Inst ToolsInst ToolsInst Tools
  • Courses
  • Automation
    • PLC
    • Control System
    • Safety System
    • Communication
    • Fire & Gas System
  • Instrumentation
    • Design
    • Pressure
    • Temperature
    • Flow
    • Level
    • Vibration
    • Analyzer
    • Control Valve
    • Switch
    • Calibration
    • Erection & Commissioning
  • Interview
    • Instrumentation
    • Electrical
    • Electronics
    • Practical
  • Q&A
    • Instrumentation
    • Control System
    • Electrical
    • Electronics
    • Analog Electronics
    • Digital Electronics
    • Power Electronics
    • Microprocessor
  • Request
Search
  • Books
  • Software
  • Projects
  • Process
  • Tools
  • Basics
  • Formula
  • Power Plant
  • Root Cause Analysis
  • Electrical Basics
  • Animation
  • Standards
  • 4-20 mA Course
  • Siemens PLC Course
Reading: Troubleshooting a Power Supply Circuit
Share
Font ResizerAa
Inst ToolsInst Tools
Font ResizerAa
  • Courses
  • Design
  • PLC
  • Interview
  • Control System
Search
  • Courses
  • Automation
    • PLC
    • Control System
    • Safety System
    • Communication
    • Fire & Gas System
  • Instrumentation
    • Design
    • Pressure
    • Temperature
    • Flow
    • Level
    • Vibration
    • Analyzer
    • Control Valve
    • Switch
    • Calibration
    • Erection & Commissioning
  • Interview
    • Instrumentation
    • Electrical
    • Electronics
    • Practical
  • Q&A
    • Instrumentation
    • Control System
    • Electrical
    • Electronics
    • Analog Electronics
    • Digital Electronics
    • Power Electronics
    • Microprocessor
  • Request
Follow US
All rights reserved. Reproduction in whole or in part without written permission is prohibited.
Inst Tools > Blog > Electronic Basics > Troubleshooting a Power Supply Circuit

Troubleshooting a Power Supply Circuit

Last updated: June 6, 2019 3:22 pm
Editorial Staff
Electronic Basics Instrumentation Design
No Comments
Share
6 Min Read
SHARE

Troubleshooting is the application of logical thinking combined with a thorough knowledge of circuit or system operation to identify and correct a malfunction. A systematic approach to troubleshooting consists of three steps: analysis, planning, and measuring. A defective circuit or system is one with a known good input but with no output or an incorrect output.

Contents
AnalysisPlanningMeasurement

For example, in Figure (a), a properly functioning dc power supply is represented by a single block with a known input voltage and a correct output voltage. A defective dc power supply is represented in part (b) as a block with an input voltage and an incorrect output voltage.

Analysis

The first step in troubleshooting a defective circuit or system is to analyze the problem, which includes identifying the symptom and  eliminating as many causes as possible.In the case of the power supply example illustrated in Figure (b), the symptom is that the output voltage is not a constant regulated dc voltage.

This symptom does not tell you much about what the specific cause may be. In other situations, however, a particular symptom may point to a given area where a fault is most likely.

DC Power Supply Fault Analysis

The first thing you should do in analyzing the problem is to try to eliminate any obvious causes. In general, you should start by making sure the power cord is plugged into an active outlet and that the fuse is not blown. In the case of a battery-powered system, make sure the battery is good. Something as simple as this is sometimes the cause of a problem.

However, in this case, there must be power because there is an output voltage. Beyond the power check, use your senses to detect obvious defects, such as a burned resistor,broken wire, loose connection, or an open fuse. Since some failures are temperature dependent, you can sometimes find an overheated component by touch.

However, be very cautious in a live circuit to avoid possible burn or shock. For intermittent failures, the circuit may work properly for awhile and then fail due to heat buildup. As a rule, you should always do a sensory check as part of the analysis phase before proceeding.

Planning

In this phase, you must consider how you will attack the problem. There are three possible approaches to troubleshooting most circuits or systems.

  1. Start at the input (the transformer secondary in the case of a dc power supply) where there is a known input voltage and work toward the output until you get an incorrect measurement. When you find no voltage or an incorrect voltage, you have narrowed the problem to the part of the circuit between the last test point where the voltage was good and the present test point. In all troubleshooting approaches, you must know what the voltage is supposed to be at each point in order to recognize an incorrect measurement when you see it.
  2. Start at the output of a circuit and work toward the input. Check for voltage at each test point until you get a correct measurement. At this point, you have isolated the problem to the part of the circuit between the last test point and the current test point where the voltage is correct.
  3. Use the half-splitting method and start in the middle of the circuit. If this measurement shows a correct voltage, you know that the circuit is working properly from the input to that test point. This means that the fault is between the current test point and the output point, so begin tracing the voltage from that point toward the output. If the measurement in the middle of the circuit shows no voltage or an incorrect voltage, you know that the fault is between the input and that test point.

