Reading: Calculate Temperature of RTD
Inst Tools > Blog > Practical Questions > Calculate Temperature of RTD
Last updated: June 6, 2018 9:49 am
Practical Questions
0 Min Read
Determine the temperature of the RTD, given a measured voltage of −59.7 millivolts between test points C and D in this circuit:
Assume a 100 Ω RTD with α = 0.00392.
Answer :
RRTD = 107.256 Ω
T = 65 degrees Fahrenheit (from table)
T = 65.32 degrees Fahrenheit (from formula)
Smart DP Transmitter Flow Meter Calculations
Why Pressure Vessel Connected to Tubing System?
Identify Problem with Oily Water Filter Instrumentation
Practical Process Control System Questions & Answers – 7
Problem on Weigh feeder
Programmable Logic Controller (PLC) Questions and Answers – 17
PLC Pump Permissive Interlocks
Instrument Salesperson Question
PLC Program to Control a Water Pump
Importance of Temperature in Remote Seal Pressure Transmitter
Determine Level of Liquid in the Vessel and its Specific Gravity
Question on Remote Seal with Capillary Tubing Transmitter
Programmable Logic Controller (PLC) Questions and Answers – 10
Instrument Switch Status
Define Normal Status of a Process Switch ?
Calculate Hydraulic System Fluid Pressure
Pressure Switch Questions
Transmitter Calibration Range of a Vessel Level
Simple Pressure Transmitter Circuit
Pressure Transmitter using Potentiometer and Diaphragm
Tank uses 3 Pressure Transmitters to Measure Level & Density
measure the temperature of RTD
Measure the Temperature of the RTD
Programming in Omron PLC
Ultrasonic Flowmeters Principle
Factors Affecting the Performance of Ultrasonic Flow Meters
Thermocouple Testing
Thermocouple Cold Junction Compensation
Modbus in Industrial Networks
Oxygen Measurement using Tunable Diode Laser System
Tunable Diode Laser Analyzer Working Principle
Measure Duty Cycle using Multimeter
How to Measure Duty Cycle using Multimeter
desuperheater
Desuperheater Design
Thyristor Firing Circuits Multiple Choice Questions