Inst ToolsInst ToolsInst Tools
  • Courses
  • Automation
    • PLC
    • Control System
    • Safety System
    • Communication
    • Fire & Gas System
  • Instrumentation
    • Design
    • Pressure
    • Temperature
    • Flow
    • Level
    • Vibration
    • Analyzer
    • Control Valve
    • Switch
    • Calibration
    • Erection & Commissioning
  • Interview
    • Instrumentation
    • Electrical
    • Electronics
    • Practical
  • Q&A
    • Instrumentation
    • Control System
    • Electrical
    • Electronics
    • Analog Electronics
    • Digital Electronics
    • Power Electronics
    • Microprocessor
  • Request
Search
  • Books
  • Software
  • Projects
  • Process
  • Tools
  • Basics
  • Formula
  • Power Plant
  • Root Cause Analysis
  • Electrical Basics
  • Animation
  • Standards
  • 4-20 mA Course
  • Siemens PLC Course
Reading: Level Transmitter and Level Gauge Design Tips
Share
Notification Show More
Font ResizerAa
Inst ToolsInst Tools
Font ResizerAa
  • Courses
  • Design
  • PLC
  • Interview
  • Control System
Search
  • Courses
  • Automation
    • PLC
    • Control System
    • Safety System
    • Communication
    • Fire & Gas System
  • Instrumentation
    • Design
    • Pressure
    • Temperature
    • Flow
    • Level
    • Vibration
    • Analyzer
    • Control Valve
    • Switch
    • Calibration
    • Erection & Commissioning
  • Interview
    • Instrumentation
    • Electrical
    • Electronics
    • Practical
  • Q&A
    • Instrumentation
    • Control System
    • Electrical
    • Electronics
    • Analog Electronics
    • Digital Electronics
    • Power Electronics
    • Microprocessor
  • Request
Follow US
All rights reserved. Reproduction in whole or in part without written permission is prohibited.
Inst Tools > Blog > Guest Articles > Level Transmitter and Level Gauge Design Tips

Level Transmitter and Level Gauge Design Tips

Last updated: September 21, 2019 3:06 pm
Editorial Staff
Guest Articles Instrumentation Design Level Measurement
14 Comments
Share
7 Min Read
SHARE

Level Transmitter and Level Gauge Design Tips

Contents
Level / Vessel SketchesDisadvantages / Advantages ?What are basic inputs required ?What are different types of vessels ?What can be different type of instruments put on vessels?Different combinations you can have on vessel (Stand pipe / direct nozzle)

Level / Vessel Sketches

What is this ?

Level sketch or vessel sketch is the drawing prepared by Instrumentation engineer to show various Level instruments nozzle details (Flange size, rating) on vessels / drums, their elevations which is used as input for Mechanical – Static (Vessel) Engineers for further engineering of vessel / drums.

Why this is prepared ?

This is prepared as an input document to Mechanical – Static (Vessel) department so that instrumentation interface is clear and documented.

Who benefits ?

It benefits both department engineers as interface details are documented and any changes are tracked as document will be revised.

Disadvantages / Advantages ?

Disadvantages :

For smaller project, if no of equipment are very less (such as 1 or 2) preparing this document would consume more efforts compared to large scale projects.

Advantages :

The interface between two disciplines is streamlined and there is no scope for difference in inputs and information. The changes will always be traceable. If ambiguity is found, this can be documented and corrected.

What are basic inputs required ?

  • P&ID (Design level),
  • IPDS (Design level),
  • Mechanical data sheet (Design level),
  • Piping Specification (Design level),
  • Instrumentation Design Basis (Design level),
  • Client / Process Licensor Specific requirements

What are different types of vessels ?

Types of Vessels for Level Transmitter Installation - 1

What can be different type of instruments put on vessels?

  • Level Transmitter (Contact / Non-Contact type)
  • Level – Differential Pressure Transmitter
  • Level Gauge (Magnetic, Transparent, Reflex)

Different combinations you can have on vessel (Stand pipe / direct nozzle)

The Level Instrument nozzle can be directly installed on vessel. 

Level Transmitter mounted on Vessel and Tank

Figure 1 – Level Transmitter and Level Gauge Directly Mounted on equipment

Stand pipes are used for installing the level instruments.

Level Transmitter and Level Gauge Mounted on Stand Pipe Diagram

Figure 2 – Level Transmitter and Level Gauge Mounted on Stand Pipe

It is generally based on no of instruments to be put on single vessel as it is not advisable to puncture vessels for many instrument nozzles. This will be governed by project specifications, process requirements and client guidelines.

Standpipes are generally used in following scenarios –

  • Multiple Level Gauges
  • More than 3 no instruments on same equipment
  • Project specifications

What all information to show ?

