Inst ToolsInst ToolsInst Tools
  • Courses
  • Videos
  • Q & A
    • Interview
      • Instrumentation
      • Electronics
      • Electrical
      • Practical Questions
    • MCQ
      • Instrumentation MCQ
      • Electrical MCQ
      • Electronics MCQ
      • Control Systems MCQ
      • Analog Electronics MCQ
      • Digital Electronics MCQ
      • Power Electronics MCQ
      • Microprocessor MCQ
      • Multiple Choice Questions
  • EE
    • Electronics
      • Electronics Q & A
      • Electronic Basics
      • Electronic Devices & Circuits
      • Electronics Animation
      • Digital Electronics
    • Electrical
      • Electrical Basics
      • Electrical Q & A
      • Power Electronics
      • Electrical Machines
      • Electrical Animation
      • Power Systems
      • Switchgear & Protection
      • Transmission & Distribution
  • Measure
    • Control Valves
    • Calibration
    • Temperature
    • Pressure
    • Flow
    • Level
    • Analyzers
    • Switches
    • Vibration
    • Solenoid Valve
  • Control
    • PLC Tutorials
    • Control Systems
    • Safety Instrumented System (SIS)
    • Communication
    • Fire & Gas System
  • More
    • Design
    • Tools
    • Animation
    • Basics
    • Formulas
    • Standards
    • TextBooks
    • Common
    • Software
    • Excel Tools
    • Erection & Commissioning
    • Process Fundamentals
    • Videos
    • Books
Search
All rights reserved. Reproduction in whole or in part without written permission is prohibited.
Reading: Instrumentation Common Measurement Issues
Share
Notification Show More
Font ResizerAa
Inst ToolsInst Tools
Font ResizerAa
  • Courses
  • PLC Tutorials
  • Control Systems
Search
  • Courses
  • Videos
  • Q & A
    • Interview
    • MCQ
  • EE
    • Electronics
    • Electrical
  • Measure
    • Control Valves
    • Calibration
    • Temperature
    • Pressure
    • Flow
    • Level
    • Analyzers
    • Switches
    • Vibration
    • Solenoid Valve
  • Control
    • PLC Tutorials
    • Control Systems
    • Safety Instrumented System (SIS)
    • Communication
    • Fire & Gas System
  • More
    • Design
    • Tools
    • Animation
    • Basics
    • Formulas
    • Standards
    • TextBooks
    • Common
    • Software
    • Excel Tools
    • Erection & Commissioning
    • Process Fundamentals
    • Videos
    • Books
Follow US
All rights reserved. Reproduction in whole or in part without written permission is prohibited.
Inst Tools > Blog > Instrumentation Design > Instrumentation Common Measurement Issues

Instrumentation Common Measurement Issues

Learn the common instrumentation transmitter measurement errors and issues in the process control industry.

Last updated: December 29, 2020 11:02 pm
Editorial Staff
Instrumentation Design
No Comments
Share
7 Min Read
SHARE

Production units and plants typically have hundreds of process instruments operating in a variety of roles.

Contents
4-20 mA Current SignalsLoop Integrity DiagnosticLeakage CurrentIncreased Electrical LoadFailing Wiring Infrastructure

These instruments are the operators’ eyes and ears, providing critical variables used to monitor and control operations.

They can also send diagnostic information to warn of a variety of developing problems internal to the instrument, within the actual process, or the larger automation infrastructure.

The latest generation of advanced instruments now exhibits a high degree of sophistication in this area.

Diagnostic information can be transmitted as a HART value superimposed on the normal 4-20 milliamp (mA) wired analog current loop, or via a digital protocol such as FOUNDATION Fieldbus, or WirelessHART.

When introduced, these diagnostics represented a major advance for reliability and maintenance departments, allowing them to address developing problems before they caused an inaccurate reading or full failure.

Everything, including the main process variable and any diagnostic functions, depends on reliable communication infrastructure.

The most sophisticated transmitter cannot send data without a reliable connection to the distributed control, asset management, or another host system.

4-20 mA Current Signals

In most environments, the majority of transmitters are wired using a 4–20 mA current loop, possibly with HART.

Normally these are very reliable but can develop problems capable of causing inaccurate readings.

Loop Integrity Diagnostic

In a typical plant environment, a pressure transmitter’s analog current loop may involve a long cable, potentially several hundred feet or more, between the transmitter and the host system I/O connection.

A current loop is very robust, so this does not necessarily pose a challenge if all the elements are intact.

However, a long cable could easily have a dozen termination points from one end to the other as it passes through trays and marshaling cabinets. Screw terminals that have worked loose or become corroded can cause a signal to be lost completely.

A short circuit can also cut off data. The live zero feature of the loop will usually call attention to a full signal loss.

More subtle problems, where the reading is corrupted but not drastically enough to be immediately recognizable, can cause operators to take the wrong action.

Here are two examples of how these can happen.

Leakage Current

Some situations can create a partial short circuit where a new circuit path is formed. Electrical current “leaks” from one side to the other, often due to moisture or corrosion, which might change the signal level.

For example, if the actual signal from the transmitter is 12 mA and the leakage allows another 3 mA, the host system will believe the reading is 15 mA and show a corresponding value to the operators.

