Reading: Split Range Control Application using PLC Ladder Logic
Inst Tools > Blog > PLC Tutorials > Split Range Control Application using PLC Ladder Logic
Split Range Control Application: Design a PLC ladder logic to control two control valves using split range control logic.
Last updated: November 3, 2023 2:49 pm
6 Comments
7 Min Read
This article covers the basics of split Range control application used for controlling more than one final control element in process control.
Split Range Control ApplicationProblem DescriptionProblem DiagramProblem SolutionList of Inputs and OutputsPLC Program for split range controlProgram Description
Split Range Control Block Diagram
Problem Description
The products need to be heated and cooled depending on the temperature. There is one PID controller and we need to control 2 control valves.
Write a PLC program using ladder diagram language for this application.
Problem Diagram
Split Range Control using PID Controller
Problem Solution
For this type of application, we need to use split range concept.
Split range concept mostly used when single controller is used to control multiple final control elements.
Here we considered temperature control application. Two control valves and one PID controller are used for temperature control.
Here consider one valve for cooling and another valve for heating process.
We will split controller output (here PID controller) for two different valves as shown in above figure.
In the diagram above, the 0% to 100% range of the PID controller output is connected to the SPLIT block and  further control valves are connected to this SPLIT block as shown in above figure.
If the PID controller output is in between 0% to 50%, it is the cooling valve that is in operation. This valve is fully open when the controller output is 0% and fully closed when the controller output is 50%.
If the PID controller output is between in 50% to 100%, it is the heating valve that is in operation. At 50%, the heating valve starts to open and it is fully open at 100% of the controller output.
So, with PLC you can split both output using programming, hence you can connect 2 control valves with separate analog output of the PLC.
Also Read: Types of Split Range Control
Inputs List
  • PID enable :- M61.0
  • Manual enable :- M61.1
  • PID reset :- M61.2
  • Analog input form TC :- IW64
Outputs List
  • Cooling control valve analog output :- QW96
  • Heating control valve analog output :- QW98
M memory
  • Set temperature :- MD500
  • Actual temperature :- MD704
  • PID output (%) :- MD758
  • PID outputs for heating control valve :- MW762
  • PID outputs for cooling control valve :- MW766
  • PID state word :- MW770
  • PID error word :- MD778
  • PID enable input :- M61.0
  • PID manual mode enable input :- M61.1
  • PID controller reset :- M61.2
  • PID high limit alarm :- M766.0
  • PID low limit alarm :- M766.1
  • PID input warning :- M766.2
Split Range Control Logic
Split Range Control Logic PLC
Valve Split Range Control Logic
Split Range Control Logic using PLC
Split Range Control application
Program Description
For this application, we used S7-1200 PLC and TIA portal software for programming.
Network 1
In network we configured standard parameters for PID function.
  • “Drive PID”.sRet.r_Ctrl_Gain:- saved proportional gain or P gain for PID (1.0).
  • “Drive PID”.sRet.r_Ctrl_Ti:-Saved integral time or I gain for PID (20s).
Network 2
“Drive PID”.sRet.r_Ctrl_Td:-Saved derivative time or D gain for PID (0s).
Network 3
Here we have taken temperature PID max output limit and minimum output limit. We have considered here max limit for PID output 100 and minimum limit is 0.
Network 4
Sampling time of the PID_Compact instruction r_Cycle is determined automatically and usually equivalent to the cycle time of the calling OB. Consider 0.1s for this application.
Network 5
When PID enable (M61.0) is pressed PID block will be executed. As per SET point (MD500) it will generate output (0-27648) and according to actual temperature transmitter will give feedback (IW96) to PID.Manual enable (M61.1) is for manual operation and PID reset (M61.2) is for resetting the PID.
Network 6
Activate Mode after CPU restart If sb_RunModeByStartup = FALSE, the controller will remain inactive after a CPU startup.
Network 7
Here we used split range concept for output splitting. If PID output is between 0% to 50%, cooling valve will be working and if PID output is between 50% to 100%, heating valve will working.
