Reading: Electrical Earthing Calculations
Inst Tools > Blog > PLC Tutorials > Electrical Earthing Calculations
Learn the electrical earthing calculations to determine the number of earth pits and the size of the earth grid conductor.
Last updated: September 28, 2022 2:10 pm
Gaurav Lunagariya
PLC Tutorials Control Systems Electrical Basics
3 Comments
In this article, we will discuss how to determine the number of earth pits, the size of the earth grid conductor, and the overall resistance of the earthing system.
Electrical Earthing CalculationsEarth Conductor SizingSurface Area of Solid Rod ElectrodeNumber of Earth ElectrodesResistance of Electrode
Sizing of earth grid conductor shall be done by considering fault current 1 sec. The uniform soil model assumption is based on a 3-meter long pipe electrode used at this installation which cannot penetrate to the second layer of lower soil resistivity.
The material of the earth grid conductor shall be galvanized iron (GI). GI strip shall be considered as the main earth conductor and earth electrodes shall be 80 mm dia pipe meeting the requirements of IS 3043.
The maximum value of a single line to earth fault current is considered as 80 kA. Based on soil resistivity testing at various locations, average soil resistivity 12.46 ohm-m shall be considered for earthing system calculation which is done by wenner’s method.
Electric Resistivity in ohm-m = 2πRS
Where,
 S: Distance between two electrodes in meter (m)
R: V/I: Resistance in Ohm Ω
The cross-sectional area of the earth conductor shall be such that the current density value determined by the following formula is not exceeded.
(I/S) = k (1/√ t)
Where;
I = Value of fault current which can flow through the protective device in amperes
S = Cross sectional area in sq.mm.
k = Factor dependent on the material of the protective conductor, the Insulation and other parts, and the initial and final temperatures.
t = Operating time of the disconnecting device in seconds
The factor k is determined from the formula:
k = sqrt [{Qc (B+20) / δ20)} x ln {1+ (θf – θ1) / (B + θ1)}]
Qc = Volumetric heat capacity of conductor material (J/ ºC mm3)
B = Reciprocal of temperature coefficient of Resistivity at 0ºC for the conductor (0ºC)
δ20 = Electrical Resistivity of conductor material at 20ºC (Ω-mm)
θ1 = Initial temperature of conductor (ºC)
θf = Final temperature of conductor (ºC)
For steel conductor;
Qc = 3.8 x 10-3 (J/ ºC mm3)
B = 202 ºC
δ20 = 138 x 10-6 (Ω-mm)
θ1 = 40 ºC
θf  = 500 ºC
 Put all values as given in equation, so we get,
k = 80.68 ≈ 80
Now, let’s find the cross-sectional area of the earth strip
S  =  (I x √ t) / k
(80000 x 0.6 x√ 1) /80    [As a total 60% of fault current will flow through the Earth conductor and the remaining 40% will flow through the soil. This is as per BS 7354 ]
S = 600 mm2
Hence S = 600 X 1.15 = 690 sq.mm. (Considering 15 % corrosion margin)
Hence GI Bar of size 36 X 36 sq. mm. size is considered adequate for the main buried earth grid conductor for the plant area.
Ae = (π x D x l) m2
Where,
D = Diameter of electrode (m)
l  = Length of electrode (m)
Ae = (π x 0.08 x 3.00) m2 (for 80 mm diameter electrode)
Ae = 0.8294 m2
Number of earth electrodes required to dissipate the fault current of 80kA are
Area of electrodes required to dissipate fault current / Area of each electrode
Number of earth electrodes = 48.49 /0.8294
Number of earth electrodes = 58.46 Nos. (≈  60 Nos.)
R = (1/2 πl) x [(ρ – ρc) (ln (8L / D) – 1) + ρc (ln (8L / d) – 1)]
Where,
ρ = Resistivity of soil in Ω-m
ρc = Resistivity of infill material in Ω-m
d = Diameter of Electrode in meters
D = Diameter of infill material in meters
L = Driven length of electrode in meters
R =  (1/ 2 π x 3) x [ (12.46 – 3) (ln (8×3/0.45)-1) + 3 (ln ((8×3/0.08)-1)]
R  =  0.59 Ω
  • DOL Starter Circuit Diagrams
  • Earth Leakage Circuit Breaker
  • Star Delta Starter Circuit Diagrams
  • Control Two Motors after Time Delay
  • Thermal Protection Relay for Motors
Example of PLC Programming based on Logic Circuit
Count and Pack Objects from Conveyor using PLC Ladder Logic
Electric Motors Noises – Types, Possible Sources, Reasons
Control Modes of Air Handling Unit (AHU) – HVAC Basics
PLC Timer Programming Examples – TON, TOF, TP and TONR
How to Control VFD with PLC using Ladder Logic
3 Comments
  • ENOCK Samwel says:
    June 18, 2022 at 10:58 pm
    Great
  • Abdalhameed stohy says:
    September 22, 2022 at 3:26 pm
    To calculate no of rods u use area required to dissipate fault current by 48 though it is calculated by 600mm2,how
    • ksn murthy says:
      December 8, 2023 at 11:50 am
      I WANT SEE THE REPLY
PID in Studio 5000
Alarm Simulator for Annunciator Logic
PLC System Documentation
PLC Program for Alarm Security System
Parts of PLC
Types of Industrial Storage Batteries
DP Master System Configuration in PLC
OMRON PLC program for waste-burning automation
Waste-Burning System OMRON PLC Program Example
Instruction List in PLC Programming
What is an Instruction List? – PLC Programming
PLC program for bread oven
Bread Oven Control in Auto and Manual Modes PLC Program
Push button Motor PLC Logic
Current Earth Leakage Circuit Breaker
Types of Earth Leakage Circuit Breaker
Latched and Momentary Operation of Motor PLC Program
Process Alarms Types
Process Switches and Alarms
PLC program for Sorting System by Size Example
PLC Based Product Sorting Machine System – Lift Control
Networking Interview Questions
Top 100 Networking Interview Questions & Answers
Temperature Switch Working
Basics of Temperature Switch
Control Sytem Open Loop and Closed Loop
Introduction to Control System
Types of Batteries
Types of Batteries
VPN for Control Engineers
How Important is VPN for Control Engineers?
MCB Nameplate Details
MCB Nameplate Questions and Answers
How to use Scale and Normalize Instructions in PLC
Control Valve Testing for Noise Measurement