Equipment Details –

  • Vessel Tag no.
  • Nozzle Nos,
  • Elevations (in mm preferable),
  • Tank Lines (Lower & Upper)
  • Zero elevation line (either from TL or at other reference point),
  • Piping Specification, material 

Process Details –

  • Process fluid,
  • Specific Gravity or Density,
  • Alarm Levels (Low, Low Low, High, High High)
  • Process & design conditions (Pressure & Temperature),

Instrument Details –

  • Instrument tag no,
  • Type of instruments (Radar, DP Level Transmitter, Magnetic Level Gauge),
  • C – C (Center to center) distance in mm preferably,
  • Isolation Valves and sizes,
  • Drain & Vent valves and sizes,
  • Scope Breaks (Instrumentation, Piping, Static),
  • Traced Lines (Steam / Electrical)/ Jacket Lines,
  • Instrument Nozzle size, connection, rating, Elevations in mm preferably,
  • Stand Pipe, size and connection details

What not to show

Other than Level Instrumentation Nozzles, other instruments nozzle such as Pressure / Temperature, Inlet, outlet nozzles, Nozzle orientation

Example: Single Level Transmitter & Single Level Gauge on a Vessel

Level Transmitter Design

Level Transmitter Design Sheet

Single Level Transmitter & Single Level Gauge

  • Service – Water
  • HLL = 1400 mm
  • HHLL = 1200 mm
  • LLL = 350 mm
  • LLLL = 300 mm
  • Density – 1000 kg/m3, Specific gravity – 1

Low Low Level should be at 10% of Transmitter Range (Subject to project specifications)

High High Level Should be at 90% of Transmitter Range (Subject to project specifications)

So based on the above guideline, different combinations can be tried to finalize the Transmitter Nozzle elevations.

Bottom Elevation (HP Tap) : 150 mm       (Refer Tip in the above diagram)

Top Elevation (LP Tap) : 1550 mm

Hence C-C Distance : 1400 mm

Transmitter Range = (HP Tap Elevation – LP Tap Elevation) * Sp Gravity

Transmitter Range =  (1550 mm -150 mm) * 1     = 1400 mm

Hence Select Transmitter Range : 0 – 1400 mm

Calculate LL Level of Level Transmitter

With This, LL level will be at @ 10.7% i.e.

Level Transmitter Design Calculation Formula

LL Level of LT =     [(300 mm – 150mm) / 1400 mm] * 100 = 10.71%

Calculate HH Level of Level Transmitter

And HH Level will be at @ 89.28%. i.e.

Level Transmitter Low Level Aalrm Design Calculation Formula

HH Level of LT =    [(1400 mm – 150mm) / 1400 mm] * 100 = 89.28%

Level Gauge Nozzle elevations can be at same elevation as it covers full transmitter Range.

Tip – The bottom nozzle elevation is at 150 mm due to welding at TL point of vessel, wherein welding thickness is @ 80 – 100 mm, Nozzle centre is at 150 mm and nozzle size is generally 2” for Transmitters due to which Instrument nozzle welding may clash with Vessel shell welding joints. Hence it is recommended to use 150 mm as general guidelines for bottom elevations.

In case it is required to go below 150 mm due to Low level alarm values, first discuss with process group if the alarm value can be changed and shifted towards upward side or discuss with client if LL alarm value at below 10% is acceptable or discuss with vessel engineer / group if nozzle elevation below 150 mm is possible.

Article Written by :
Nilima singh
Instrumentation and control Engineer
13 year experience in Detail engineering
Worked on various Refinery, Oil & Gas, Petrochemical and chemical projects
Don't Miss Our Updates
Be the first to get exclusive content straight to your email.
We promise not to spam you. You can unsubscribe at any time.
Invalid email address
You've successfully subscribed !

Continue Reading

Open and Closed Tank Level Calculations
Nuclear Level Detectors Cascade or Master/Slave concept
Ultrasonic Tank Gauging
How to select a load cell?
Instrumentation Bulk Material Requirements in Oxygen Service
General Specification of Thermowell
Share This Article
Facebook Whatsapp Whatsapp LinkedIn Copy Link
Share
14 Comments
  • Raj M says:
    September 9, 2017 at 5:58 pm

    Superb, Useful Information. I am maintanance instrumentation engineer. These are very useful to me & valuable knowledge to learn. Thanks

    Reply
  • Shoaib says:
    November 8, 2017 at 7:43 am

    thanks for sharing such useful info.

