How-to do 4-20mA Transmitters calculations easily. This articles provides Industrial Instrumentation 4-20mA calculations with easy examples.
4-20mA Transmitters Calculations
Given a pressure transmitter with a measurement range of 150 to 400 PSI and a signal range of 4 to 20 milliamps, calculate the applied pressure corresponding to a signal of 10.6 milliamps.
Answer :
- Take 10.6 milliamps and subtract the LRV (4 milliamps),
- then divide by the span (16 milliamps) to arrive at 41.25% (0.4125 per unit).
- Take this number and multiply by the span of the pressure range (400 PSI − 150 PSI, or 250 PSI) and
- lastly add the LRV of the pressure range (150 PSI) to arrive at a final answer of 253.125 PSI.
Given a temperature transmitter with a measurement range of −88 degrees to +145 degrees and a signal range of 4 to 20 milliamps, calculate the proper signal output at an applied temperature of +41 degrees.
Answer :
- Take 41 degrees and subtract the LRV (−88 degrees) which is the same as adding 88 to 41,
- then divide by the span (145 degrees − (−88) degrees, or 233 degrees) to arrive at 55.36% (0.5536 per unit).
- Take this number and multiply by the span of the current signal range (16 milliamps) and
- lastly add the LRV of the current signal range (4 milliamps) to arrive at a final answer of 12.86 milliamps.
Given a pH transmitter with a measurement range of 3 pH to 11 pH and a signal range of 4 to 20 milliamps, calculate the proper signal output at 9.32 pH.
Answer :
- Take 9.32 pH and subtract the LRV (3 pH),
- then divide by the span (11 pH − 3 pH, or 8 pH) to arrive at 79% (0.79 per unit).
- lastly add the LRV of the current signal range (4 milliamps) to arrive at a final answer of 16.64 milliamps.
Do You know any simple 4-20mA conversions ?
Share with us, use comments section.
Articles You May Like :
Level Transmitter Zero Elevation
Em đang cần tài liệu chi tiết sửa chửa hệ thống valve solenoi symoi . Mong add giúp em với.
Translated : I need detailed documentation repair solenoid valve system. Please.
Dear Sir..
I want know your university name and address. From where. you did your study.
Please sir guide me
We have temp controller range 0 to 100 deg. C and it”s re-transmitting output is 4-20 ma I want to scaling PLC program y=ax+b here a is multiple factor and b is offset. Request you to please suggest value of a and b .