Reading: Voting Logic in Safety Instrumented System (SIS)
Inst Tools > Blog > Safety Instrumented System (SIS) > Voting Logic in Safety Instrumented System (SIS)
Last updated: July 26, 2020 11:16 am
3 Min Read
There are 1oo1, 1oo2, 2oo2, 2oo3 etc voting logic in the safety instrumented system architecture.
The voting logic architecture usually used in the field instrument and or final control elements to reach certain Safety Integrity Level (SIL)  or to reach certain cost reduction due to platform shutdown. In general when we must use 1oo1, 1oo2, 2oo2, or 2oo3 voting logic architecture?
Voting Logic
As mentioned above, there are two purposes why certain voting logic architecture were chosen, first is to reach certain SIL and secondly to reach certain cost reduction due to spurious platform shutdown.
In order to determine a certain SIL requirement, a risk or process hazard analysis is used to identify all process, safety and environmental hazards, estimate their risks, and decide if that risk is tolerable. Where risk reduction is required an appropriate SIL is assigned.
The individual components (sensor , logic solver , final elements, etc.) that are working together to implement the individual safety loops must comply with the constraints of the required SIL.
In essence, this means that all components within that loop must meet a certain Probability of Failure on Demand (PFD), Safe Failure Fraction (SFF) and Hardware Fault Tolerance (HFT) requirement for the intended SIL.
Readers are encouraged to see further detail regarding this PFDavg, SFF, and HFT in the IEC 61508 & IEC 61511.
As general rule, first of all the SIL requirement for any particular condition or application will be determined using a risk or process analysis.
After the SIL was determined then the architecture of the sensor, logic solver, and final control element is studied to investigate which architecture will fulfill the SIL requirement.
For example, if the SIL requirement for a high pressure incoming pipe line is SIL 3, then the architecture of the pressure sensor and final element will be investigated.
If 1oo1 sensor, 1oo1 logic solver, and 1oo1 shutdown valve can fulfill the SIL 3 requirement, then this architecture is chosen. If not, then any other voting logic architecture is investigated.
Let’s say after several investigations the voting logic 1oo2 sensor, 1oo2 logic solver, and 1oo2 shutdown valve can fulfill the requirement of SIL 3, then this voting logic is chosen. If the cost reduction study need to minimize spurious trip due to one of the sensor failed, then may be the sensor voting logic architecture must be upgraded to become 2oo3 architecture.
This architecture may be chosen since if one sensor failed, then the overall architecture is still fulfilling SIL 3 requirement with 1oo2 sensor configuration. Thus it doesn’t need to have a platform shutdown when one sensor failed.
Articles You May Like :
SIS Module Failure
SIS, PLC or BPCS ?
Questions on SIS
Shutdown Logic
ESDV Advantages
What is a Logic Solver? – Safety PLC
Automated Block Valve (ABV)
SIS Design – Safety Instrumented System
High Reliability of Safety Instrumented Systems
SIS Logic Solver
  • Vivek M says:
    May 21, 2019 at 12:12 pm
    ESD transmitters serving critical shutdown level in Safety Instrumented System are recommended to have voting logic configuration.
    Voting logic is applied to minimize the occurrence of complete loss of production caused by single transmitter fault or spurious trip shutdown. The voting configuration can be 2oo3 or 1oo2D based on SIL assessment and verification.
    There are some consideration when applying voting logic in the process:
    > Transmitters not to have common tapping to the process line/equipment.
    > The transmitters forming the same voting logic shall not be assigned on the same I/O module of Safety Instrumented System.
    > Each instrument cable is routed diversely.
    > Transmitters are set with the same calibration range.
    > It is also recommended to have transmitters from different manufacturer to avoid manufacturing defect causing common mode failure.
    Also on this voting logic configuration, SIS needs to compare the transmitters value and initiate alarm on Human Machine Interface (HMI) for any deviations on measurement among the transmitters.
S84 / IEC 61511 Standard for Safety Instrumented Systems
SIS Final Control Elements
SIS Sensors
What is Safety Instrumented Functions ?
What is Safety Control System ?
energized-to-safe-loop
Difference between SIS, PLC and BPCS Systems
Emergency Shutdown System Philosophy
Shutdown Philosophy
SIS Application Program - Safety Instrumented System
SIS Application Program – Safety Instrumented System
Basic Terms used in SIL Verification
Intrinsic Safe Calculation
level of liquid inside a vessel
Concept of Redundancy in Control Systems
pressurized water reactor
SIS Example : Nuclear Reactor Controls
Manometer Measures Differential Pressure
How Manometer Measures Differential Pressure for Different Fluids?
Displacement Transducers Objective Questions
Safety Relief Valve
Safety Relief Valve Quiz: Test Your Knowledge
Bonding and Grounding Electrical Systems
Testing and Inspection of Bonding and Grounding Systems
Connecting Faceplates to PLC Project
Connecting Faceplate to PLC Project – HMI Tutorial
Time Response Analysis
State Variable Analysis – Part I
0 to 10 mA Current Loop
What is Live Zero in 4-20 mA Current Loop?
Instrument Process Datasheet
Instrument Process Datasheet (IPDS)