Reading: Run 4 Motors Sequentially from Same Push button PLC Program
Inst Tools > Blog > PLC Tutorials > Run 4 Motors Sequentially from Same Push button PLC Program
Last updated: March 4, 2021 11:50 am
3 Min Read
In some industrial automation applications, you may need to operate more than one motor or pump in sequential order by the same digital input such as start push button.
Run 4 Motors Sequentially from Same Push buttonPLC Program
Write a PLC program to run 4 motors in a case that every time you press the same push button it runs one motor at a time and then press the stop pushbuttons all motors should be stopped.
Note the best practice to learn the PLC programming is to start writing the PLC program, take your time before you review the answer.
Inputs & outputs:
  • I0.0: Start (Normally open contact)
  • I0.1: Stop (Normally closed contact)
  • Q0.0: Motor_01
  • Q0.1: Motor_02
  • Q0.2: Motor_03
  • Q0.3: Motor_04
  • M0.0: marker for positive edge
  • M0.1: marker for positive edge
  • M0.2: marker for positive edge
PLC Program
First network:
Motor # 04 will be on if the motor# 03 is on and a positive edge is detected from the Start Push Button. And will be off if the stop push button is pressed.
Second network:
Motor # 03 will be on if the motor# 02 is on and a positive edge is detected from the Start Push Button. And will be off if the stop push button is pressed.
Third network:
Motor # 02 will be on if the motor# 01 is on and a positive edge is detected from the Start Push Button. And will be off if the stop push button is pressed.
Fourth network:
Motor# 01 will be on if the start push button is pressed. And will be off if the stop push button is pressed.
Why we used positive edge detection? To avoid running all the motors in one time if the push button is pressed for the first time.
The order of all the networks is important. That’s why you can see the first network is dedicated to the 4th motor and so on, that’s because the fact that the PLC executes the program as the following it first reads all the inputs, then executes the program from the first network to the last network and then move the outputs values upon the program execution.
Author: Karim Ali Anwar
  • FC Function in Siemens
  • Pulse Generation using PLC
  • Motor Control Circuit
  • Memory Structure of PLC
  • What is Motor Jogging?
#9 PLC Best Practices – Validate indirections
Peripheral Inputs and Outputs in Siemens PLC
Basic Pumping System Application Used in Industrial Automation
Getting to Know the LED Indications on GE Make PLC
What is Profinet and How to Configure in Siemens PLC?
Delta PLC Counter with Comparison
PLC Programming Videos
Automatic Railway Crossing Gate Control PLC Program
PLC Programming for Sequential Batch Mixing System
Exhaust Fan Control
Exhaust Fan Control: Example of PLC Timer Programming
Redundant system communication cable
What is Interface Module in Siemens PLC?
How to Create DFB in Schneider PLC? – Derived Function Block
If Else Statement in SCL Language
MCQ on PLC (Programmable Logic Controller)
PLC Programming Software
What is Siemens TDC - Siemens Control System
What is Siemens TDC? – Siemens Control System
PLC Power Supply and Operating Voltages
Interferometer Principle
Radar and Ultrasonic Level Transmitter Problems Troubleshooting
Radar and Ultrasonic Level Transmitter Practical Problems Troubleshooting
Guide to vibration severity per ISO 10816
Importance of Vibration Measurement
Power Transistor Quiz
Simulating Level Sensor and the Pump Logic in PLC
PLC Basics – Manual Control, Closed Loop, ON-OFF with Hysteresis
Rotameter
What is a Variable Area Flow Meter?
DC Machines Torque Quiz
Steam Pressure Taps Primary Block Valves Glands and Bonnets Leaks
Instrument Steam Pressure Taps Primary Block Valves Glands and Bonnets Leaks