ABS.)

III) Wet Vapor: Non-choked flow   ΔP <P1 / 2

CV Value Formula for Steam & Wet Vapour Non choked flow

Q s  :  Flow rate (kg / H)

X    :  Quality of Vapor (X = 1 is Dry Steam)

Y  :    Vapor Correction factor (Water Vapor = 19.4)

△ P :  Differential pressure (kg / cm 2 )

P M:  (P1 P2) / 2

IV) Wet Vapor: choked flow ΔP ≥ P1 / 2

CV Value Formula for Steam & Wet Vapour choked flow

Q s :  Flow rate (kg / H)

X  :    Quality of Vapor (X = 1 is Dry Steam)

Y :     Vapor Correction factor (Water Vapor = 19.4)

P 1 :  Inlet pressure (kgf / cm 2 ABS.)

v) Superheated Vapor: Non-choked flow   ΔP <P1 / 2

CV Value Formula for Steam & Superheated Vapour Non choked flow

Q s  :  Flow rate (kg / H)

Y  :    Vapor Correction factor (Water Vapor = 19.4)

△ P : Differential pressure (kg / cm 2 )

S :   Superheat ( o C)

P M :  (P1 P2) / 2

VI) Superheated Vapor: choked flow ΔP ≥ P1 / 2

CV Value Formula for Steam & Superheated Vapour choked flow

Q s :  Flow rate (kg / H)

Y :     Vapor Correction factor (Water Vapor = 19.4)

S :     Superheat ( o C)

P 1 :  Inlet pressure (kgf / cm 2 ABS)

In the example for calculating it. Time calculation aware of it. The manufacturing unit will have a total abs.

Example # 1

Application : Fluid Water

Flow rate 50 M 3 / HR.

Inlet Pressure 10 kgf / cm 2 G.

Outlet Pressure 5 kgf / cm 2 G.

Pressure different 5 kgf / cm 2 G.

Temperature 120 degree C

Density 943 kg / M 3

Because the fluid is a liquid So we will use the formula

CV Value Formula for Liquid

Q L = 50 M 3 / HR.

G L = 943 kg / M 3   Convert to (UNIT Water = 1) = 0.943.

ΔP = 5 kg / cm 2.

So,

Cv = 1.17 (50) x sqrt (0.943 / 5).

Cv = 25.4

================================================== =====

Example # 2

Application : Fluid Gas

Flow rate 48,000 Sm3 / hr

Inlet Pressure 32 kgf / cm2 Convert to absolute pressure = 33.03 kgf / cm2 (A).

Outlet Pressure 15 kgf / cm2 convert to absolute pressure = 16.03 kgf / cm2 (A).

Pressure different 17 kgf / cm 2.

Temperature 240 degree C

Density 0.86 Air = 1

Because the fluid is a gas and ΔP ≥ P1 / 2 so we will use the formula.

CV Value Formula for Gas & Choked Flow

Cv = (48000 / (248 × 33.03)) x sqrt (0.86 x (273 240)).

Cv = 123.08

Articles You May Like :

Diaphragm Solenoid Valve Principle

Valve Technician Interview Questions

What is Butterfly Check Valve ?

Control Valve Tips and Tricks

Types of Control Valves Noise

Don't Miss Our Updates
Be the first to get exclusive content straight to your email.
We promise not to spam you. You can unsubscribe at any time.
Invalid email address
You've successfully subscribed !

Continue Reading

Reversing Control Valve Actuator Fail Safe Mode
Compare Relief Valve and Safety Valve
Displacer Level Measurement Calculations
Control Valve Parts Questions and Answers
When to choose Full Bore Valve or Reduced Bore Valve ?
The Replacement Procedure for Control Valve Stem Packing
Share This Article
Facebook Whatsapp Whatsapp LinkedIn Copy Link
Share
9 Comments
  • RAMESHB says:
    January 26, 2016 at 1:33 pm

    Sir,
    l am working in power plant plz send electrical questions and answers
    Sir urged arrivals very useful
    thank u sir

    Reply
    • S Bharadwaj Reddy says:
      January 26, 2016 at 3:20 pm

      Hello Ramesh,
      For Electrical Questions & Answers Please Click Here

      Reply
    • aslam says:
      January 27, 2016 at 3:11 pm

      Sir, I am aslam khan please explain hydraulic control valve working principles and also explain i/p working hydraulic oil possible

      Reply
  • Mohit Bansal says:
    February 13, 2016 at 1:13 pm

    Please share the calibration procedure (steps) for calibration of flow Instrumentation like – orifice flowmeter ,venturi, Coriolis, vortex, Magnetic flowmeter.

