Inst ToolsInst ToolsInst Tools
  • Courses
  • Automation
    • PLC
    • Control System
    • Safety System
    • Communication
    • Fire & Gas System
  • Instrumentation
    • Design
    • Pressure
    • Temperature
    • Flow
    • Level
    • Vibration
    • Analyzer
    • Control Valve
    • Switch
    • Calibration
    • Erection & Commissioning
  • Interview
    • Instrumentation
    • Electrical
    • Electronics
    • Practical
  • Q&A
    • Instrumentation
    • Control System
    • Electrical
    • Electronics
    • Analog Electronics
    • Digital Electronics
    • Power Electronics
    • Microprocessor
  • Request
Search
  • Books
  • Software
  • Projects
  • Process
  • Tools
  • Basics
  • Formula
  • Power Plant
  • Root Cause Analysis
  • Electrical Basics
  • Animation
  • Standards
  • 4-20 mA Course
  • Siemens PLC Course
Reading: Root Cause Analysis for Tank Overflow due to Valve Problem
Share
Notification Show More
Font ResizerAa
Inst ToolsInst Tools
Font ResizerAa
  • Courses
  • Design
  • PLC
  • Interview
  • Control System
Search
  • Courses
  • Automation
    • PLC
    • Control System
    • Safety System
    • Communication
    • Fire & Gas System
  • Instrumentation
    • Design
    • Pressure
    • Temperature
    • Flow
    • Level
    • Vibration
    • Analyzer
    • Control Valve
    • Switch
    • Calibration
    • Erection & Commissioning
  • Interview
    • Instrumentation
    • Electrical
    • Electronics
    • Practical
  • Q&A
    • Instrumentation
    • Control System
    • Electrical
    • Electronics
    • Analog Electronics
    • Digital Electronics
    • Power Electronics
    • Microprocessor
  • Request
Follow US
All rights reserved. Reproduction in whole or in part without written permission is prohibited.
Inst Tools > Blog > Root Cause Analysis (RCA) > Root Cause Analysis for Tank Overflow due to Valve Problem

Root Cause Analysis for Tank Overflow due to Valve Problem

Here we will discuss the root cause analysis of an incident in which a tank filled with water started overflowing due to a valve problem.

Last updated: September 28, 2022 4:47 pm
Editorial Staff
Root Cause Analysis (RCA) Control Valves
No Comments
Share
5 Min Read
SHARE

Today in this article we will discuss about the root cause analysis of an incident in which a tank filled with water started overflowing.

Contents
Problem StatementRoot Cause Analysis for Valve Problem

The incident had occurred in a tank in which water was filled. If the tank had some other hazardous liquid, then this could have created fatality.

Root Cause Analysis for Valve Problem

Problem Statement

A tank was installed in one of the plants in a refinery for storing the water in it. The feed inlet of the tank was controlled using an On-Off valve (butterfly body & rack and pinion actuator). The fail action of the On-Off valve was fail-close.

One day, the field operator informed us that the valve is having some leakage from the actuator side. The instrumentation team checked the valve and found that the actuator of the valve is passing. So, actuator overhauling was needed.

On the next day, the actuator was dropped for overhauling purposes. But the operation requirement was to have the valve in an open condition as the tank was having a low level. Tank filling was in-progress.

So, in valve open condition, the actuator was dropped by giving external air to the actuator to keep the actuator open. After overhauling the actuator, the actuator was reinstalled. The actuator was reinstalled in another shift by a different person.

After a few hours, during the field round, the field operator observed that the tank was overflowing. Immediately the tank inlet was isolated.

When the actuator was reinstalled after the maintenance job, the tank level was 82%. Above 80%, the tank feed inlet valve is in close condition. When the level goes below 25%, the feed inlet valve opens again.

Root Cause Analysis for Valve Problem

So, what can be the probable reason for tank overflow?

Probable Problem 1: The level transmitter showed a low value while the actual level was high.

The level transmitter was working ok. When the tank started overflowing, the level transmitter was showing 101%. The same level was confirmed with the level gauge.

Probable Problem 2: On-Off valve did not close when the level was above 80%.

The feedback from the On-Off valve was close feedback.

Probable Problem 3: The proximity switch malfunctioned and started showing close feedback when the valve was open.

