Reading: Instrumentation Basics – Range Conversion Formula and Examples
Inst Tools > Blog > Formulas > Instrumentation Basics – Range Conversion Formula and Examples
In this article, you will learn the instrumentation basics and transmitter range conversion formula, and industry examples.
Last updated: June 21, 2022 6:26 pm
Formulas
2 Comments
We encounter many transmitters in daily activities like preventive maintenance, breakdown, or commissioning activities.
Instrumentation BasicsInstrument Range Conversion – Method 1Instrument Range Conversion – Method 2
We may need to convert any given transmitter range to other range like from (0oC – 100oC) to (4 mA – 20 mA) or (0 kg/cm2 – 10 kg/cm2) to (3 psi – 15 psi) or (0 mmH2O – 2000 mmH2O) to (0% – 100%), etc.
Instrumentation Basics - Range Conversion Formula and Examples
All the above conversions are easy to implement. But now think of a case in which you are supposed to convert from (-250oC to 150oC) to (4 mA to 20 mA) or any such instrument range which has uneven starting and endpoints.
Don’t worry friends, in this article we will learn two methods to convert the value from one range to another range.
This method might be known to many engineers who are reading this article. But still, we don’t use it frequently because we often forget the formula.
Every transmitter range has two parameters which are LRV and URV. Here LRV means lower range value and URV means upper range value.
Let us recall the method. Suppose the first range is having LRV and URV as LRV_1 and URV_1 and another range has LRV_2 and URV_2.
Desired values are Value_1 and Value_2 in both ranges.
So, we use the below formula:
Let us see an example.
Suppose range one is 0 kg/cm2 – 100 kg/cm2
Range two is 4 mA to 20 mA
What will be value corresponding to 25 kg/cm2? (in milli amps)
Here Value_1 = 25
LRV_1 = 0
URV_1 = 100
Value_2 = to be calculated
LRV_2 = 4
URV_2 = 20
Put these values into the formula
(25-0) / (100-0) = ((Value_2) – 4) / (20-4)
25/100 = (Value_2 – 4) / 16
0.25 = (Value_2 – 4) / 16
Value_2 – 4 = 0.25 x 16
Value_2 = 4 + 4
Solving this equation, we get
Value_2 = 8
Hence for 25 kg/cm2, we get 8 mA as a proportional value.
This was quite an easy calculation that can even be done without using this formula.
Now have a look at the below example.
Range one: -70 o C to 190 o C
Range two: 4 mA to 20 mA
What will be the value corresponding to 50 o C? (in milli amps)
Put all values in our standard equation.
(50-(-70)) / (190-(-70)) = ((Value_2)-4) / (20-4)
120/260 = (Value_2 – 4)/16
0.4615 = (Value_2 – 4)/16
Value_2 – 4 = (0.4615 x 16)
Value_2 = 7.384 + 4
Value_2 = 11.384 mA
This is the first method.
Now let us see the second method which is for those who do not want to remember the formula.
Let us see this method by taking an instrument example. Let us take the above example only
Range one: -70oC to 190oC
We need to calculate the equivalent milli amperes for the value of 50oC
First, calculate how much % is 50oC in the range of -70oC to 190oC.
The range is 260oC
For this we will use a simple formula :
50-(-70)  —->  260
     ?      <—-  100
We have to take 50-(-70) because we want absolute value from LRV.
We get,
(100*120)/260 = 46.1538 %
Now we need a 46.1538% value for the 4 mA to 20 mA range
Divide the above value by 100. (46/100 = 0.461538)
Here 16 is the difference between URV and LRV.
So, multiply 0.461538 by 16. We get 7.3846.
Now add this value to our LRV. (7.3846 + 4)
We get 11.3846 mA which is our required value.
This is how we can convert values from one range to another.
  • 4 to 20 mA Formula
  • Calculate Process Variable
  • How to do 4-20mA Conversion
  • Raw Counts to Engineering Units
  • Turbine Flow meter Coefficient
Formula for Linear % to Square root % conversion
Scaling Sensor Output to Engineering Units
Remote Seal Transmitters Ranging Calculation
Formula to Calculate 4-20 mA from Process Variable
How to Convert Cable Size from AWG to Inches
Formula for Current 4-20ma to Percentage Conversion
2 Comments
  • Rafael Ramirez says:
    June 16, 2022 at 12:43 am
    I would love more training on all these courses
  • JULFIHAR says:
    March 17, 2023 at 2:11 am
    Thermocouple k and j type
    . I know mv , how to find degree ? Formula
    I know degree , how to find mv ? Formula
    Please.
Calculate Process Variable from 4-20mA using Fraction of Measurement
Level Calculation with Remote Seals
Calculate Flow Transmitter Output Current
4-20mA Transmitters Calculations
Calculate Control Valve Stem Position
Standard 4 to 20 mA Conversion Formula
Siemens Pressure Transmitter with Remote Seals Calculations
Instrument Percent of Span Error
DP Transmitter Level Measurement for Closed Tank Wet leg Method
DP Transmitter Dry Leg & Wet Leg Calculations
Relationship between Temperature Scales
PLC Problems Troubleshooting
Closed Tank Non-Zero-Based Direct Mount Application
Open and Closed Tank Level Calculations
Turbine Flow meter coefficient
Turbine Flow Meter Coefficient and Scaling Factor
Temperature Transmitter Formula
Calculate Temperature Transmitter Output
Elevated Span and Suppressed Span
DP Level Transmitter Elevation and Suppression Corrections
Flip Flops Objective Questions – Part 2
Sequential Timer Control of Lamps
Schneider PLC Example: Control Lamps Sequences
Immersion Electrical Heaters
Single and Three Phase Immersion Electrical Heaters Wiring Circuits
Rotary Encoder
Rotary Encoder Interview Questions and Answers
Smoke Detection System Questions
Interview Questions on Smoke Detection System
HIPPS Operating Philosophy
Understanding High Integrity Pressure Protection Systems (HIPPS)
Off load Tap Changer Principle
Transformer Tap Changing Working Principle