Reading: Temperature Error of 2-Wire, 3-Wire & 4-Wire RTD
Inst Tools > Blog > Temperature Measurement > Temperature Error of 2-Wire, 3-Wire & 4-Wire RTD
Last updated: August 17, 2020 5:53 pm
6 Comments
3 Min Read
RTD or Ohm Inputs
The transmitters will accept a variety of RTD configurations, including 2-wire, 3-wire, 4-wire. If the transmitter is mounted remotely from a 3-wire or 4-wire RTD, it will operate within specifications, without recalibration, for lead wire resistances of up to 60 ohms per lead (equivalent to 6,000 feet of 20 AWG wire).
RTD or Ohm InputsSensor Lead Wire Resistance Effect – RTD InputTemperature Error of RTD
In this case, the leads between the RTD and 4-20ma transmitter should be shielded. If using only two leads, both RTD leads are in series with the sensor element, so significant errors can occur if the lead lengths exceed three feet of 20 AWG wire (approximately 0.05 °C/ft). For longer runs, attach a third or fourth lead as described above.
When using a 4-wire RTD, the effect of lead resistance is eliminated and has no impact on accuracy. However, a 3-wire sensor will not fully cancel lead resistance error because it cannot compensate for imbalances in resistance between the lead wires.
Using the same type of wire on all three lead wires will make a 3-wire RTD installation as accurate as possible. A 2-wire sensor will produce the largest error because it directly adds the lead wire resistance to the sensor resistance. For 2- and 3-wire RTDs, an additional lead wire resistance error is induced with ambient temperature variations.
The table and the examples shown below help quantify these errors.
RTD Sensor Error
Consider a RTD with the following parameters mentioned below. Calculate Resistance error or final temperature reading error in the transmitter with 2-wire, 3-wire and 4-wire configurations.
Given Data:
Total cable length: 150 m
Imbalance of the lead wires at 20 °C: 1.5 Ω
Resistance/length (18 AWG Cu): 0.025 Ω/m °C
Temperature coefficient of Cu (αCu): 0.039 Ω/Ω °C
Temperature coefficient of Pt(αPt): 0.00385 Ω/Ω °C
Change in Ambient Temperature (∆Tamb): 25 °C
RTD Resistance at 0 °C (Ro): 100 Ω (for Pt 100 RTD)
Pt100 4-wire RTD:
No lead wire resistance effect
Pt100 3-wire RTD:
Three Wire RTD Lead Wire Resistance Error
Pt100 2-wire RTD:
Two Wire RTD Lead Wire Resistance Error
Reference : Rosemount Temp Manual
Thermocouple Working Principle
Thermocouple Temperature Range Questions and Answers
Foundation Fieldbus Temperature Transmitter Configuration
Temperature Switch Principle
RTD Calculator Software
Temperature Switch Working Principle
6 Comments
  • Venkatesh says:
    March 2, 2017 at 3:22 am
    Very very useful data thanq for giving me such a data
  • Ali says:
    March 2, 2017 at 3:10 pm
    Thankyou so much Sir.You are doing a great job. Your efforts are helping thousands of people like me. God bless!
  • Shailesh says:
    January 1, 2019 at 4:38 pm
    Very very useful
  • Thamprasad says:
    January 6, 2019 at 6:45 pm
    I was having a question. It will be of grate help if someone could help me out.
    How are you going to compensate temperature in a RTD??
  • Steve says:
    September 28, 2019 at 8:07 am
    I have an RTD. Sometime the reading go bad and some time it ok. I measure rtd resistance it ok. And wire not shorted. It if the rtd body touches the metal piping it causes my reading on my transmitter to go bad. I remove the rtd from any metal contact then ok. We have replace the transmitter also same.
  • Nicolas says:
    December 19, 2020 at 12:47 am
    Is it possible that the error due to amb. temp. var. of +-25 deg C, for 3-wire RTD, would be +-0.13degC (instead of +-13 deg C)?
Helix Bimetallic Thermometer Principle
Thermistors and Resistance Temperature Detectors (RTDs)
What is a Thermopile ?
Thermocouples Sources of Error
Optical Pyrometer Working Principle
Seebeck Effect Theory
Applications of Temperature Scanner
Formula of 2 Wire RTD, 3 Wire RTD & 4 Wire RTD
Temperature Sensors Questions
Questions on Thermocouple and Pyrometer
RTD Graph
Calculate Temperature Coefficient of RTD
Temperature Calibration Bath
Temperature Calibration Bath Principle
PTC NTC Thermistors Comparation
Thermistor Working Principle
Convert 2 wire RTD to 4 wire RTD Sensor
How to Convert 2 wire RTD into 3 or 4 wire RTD?
RTD Testing Methods
RTD Testing Methods in Calibration Laboratory
non-contact pyrometer principle
Non-contact Temperature Sensors
Temperature Measurement Questions
Interview Questions on Temperature Measurement
deadweight tester principle
Pressure Standards
Solenoid Valves Selection Guidelines
HART Multidrop Network
HART Communication Tutorial Part 2
Control Systems Questions & Answers
Control Systems Objective Questions & Answers – Set 6
Slop Tank Level Transmitter Erection
Wrong Installation of Horn Type Radar Level Transmitter on Sloping Tank
Battery Interview QuBattery Interview Question and Answersestion and Answers
Battery Terminology
why-symmetrical-components-used
Why Symmetrical Components Used for Unbalanced faults in Power System
Precision Instruments Interview Questions