The proximity switch’s functionality was checked. Found ok.

Probable Problem 4: Passing from the On-Off valve body

This might be the probable reason.

Probable Problem 5: Passing problem in bypass valve given for feed inlet valve.

When the isolation valve for the On-Off valve was closed, the tank’s overflow stopped. Hence there was no issue with the bypass line valve.

Probable Problem 6: The actuator direction was incorrect during installation

This can also be one of the reasons.

Observations after taking the On-Off valve for maintenance:

  1. The actuator was dropped for further checking purposes. The valve was in close condition while dropping the actuator.
  2. While dropping the body for checking the passing issue, the body was found in open condition.

This means that the actuator’s direction of installation was incorrect.

What went wrong?

During the job, the actuator was dropped in open condition. While reinstalling the actuator, the technician installed the actuator in close condition, while the body was in open condition.

The technician was unaware of this because the body had a coupler of square shape. The technician did not check the condition of the body by removing the coupler.

The technician installed the actuator in close condition. Then he set the feedback and handover the valve for operation.

The direction of every instrument before removing should be marked as well as the proper handover of jobs should be given.

Don't Miss Our Updates
Be the first to get exclusive content straight to your email.
We promise not to spam you. You can unsubscribe at any time.
Invalid email address
You've successfully subscribed !

Continue Reading

Hunting of Control Valves
Solenoid Valves Practical Problems
Totally Enclosed Fan Cooled (TEFC) Motors Rampant Winding Burnouts
Solenoid Valve Functional Testing
Seal Pressure Instruments Root Cause Analysis
What is a Shuttle Valve? Principle, Advantages, Disadvantages
Share This Article
Facebook Whatsapp Whatsapp LinkedIn Copy Link
Share
Leave a Comment

Leave a Reply Cancel reply

Your email address will not be published. Required fields are marked *

Stay Connected

128.3kFollowersLike
69.1kFollowersFollow
210kSubscribersSubscribe
38kFollowersFollow

Categories

Explore More

Working Principle of Pneumatic Actuators
Carbamate Plunger Pump Packing Problems Eliminated
Premature Arc Fault Breaker Failures
Flange Joint Errors shutdowns root cause analyzed and eliminated
Electro Pneumatic Valve Positioner Schematic & Principle
Cooling Tower Fans Frequently Failing
Electric Motor Actuator Parts
How to Select Control Valve Failure Mode

Keep Learning

Internal Parts of Globe Valve

How to Choose a Control Valve?

Demister Pads Problem

Problems with Demister Pads – Root Cause Analysis (RCA)

HT motors Corrosion Problem

HT motors Corrosion Problem

CO2 Absorber Graphics in DCS

CO2 Absorber Corroded Wall Thickness & Weld Building

Functional Testing of Control Valve Positioners

Functional Testing of Control Valve Positioners

Leaking Plug Valves pose Safety Hazards and Lead to Plant Shutdown

Leaking Plug Valves Pose Safety Hazards and Lead to Plant Shutdown

Incident Investigation: Motor Operated Valve Lesson

Incident Investigation: Motor Operated Valve Lesson

Wrongly terminated Thermocouple (TC) wires

Too Low-Temperature Readings after a Failed Thermocouple Change

Learn More

Instrumentation Engineering Materials Test

Instrumentation Materials Test

GATE Instrumentation Questions and Answers

GATE Instrumentation Questions and Answers

Strain Gauge Pressure Transducer

Resistance Type Pressure Transducers Principle

Calibration Sheet

Calibration : Up-tests and Down-tests

Shaft and Coupling Bore Tapers Repair Caused Frequent Shutdowns

Shaft and Coupling Bore Tapers Repair Caused Frequent Shutdowns

SIL Levels

Understanding Safety Integrity Level IEC 61511

Power Electronics Objective Questions

Thyristor Firing Objective Questions

Pneumatic Transmitter

Pneumatic Level Transmitter Calibration Table

Menu

  • About
  • Privacy Policy
  • Copyright

Quick Links

  • Learn PLC
  • Helping Hand
  • Part Time Job

YouTube Subscribe

Follow US
All rights reserved. Reproduction in whole or in part without written permission is prohibited.
Welcome Back!

Sign in to your account

Username or Email Address
Password

Lost your password?