Reading: Root Cause Analysis – Burst Transformers and 11 kV Input Breakers
Inst Tools > Blog > Electrical Basics > Root Cause Analysis – Burst Transformers and 11 kV Input Breakers
Root Cause Analysis (RCA): An 11000/400V electrical transformer and its 11 kV input breaker burst on an occasion incident.
Last updated: September 28, 2022 3:20 pm
S Raghava Chari
Electrical Basics Root Cause Analysis (RCA)
2 Min Read
Root Cause Analysis (RCA): An 11000/400V transformer and its 11 kV input breaker burst on an occasion and an 11/3.3KV transformer only on another.
Note: This root cause analysis (RCA) is from real-time scenarios that happened in industries during the tenure of one or two decades ago. These articles will help you to improve your troubleshooting skills and knowledge.
Burst Transformers Root Cause Analysis
Transformer Image (Note: This image is not related to this article)
Electrical Systems Insulation Resistance (IR) falling below the thumb rule 1 MΩ / kV because of the plant’s corrosive emissions and system flashes were common in that plant.
The author tipped by a US journal ad purchased the advertised Silicone Compound 800 kg, cleaned well all indoors and outdoors 110 kV, 11 kV, 3.3kV, and 400 V electrical systems insulators and 3-mm thick SC coated.
Maybe one such low IR – before the SC era – caused several times the rated load current fault currents and the unreliable breaker not tripping on protection relay command burst; the connected transformer also burst.
The second case is analogous to the first but the transformer only burst and fortunately the breaker survived.
Author: S. Raghava Chari
  • Contactor – Basics, Wiring
  • What is a Capacitor Bank?
  • What is an Electrical Drive?
  • Electrical Enclosure Book
  • Types of Circuit Breakers
Frequent Feeder-A Lightning Arrester (LA) Bursts – Root Cause Analysis
DOL Starter – Working, Circuit, Advantages, Disadvantages, Applications
Motor Cooling Methods
How do AC Drives Work? – Variable Frequency Drive (VFD)
Instrumentation Engineering Problems Solved – Root Cause Analysis
Compressor IP Case Discharge Temperature Gradually Increases
What is a Semiconductor Fuse?
Difference Between UL489 and UL1077
Introduction to Protective Systems
Safety Liquid Ammonia Disconnect threatens NH3 Vapor Spill
Applications of Variable Frequency Drive (VFD)
How to Locate Faults in Cables? – Fault Analysis & Location
Formula of AMP, KW, KVA, HP for AC and DC Voltages
CO2 Stripper Collapsed Internals Revamp
Weigh Feeder Drive
Failing Weigh Feeders and Mechanical Variable Speed Drives (VSD)
Capacitor Bank
Poor Power Factor Boosted – Industrial Electrical Problems
What Happens When a Pump Runs Dry
What Happens When a Pump Runs Dry? How to Avoid it?
Fence grounding specifications
All About Electric Fence Gates
VFD Engineer Roles - Installation and Commissioning
VFD Engineer Roles – Installation and Commissioning
Electrical Drives Animation
Why is Motor Control Required in Control Systems
Why is Motor Control Required in Control Systems?
Calculating Loop Voltage Drop
Instrument Cable Voltage Drop
Digital Electronics Objective Questions – Set 7
Vibration Measurement Questions
Interview Questions on Vibration Measurement
Impulse Line Pressure Testing Procedure
PLC Sequence Programming Ladder Logic
Creating Logic in Intouch Using Scripting
Create Logic with InTouch Scada using Scripting
Pilot Operated Back Pressure Regulator Valve