Therefore, begin tracing the voltage from the test point toward the input. For illustration, let’s say that you decide to apply the half-splitting method using an oscilloscope.

Measurement

The half-splitting method is illustrated in Below Figure with the measurements indicating a particular fault (open filter capacitor in this case). At test point 2 (TP2) you observe a full-wave rectified voltage that indicates that the transformer and rectifier are working properly.

This measurement also indicates that the filter capacitor is open, which is verified by the full-wave voltage at TP3. If the filter were working properly, you would measure a dc voltage at both TP2 and TP3. If the filter capacitor were shorted, you would observe no voltage at all of the test points because the fuse would most likely be blown.

A short anywhere in the system is very difficult to isolate because, if the system is properly fused, the fuse will blow immediately when a short to ground develops.

Power Supply Capacitor Filter Fault

Fig : Example of the half-splitting approach. An open filter capacitor is indicated.

For the case illustrated in Figure, the half-splitting method took two measurements to isolate the fault to the open filter capacitor. If you had started from the transformer output, it would have taken three measurements; and if you had started at the final output, it would have also taken three measurements, as illustrated in Figure.

Power Supply Transformer Problem

Fig (a) : Measurements starting at the transformer output

Power Supply Voltage Regulator Problem

Fig (b) : Measurements starting at the regulator output

Fig : In this particular case, the two other approaches require more oscilloscope measurements than the half-splitting approach in Figure.

Don't Miss Our Updates
Be the first to get exclusive content straight to your email.
We promise not to spam you. You can unsubscribe at any time.
Invalid email address
You've successfully subscribed !

Continue Reading

How to Measure capacitance using Multimeter
Basics of Permissive and Interlock Circuits
Instrument Numbering Philosophy
How to Select a Directional Valves
Difference Between Clamp Meters and Multimeters
Tagging Philosophy for Junction Box, Cable, and Cable Drum
Share This Article
Facebook Whatsapp Whatsapp LinkedIn Copy Link
Share
Leave a Comment

Leave a Reply Cancel reply

Your email address will not be published. Required fields are marked *

Stay Connected

128.3kFollowersLike
69.1kFollowersFollow
210kSubscribersSubscribe
38kFollowersFollow

Categories

Explore More

How to Select a Pressure Gauge
Testing a Transistor with a Digital Multimeter
Multiple Thermowell Installations Problems
Calculate Flow Coefficient Kv of Solenoid Valve
Important Factors for Thermocouple Selection
Package Control and Safety Systems Implementation Methods
Where should we Terminate the Cable Shields ?
Normally-Closed Contacts for Stop Buttons

Keep Learning

Instrumentation Cable trays in Horizontal Installation

Instrumentation Cable trays Installation in vertical orientation

Process Variable Damping Graph

Process Variable Damping of Transmitter

Analog signal with noise

Signal Coupling and Cable Separation

Failsafe interlock Design

Failsafe Wiring Practices

System Architecture in Industrial Automation

How to Design a System Architecture in Industrial Automation?

Differences between No-load Supply Current and Load Current

Differences between No-load Supply Current and Load Current

How to Identify the Transistor Terminals

Control Valve Packing

Control Valve Packing

Learn More

Bubbler Level Measurement System

Bubbler Level Sensor

Difference Between AIS and GIS Panels

Difference Between AIS and GIS Panels

Switched Mode Power Supply (SMPS)

How does SMPS Works? – Switched Mode Power Supply

Closed Tank Remote Seal Level Transmitter calculation

Remote Seal Transmitters Ranging Calculation

Industrial Oven Control Application with PLC Controller

Industrial Oven Control Application with PLC Controller

Oval gear Flow Meter Principle

Oval Gear Meter – Principle, Advantages, Limitations, Applications

SCR Switching Characteristics

SCR Switching Characteristics

MTech Project Ideas for Electronics and Electrical Engineering

100 MTech Project Ideas for Electronics and Electrical Engineering

Menu

  • About
  • Privacy Policy
  • Copyright

Quick Links

  • Learn PLC
  • Helping Hand
  • Part Time Job

YouTube Subscribe

Follow US
All rights reserved. Reproduction in whole or in part without written permission is prohibited.
Welcome Back!

Sign in to your account

Username or Email Address
Password

Lost your password?