Let us understand the logic written for detecting motor failure and stopping the system.
A start pushbutton is used to start the motor. A stop button is used to stop the motor. After pressing the start pushbutton, the motor will be started but due to any other reasons if the motor was not started in 5 seconds then initiate an alarm.
This logic is basically divided into four rungs.
PLC Motor Feedback
Let us understand the flow of each rung one by one:
  1. Start button and stop button are used as PLC inputs. The motor is the digital output. Start button is NO contact and stop button is NC contact. On pressing start button, the motor will start and latch in parallel with start button. This is written in first rung
  2. In the second rung, we check for motor feedback after motor turns ON. If feedback is not received after 5 seconds, then the alarm timer will turn ON.
  3. In the third rung, the alarm timer output turns on the alarm bit and latches it. As soon as this happens, the first rung is cut off due to alarm contact, and the motor turns OFF. Now, the motor will remain OFF as long as the alarm is ON.
  4. In the fourth rung, the alarm reset input is used to reset the alarm. As soon as the alarm is reset, the motor path will again become open for operation in the first rung. Then, after pressing start button, the cycle repeats.
  • Automation Documents
  • Delta PLC & VFD Modbus
  • Compare PLC and SCADA
  • PLC and DCS System Checks
  • DCS System Maintenance
PLC Program for Controlling a Water Pump with 3 Power Sources
CX-Programmer Products Sorting & Counting – Omron PLC
Basic PLC Exercise on Heater and Cooler for Students
Free SCADA Training Course
3 Comments
  • Supriadi says:
    December 25, 2022 at 8:09 pm
    how can the timer work while not getting power supply
  • Deen says:
    December 30, 2022 at 9:26 am
    Is #Motor_Fb tag in rung 2 a PLC input?
    • Editorial Staff says:
      December 30, 2022 at 2:52 pm
      Yes, motor running feedback from substation/mcc.
Allen Bradley Studio 5000: Motor Running Hours PLC Program
SAVE and BR Memory Instructions in Siemens PLC Programming
Mitsubishi PLC Programming Tutorials
Pump and Mixer Operations Example: PLC Timer-Based Control
Procedure for Reading or Searching the Tag number in Siemens PLC
Can a PLC Function Without an HMI or SCADA?
PLC Program for Continuous Filling Operation
PLC Program for Traffic Light Sequence using Functional Blocks
Static and Temp Variables in PLC
PLC Programming Example on Bottle Line Control
Free Industrial Control System (ICS) Cyber Security Training Course
Functional Block Diagram of XNOR Logic Gate
PLC Functional Block Diagram for Logic Gates
Top PLC Manufacturers
PLC Brands Software Information
Retrieve from memory card
How to Retrieve PLC Project From Memory Card?
Features of Scada Which are Must in an IoT System
Frequency Response MCQ
How Much Pressure indicated by Micromanometer
How Much Pressure Indicated by Micromanometer?
Interview Questions for Instrument Engineers
principle of time base generator
Time Base Generator
What is a Current Transformer
What is a Current Transformer?
Loop Diagram
PT Loop Diagram Faults
Difference-between-pneumatic-electric-hydraulic-actuators
Difference between Pneumatic, Electrical & Hydraulic Actuators
Fibre Optic Sensors Objective Questions