Reading: Question on Analytical Controller
Inst Tools > Blog > Practical Questions > Question on Analytical Controller
Last updated: March 10, 2020 9:24 am
Practical Questions
2 Min Read
The ratio between base flow and pigment flow in this paint-mixing control system is not fixed. Rather, it comes from the output of an “analytical” controller:
1. Explain the rationale behind this ratio control system. Also, identify what the “other control system” might be that drives the base control valve.
Answer:
The purpose of this control system is to control the coloring of the paint by analyzing its color using a special instrument, which feeds its color signal to a color controller (AIC), which then automatically adjusts the ratio between base and pigment to achieve the desired output color.
As for the “other control system,” it would most likely be a flow (production) controller.
2. Identify sources of dead time in this process, and which control loop(s) will have to manage despite the presence of dead time.
3. Analyze the effects of the base flowmeter turbine jamming, so that it does not spin even while liquid is still flowing.
4. Analyze the effects of the pigment flowmeter turbine jamming, so that it does not spin even while liquid is still flowing.
5. Assuming the AT outputs a greater signal as the paint becomes more pigmented, determine the correct action for the AIC controller.
Join the Discussion! Share your answers with us through below comments section.
  • Ziegler-Nichols Open-Loop
  • Ultrasonic Tank Gauging
  • What is Annunciator Panel?
  • Distributed Control System
  • What is Orifice equation?
Displacer Level Transmitter Question & Answer
Loop Powered Pressure Transmitter
Air Pressure Regulator Questions
Identify Instrumentation Terms in Water Supply System
Thermocouple Measurement and Reference Junction Temperatures
Determine Resistance value of Resistors
Pressure Switch Questions
Solenoid Valves Practical Problems
Programmable Logic Controller (PLC) Questions and Answers – 8
Thermocouple Terminal block Questions
Practical Process Control System Questions & Answers – 10
Simple Pressure Repeater
Identify High Flow Alarm and Low Flow Alarm?
Connect the Differential Pressure Gauge at the Filter
How Do You Connect the Differential Pressure Gauge at the Filter?
statuses of all lamps and relay coils in the circuit
Analyze the Relay Circuit and Find the Status ?
Electronic Force Balance Pressure Transmitter
Level-Measuring-Instruments-Velocities-of-Propagation
Level Measuring Instruments Velocities of Propagation
Identify Problem with Oily Water Filter Instrumentation
two chemical streams are mixed together
Practical Process Control System Questions & Answers – 12
Explain What these Spool Valve Represent
Explain What these Spool Valve Symbols Represent?
Calculate the 0%, 50%, and 100% Calibration Points
Do’s and Don'ts in PLC
#18 PLC Best Practices – Store PLC Hard Stop Events from Faults
Difference Between RS232 and RS485
How to Delay a Sensor Signal in PLC?
Multiple Thermowell Installations Problems
How Could FB and FC Make Me Professional PLC Programmer
How Could FB and FC Make Me Professional PLC Programmer?
PLC-Complete-Training-Package
Free PLC Training Software Download
Control Systems Questions & Answers
Control Systems Objective Questions & Answers – Set 7
SCL Language in Siemens Tia Portal