Reading: PLC Pump Permissive Interlocks
Inst Tools > Blog > PLC Tutorials > PLC Pump Permissive Interlocks
Last updated: March 4, 2021 4:41 pm
PLC Tutorials Practical Questions
5 Comments
The following PLC program was written to control the operation of a large electric motor-driven pump.
PLC Pump Permissive InterlocksAnswer :“Valve open” limit switch:Low oil pressure:High bearing temperature:
A variety of “permissive” inputs protect the pump from damage under abnormal conditions, and one permissive in particular (“valve open”) will only allow the pump to start up if one of the valves in the piping system is in the full-open position:
Identify the type of contact (either NO or NC) necessary for each of these electrical switch contacts, based on the trip condition (either high or low) and how each input is applied in the PLC program:
  1. Start pushbutton = NO or NC?
  2. Throttling valve open limit = NO or NC?
  3. Stop pushbutton = NO or NC?
  4. High bearing temperature = NO or NC?
  5. High vibration = NO or NC?
  6. High motor temperature = NO or NC?
  7. Low oil pressure = NO or NC?
Answer :
  2. Throttling valve open limit = NC
  5. High vibration = NC
A helpful problem-solving technique is to first identify the necessary coloring which will allow the motor to start up and keep running (i.e. the condition of all permissives during correct operating conditions):
PLC Pump Interlocking
Since the motor is controlled by retentive coil instructions (“Set” and “Reset”), we know all the permissive contacts on the Reset rung must be uncolored in order for the motor to run.
The normally closed “Valve open” instruction must be colored in order to allow the Start input to latch the Set coil and start the motor.
Once we know this, we may determining the necessary “normal” statuses of all permissive switches in order to make their corresponding PLC program contact instructions colored.
A few examples will be given here:
The PLC contact instruction for this permissive is normally-closed, which means that PLC input must be de-energized in order to color that contact instruction.
This means the limit switch must be in the open condition when the valve mechanism moves into the switch’s sensing range (in the fully-open position), and close when the valve mechanism moves away from the switch.
A limit switch that is closed with nothing near it is a normally-closed (NC) limit switch.
Low oil pressure:
The PLC contact instruction for this permissive is normally-closed, which means that PLC input must be energized with electricity in order to maintain that contact instruction in an uncolored state.
This means the low oil pressure switch must be in the closed condition while everything is running as it should (i.e. adequate oil pressure), and open if oil pressure becomes too low.
A pressure switch that is open when pressure is below the trip threshold is a normally-open (NO) pressure switch.
The PLC contact instruction for this permissive is normally-open, which means that PLC input must be de-energized in order to maintain that contact instruction in an uncolored state.
This means the high bearing temperature switch must be in the open condition while everything is running as it should (i.e. low bearing temperature), and close if temperature becomes excessive.
A temperature switch that is open when temperature is below the trip threshold is a normally-open (NO) temperature switch.
Share Your Answer / Comments
Credits : by Tony R. Kuphaldt – under CC BY 1.0
For More PLC Questions : CLICK HERE
  • PLC Electric Motor Interlocks
  • Permissive and Interlock Circuits
  • Troubleshooting PLC Permissive Inputs
  • Basics of Trips, Interlocks, Permissives & Sequences
  • PLC Permissive for Motor Control
Allen Bradley Bitwise Logical Operations
Advanced PLC Programming for Defective Parts Sorting
Sorting & Distribution Line PLC Programming – Advanced Logic
What is SCADA System?
The Concept of Shift Register in Omron PLC with Example
5 Comments
  • Bhargav Reddy says:
    September 3, 2017 at 11:53 am
    Sir
    Difference between DCS & PLC in single line
    • S Bharadwaj Reddy says:
      September 3, 2017 at 11:57 am
      Hi, Check these articles. Article 1 Article 2
  • Jasim Akram says:
    September 7, 2017 at 3:41 am
    Sir, is there any website through which I can understand instrumentation in Hindi ? If website is exit then please reply me.
  • Vikram says:
    July 2, 2019 at 10:08 pm
    Sir,I can’t understand plc program’s,will you get easily simple process is there?
  • Brent says:
    July 1, 2020 at 7:43 pm
    Why is vibration contact NC and oil pressure NO?
Free InTouch SCADA Tutorial Course for Beginners
PID Simulator Download
Types of Interrupt OB in Siemens Tia Portal
Difference Between Wifi and Industrial Wireless
How CPU Execute Program in Siemens PLC?
Product Sticker Machine with Weighing PLC Program
Allen-Bradley PLC Program
Sequential Operation of Output Bits using Two Push buttons
Calculation of Hydrostatic Pressure
What is a function call in TIA Portal
Difference Between FC and FB in Tia Portal
Allen Bradley PLC ControlLogix Hardware
Parts of PLC
Parts of PLC
Top PLC Manufacturers
PLC Brands Software Information
Current-to-Pressure Transducer Calibration Table
diode-clamper-circuit
Full Wave Voltage Doubler using Diodes
How to Troubleshoot a PLC System
How to Troubleshoot a PLC System?
PLC Programming for Train Detection and Gate Operation
Siemens PLC
Will PLCs become obsolete?
What are Pressure Sensing Lines
What are Pressure Sensing Lines? – Causes of Errors in Measurement
Types of Tripping Protection in MCCB
PLC Programming Classroom Bell System
Classroom Bell System – PLC Programming Practice Examples
Dew Point Meter Principle