    Reply
  • Ramu Sunke says:
    March 15, 2016 at 2:50 am

    Hi Bharadwaj

    This is Ramu from Anrak. I have seen your website. Very much useful for all. You are doing very good job. Well done Bharadwaj. Be continue.

    Reply
  • Hardik Makvana says:
    July 11, 2016 at 4:21 am

    Dear sir,
    Please sir share the DP type transmitter basic principal and how its work..??

    Reply
  • DEvanathan says:
    December 29, 2018 at 9:34 pm

    Devanathan,

    Dear sir,

    please share Convertion table for all units like pressure,temp,mm water column, mercury column, psi to bar,and bar to kg–etc.

    Reply
  • Jason Blankenship says:
    December 22, 2019 at 9:53 am

    I have a customer who wants the ESD to close in 2 seconds. I know the cv of the valve and have the actuator chosen to operate the valve. I just need to know how to choose the correct cv of the pilot valve, solenoid and filter regulator to make the actuator and valve close I. 2 seconds. Can anyone help me?

    Reply
  • Kamran says:
    July 4, 2023 at 1:51 pm

    Hi
    How to calculate PM in the formula for calculating CV related to Case of the Gas? Is P1 added to P2 or subtracted or multiplied?

    Reply

Leave a Reply Cancel reply

Your email address will not be published. Required fields are marked *

Stay Connected

128.3kFollowersLike
69.1kFollowersFollow
210kSubscribersSubscribe
38kFollowersFollow

Categories

Explore More

Identify Valve Parts Quiz with Answers
What is Cavitation? What are the Causes?
How to Install a Control Valve?
Why we Require Dual SOV on a Control Valve?
Relative Flow Capacity of a Valve
Digital Control Valves – Introduction, Principle, Setup, Applications
DIN Valve Connectors – Definition, Types
Basics of Valves Interview Questions & Answers

Keep Learning

5-Port-2-Position-Valve-Animation

5 Port 2 Position Valve Working Principle

fluid flow reversed through a Control Valve

What happens when Fluid Flow Reversed through Control Valve?

Valve Basics, Sizing, and Actuators Books

Valve Basics, Sizing, and Actuators Books

Current to Pressure Converter Principle

Current to Pressure (I/P) Converter Principle

Closed Tank Level Measurement Formula

Siemens Differential Pressure Transmitter Calculations (Flange Type)

JT Valve Working Principle

JT Valve Working Principle

Solenoid-Valve-Manual-Reset-function

Solenoid Valve with Manual Reset Working Principle

Incident Investigation: Motor Operated Valve Lesson

Incident Investigation: Motor Operated Valve Lesson

Learn More

Water Treatment Industry

Water Softening Systems in Water Treatment Industry

Instrument Protection Methods: Seals

non-contact pyrometers distance calculation

Non-contact Pyrometers Characteristics

Analyzers Questions and Answers

Biosensors Questions & Answers

Nuclear Magnetic Resonance Spectrometer Questions and Answers

Continuous Wave NMR Spectroscopy Questions & Answers

Ethernet IP Commissioning Tool software

How to Configure IP Address in Rockwell PLC?

Material Certificate versus Positive Material Identification (PMI)

Material Certificate versus Positive Material Identification (PMI)

Simple RL Circuit

Impedance in RL Circuits

Menu

  • About
  • Privacy Policy
  • Copyright

Quick Links

  • Learn PLC
  • Helping Hand
  • Part Time Job

YouTube Subscribe

Follow US
All rights reserved. Reproduction in whole or in part without written permission is prohibited.
Welcome Back!

Sign in to your account

Username or Email Address
Password

Lost your password?