Reading: Interposing Relay Panel (IRP) – Wiring and Testing Requirements
Inst Tools > Blog > PLC Tutorials > Interposing Relay Panel (IRP) – Wiring and Testing Requirements
The components location, wiring, and termination in the Interposing Relay Panel (IRP) shall be as per the approved system drawing.
Last updated: March 4, 2021 10:53 am
PLC Tutorials Control Systems
3 Min Read
Check the locations of the components like relay’s and Terminal blocks in the IRP panel shall be as per the approved IRP GA/IA drawing. Refer to the above photograph for easy understanding.
Interposing Relay Panel (IRP)Termination of Digital Input (DI) signalsTesting of the Digital input (DI) SignalsTermination of Digital Output (DO) SignalsTesting of Digital Output (DO) Signals
Also Read: What Is Interposing Relay in a PLC?
  • Identify the terminal block for the DI signal as per Instrument wiring interconnection drawing and Electrical schematic wiring drawing.
  • Check the cross-wiring between the Electrical side MCC terminal and the System side Instrument terminal.
  • Check the proper ferrule for the input signal i.e. Status, L/R, and Fault from and to assigned terminals.
  • Short the terminal blocks of the DI signal at the MCC end in the IRP cabinet.
  • Check and ensure the continuity in the multimeter at the terminal end in the IRP cabinet for the same.
  • Repeat the above steps for each DI signal and highlight each signal in the I/O list to ensure all the DI signals are covered under the test.
  • Identify the terminal block and relay numbering for the DO signal as per Instrument wiring interconnection drawing and Electrical schematic wiring drawing.
  • Check the cross-wiring between the Electrical side MCC terminal, Relay, and the System side Instrument terminal.
  • Check the proper ferrule for the output signal i.e. Start, Stop, and Trip from and to assigned terminals.
  • Inject 24V DC with current ranging from (50-100mA) to the Coil side of the DO signal.
  • Confirm that the intended relay is energized / de-energized as per the Electrical schematic wiring drawing.
  • Check and ensure the continuity at the MCC end for the same signal using a multimeter.
  • Repeat the above steps for each DO signal and highlight each signal in the I/O list to ensure all the DO signals are covered under the test.
Note: Hope the above explanation for the wiring and testing of the Interposing relay panel is understood.
Have a nice day!!
Stay Safe!!
Author: Mohammed Khaleel
  • Loop Test Requirements
  • Digital Signals Wiring
  • Yokogawa DCS System
  • Loop diagram Lab Exercise
  • Flow Control Loop
Components of PLC
Basic Pumping System Application Used in Industrial Automation
Series Tanks Level Control using PLC Ladder Programming
Inside the PLC Control Panel: How Much Do You Know?
How to Reduce Relay Noise in PLC Systems?
What are FIFO and LIFO Sequences in PLC?
  • Suresh vittamsetty says:
    September 21, 2020 at 10:22 pm
    Please can you explain freewheeling diode for inductance
Conveyor Sorting Machine PLC Program with Calculation Function
What is Alarm Shelving? – Nuisance Alarms, Types, Suppression
Building Management System
Case Statement in SCL Language
What is PID Controller?
Difference between Compact PLC and Modular PLC
Use of Regions in SCL Language
How to do Force in GE PLC Proficy Machine Edition?
On Delay Timer using PLC
ON Delay Timer using PLC
Automatic Car Washing Process using PLC Ladder Diagram
PLC-Complete-Training-Package
Free PLC Training Software Download
Create an Application in HMI using Tia Portal
Boiler Intelligent Control Cabinet
IoT based Smart Boiler Control System with Cloud PLC and SCADA
Function Block Diagram - Studio 5000 Logix Designer
Define the Order of Execution in Functional Block Diagram of Studio 5000
Rotameters Working
Rotameter Working Principle and Animation
HVAC Principle and Theory
Recommendations to HVAC Engineers
Proportional only Control Theory
Proportional-only Control Theory
Batteries in parallel animation
Batteries in Series and Parallel Animation
6.6kV HV Induction motor Protection
Electrical Ground Loop
How to Solve Electrical Ground Loop Problems?
How to Test a Pressure Gauge
Pressure Control Loop
Pressure Control Loop Wiring Connections