If the transmitter sends a signal greater than 18 mA, the system will incorrectly show a fault because the value will exceed 20 mA.

This on-scale failure can cause operators to take improper action, or it can cause a control loop governed by that transmitter to respond incorrectly.

Increased Electrical Load

Correct functioning of a loop depends on having a known resistance for the wiring and a reliable, consistent power supply.

If wires or terminals are corroded or loose, there may still be contact, but those points will add an additional load just as if a resistor had been added to the circuit.

Similarly, a failing or overtaxed power supply can create a brownout condition with sagging output. These can reduce the voltage available to the transmitter which can keep it from being able to reach a full 20 mA signal.

Under those conditions, the transmitter might only be able to communicate a maximum of 15 mA even though the process calls for something higher.

This condition is particularly difficult to recognize since the transmitter can behave correctly through much of its range leaving operators unaware of this critical failure condition.

Both these conditions can be detected through manual loop checks by a qualified technician, but few facilities have the resources to perform these with sufficient regularity.

Some new advanced transmitters are available with loop integrity diagnostics to perform these tests automatically, monitoring the available voltage on a continuous basis.

If voltage deviates from baseline conditions, operators and maintenance technicians can be notified immediately, allowing them to detect and correct the issue, avoiding potential process upsets or even safety incidents.

Thresholds can be programmed in the configurations to correspond to the criticality of a given loop.

Failing Wiring Infrastructure

Some older plants still running ancient automation infrastructure often deal with the loop integrity problems just discussed, combined with outright failures of legacy cabling, but the cost of replacing it is impractical or far too expensive for every instrument.

Plants may try workarounds, but eventually, the failures are simply too significant, and operators begin to lose critical information.

The easiest and most economical solution is abandoning the wiring entirely and replacing it with WirelessHART for all monitoring applications and some real-time control applications.

Any existing 2-, 3- or 4-wire HART-enabled transmitter can be equipped with a WirelessHART adapter, capable of sending multiple process variables and diagnostic data via the network.

This allows working legacy transmitters to stay in a place where possible, although some may still need external power.

This eliminates the need to replace long wiring runs, likely improves on existing signal quality and reliability, and can deliver more data to the host system.

It may be desirable to replace some of the oldest transmitters with newer units using native WirelessHART designs.

The variety of these self-powered units is growing, eliminating the need for signal or power wiring.

Read Next:

  • What is Safety Control System?
  • Security of Industrial Automation Systems
  • Overview of Industrial Control Systems
  • Remote Functions in Industrial Control Systems (ICS)
  • Compressor Emergency Shutdown Root Cause Analysis
Don't Miss Our Updates
Be the first to get exclusive content straight to your email.
We promise not to spam you. You can unsubscribe at any time.
Invalid email address
You've successfully subscribed !

Recommended Articles

I&C Engineer Roles & Responsibilities – Instrumentation Design
Industrial Automation Pre-Engineering Design Documents – Project & Process
Pneumatic Valves and Cylinders Sizing – Part 2
When to use a Diaphragm Seal?
How to Select the Right Panel Enclosure for Your Application?
Thermowell Problems
Share This Article
Facebook Whatsapp Whatsapp LinkedIn Copy Link
Share
Leave a Comment

Leave a Reply Cancel reply

Your email address will not be published. Required fields are marked *

Stay Connected

128.3kFollowersLike
69.1kFollowersFollow
208kSubscribersSubscribe
38kFollowersFollow

Categories

Recent Comments

  • William Snyder on Top Non-PLC Certification Courses for Automation Professionals
  • Kamli on Top Free PLC Software
  • Guifty Shimica on Top Non-PLC Certification Courses for Automation Professionals
  • Guifty Shimica on Top Non-PLC Certification Courses for Automation Professionals

Related Articles

Zener Diode Regulator

Zener Diode Voltage Regulators

Earth Meter Working Principle

How Earth Resistance is Measured

control-valve-actuators

Control Valve Selection Tips

Field Instruments Scaling and Unit Conversions

Field Instruments Scaling and Unit Conversions

Pull-up switch circuit.

Pull Up and Pull Down Switch Circuits

Relay Permissive and interlock circuits

Basics of Permissive and Interlock Circuits

Multiple Thermowell Installations Problems

Multiple Thermowell Installations Problems

Instrument Loop Diagram

How-to Create Instrument Loop Diagram (ILD)?

More Articles

Power Electronics Objective Questions

Type C Chopper Objective Questions

How to Upload PLC Program in Siemens PLC if Upload Icon is Disabled

Upload Option Disabled in Siemens PLC

Marking Machine

PLC SCL Program for Marking Machine

Programmable Logic Controller (PLC) Questions and Answers

Programmable Logic Controller (PLC) Questions and Answers – 6

What are Switchgear Interlocks?

What are Switchgear Interlocks?

Interlock Philosophy

Types of Interlocks

Scaling Sensor Output to Engineering Units

Scaling Sensor Output to Engineering Units

DeltaV System to Excel

How to Export Data from DeltaV System to Excel

Follow US
All rights reserved. Reproduction in whole or in part without written permission is prohibited.
Welcome Back!

Sign in to your account

Username or Email Address
Password

Lost your password?