Here we consider fail open valve for cooling and fail close valve for heating. Hence cooling valve is fully open when PID output is 0% and fully closed when PID output is 50%.
Similarly for heating valve, it will start to open when PID output is 50% and fully open when PID output is 100%.
Network 8
If PID output is less than 50%, zero valve will move in heating valve analog channel.
Network 9
Here we used inverse PID logic for fail to open valve.
Note:- Above application may be different from actual application. We can also make this application by using ready-made PID controllers and current to pressure converters.
This example is only for explanation purpose only. We can implement this logic in other PLC also. This is the simple split range control application used in industry, we can use this concept in other examples also.
All parameters and graphical representations considered in this example are for explanation purpose only, parameters or representation may be different in actual applications. Also all interlocks are not considered in the application.
Author: Bhavesh
  • PID Controller Selection
  • Exclusive Control Valve Sequence
  • How to tune a PID Controller?
  • PID Controller Theory
PLC Program for 2 Push buttons to Control 1 Output
Smart Spray System using Wecon PLC
PLC Program for Trash Compactor
PLC based Automatic Bell System for a School
What are Trends in SCADA?
Timer in Studio 5000 – TON, TOF, RTO
6 Comments
  • Jerko Viskov says:
    November 23, 2018 at 11:38 pm
    Where do you write your MW766 for cooling control valve , if there is only on PID function?
    November 23, 2018 at 11:50 pm
    Oh i see, network 9. Nice article btw.
  • Sankar says:
    December 11, 2018 at 10:04 am
    Hi I learn a plc
  • Digvijay Patil says:
    September 19, 2019 at 11:18 am
    Hello sir … Your every article is very usefull for us..can you make an article of program distribution and subroutine call up for AB PAC series
  • Krupali says:
    May 7, 2020 at 11:00 pm
    How split range control carried out in field without 2 Analog Outputs?
    • Jigar Patel says:
      May 12, 2020 at 3:38 pm
      Krupali, We have implemented split range control with one analog output. we have split the air output from one I/P converter to two control valves.
      For 0 to 50% o/p valve-1 will operate, 50-100 % valve-2 will operate( CV-2 is air to open and CV-1 is air to close) at 50% output both CVs are closed.
      we have Calibrated CV-1 Positioner to be fully open 0%( 3 psi from I/P ) and fully open at 50% (9 Psi from I/P). same for CV-2 Positioner fully closed at 50% (9 psi from I/P) and fully open at 100% (15 Psi from I/P). For this to work we need to Calibrate CV Positioner with our suitable range. CV-1 is Cooling valve, CV-2 is heating valve.
Allen Bradley RSLogix 500 PLC Programming
Two Hand Control Logic using PLC
PLC Program to Separate Different Size Objects
#6 PLC Best Practices – Validate Timers and Counters
Classroom Bell System – PLC Programming Practice Examples
Single-acting Cylinder OR Logic Operation (PLC and Sensors)
A Typical Sequential Function Chart
What is Sequential Function Chart (SFC?)
Ladder Logic Vs. Other Programming Languages - PLC Basics
Ladder Logic Vs. Other Programming Languages – PLC Basics
What is Ladder Diagram Programming ?
SCADA System
What is SCADA System?
Basics of Motion Controllers
OPC Server
What is the OPC Server?
DeMorgan's Theorems
DeMorgan’s Theorems using Ladder Diagram
Distributed Network Protocol Communication
DNP3 Communication Protocol Overview
Start the Counting from a Preset Value in PLC
How to Update the Firmware Version of your PLC
How to Update the Firmware Version of your PLC? – TIA Portal
Bourdon Tube Pressure Gauge Parts
Capacitor Bank
Poor Power Factor Boosted – Industrial Electrical Problems
Convert-Transmitter-Output-in-Percentage-to-Process-Variable
Conversion of Transmitter Output in Percentage to Process Variable
What is Temperature
What is Temperature ?
gas chromatograph principle
Online Gas Chromatograph Principle