    Reply
  • Qadir Mohtasham says:
    May 17, 2018 at 12:18 pm

    Tnx for experience sharing

    Reply
  • George Ibraheem Yokhana says:
    May 17, 2018 at 1:41 pm

    Dear Nilima
    first of all thanks for this valuable information about the detail design for the level transmitter used for level measurement with the value of HH/LL/H/L according to the design criteria to detect all expected types of levels in case of filling or evacuate the tank and to avoid unexpected measurement during the two operation

    So all above drawings were related to liquid measurement .
    And kindly if possible can u provide us with the measurement detail design features used for Gas such as NGL or LPG of Spherical types ,because all above example or application are for liquid phase not gas phase thanks in advance

    Reply
  • Peter Obasi says:
    August 27, 2018 at 12:49 am

    thanks for the valuable information.

    Reply
  • Canaan sibanda says:
    May 4, 2019 at 4:11 pm

    Thank you so much…this is good information

    Reply
  • Kanterson says:
    June 6, 2019 at 12:17 pm

    As a general engineering practice, to consider at least 150 mm elevation not only for above BTL, but also for below TTL. The instrument nozzle elevation closed to the vessel/column TL should be avoid.

    Reply
  • ahammad says:
    January 20, 2020 at 4:46 pm

    thanks for your valuable information madam

    Reply
  • Sundararaman Radhakrishnan says:
    June 11, 2021 at 10:53 pm

    It should be noted that the level transmitters of displaced type come in standard lengths and level gages can match that distance by use of magnetic type ( glass types are not preferred as they are prone for breakage).

    Further, care should be exercised in condensing type services ( steam drums or other high temperature services) where it is preferable to use DP transmitter type ones.

    Unless otherwise mandated by codes ( boiler code mandate use of glass type level gauges , at least one ), other type of non-intrusive types such as capacitance or micro- wave type can be applied subject to temperature of the medium.

    For heavy hydrocarbon fluids ( such as pitch or tar), a nuclear gauge is optimum as this is non-contact type. Even use of diaphragm seal type is not ideal as this would dis-continuous flushing and complex.

    Again, for hydrocarbon large storage tanks , glass types in multiple lengths are expensive and an Enraf type micro-wave s ideal and cheap.

    Reply
  • Swathipriya S says:
    June 28, 2021 at 2:01 pm

    Thank you for this valuable information . I have a doubt regarding the vent valves in level gauge line can you please explain why do we need vent in level gauge line.

    Reply
  • robin says:
    July 13, 2021 at 2:12 pm

    some of LG lt Elevations not same why ?

    Reply
  • Deepak kumar says:
    October 15, 2021 at 4:05 pm

    When installed in two magnetic level gauge is vessel/tank. What is distance between one magnetic level gauge to another magnetic level gauge? Why?

    Reply
  • Deepak kumar says:
    November 9, 2021 at 9:12 am

    When installed into two magnetic level gauge is vessel/tank. What is distance between one magnetic level gauge to another magnetic level gauge? Why?

    Reply
  • Sanjay sheth says:
    April 6, 2024 at 10:11 am

    In addition for safety (SIS emergency shutdown). We have to design separate loops according to International Standards (IEC 61511)
    Means HH and LL will be insisted Shutdown.

    Reply

Leave a Reply Cancel reply

Your email address will not be published. Required fields are marked *

Stay Connected

128.3kFollowersLike
69.1kFollowersFollow
210kSubscribersSubscribe
38kFollowersFollow

Categories

Explore More

How to do Interface Level Calculation using DP Transmitter ?
cat5e Plenum Cable History, Advantages and Disadvantages
Why 4-20 mA Standard is so popular ?
30 Concerns for Process Control Systems Philosophy
Ultrasonic Level Switch Principle
Selection Criteria of pH Analyzers
Thermowell Installation near Critical Equipment
Pneumatic Signal Piping and Fittings

Keep Learning

Power Supply Voltage Regulator Problem

Troubleshooting a Power Supply Circuit

Readings Mismatch between Field & Control Room

Readings Mismatch between Field & Control Room ? Why

Transmitter Range and Sensor Limits

Transmitter Minimum Span, Accuracy & Turndown

Location of Pressure Taps

Design Considerations of Orifice Plate

Level-Transmitters-Animation

Level Transmitter Animation

Digital Control Valve (DCV) Calibration Procedure

Digital Control Valve (DCV) Calibration Procedure

Electromechanical_Relays Circuit

Relay Loop Back Circuit

Loop Current Step Response (LCSR) Test for RTD

Response Time Test of RTD and Thermocouple

Learn More

Sensor Trim and Output Trim in Smart Transmitter

What is Sensor Trim and Output Trim in Smart Transmitter?

Gauge Display Scale

How to Read Gauge Analog Scales

Active Electrical Filters

Active Electrical Filters Objective Questions

Laser Diode Working Principle

Laser Diode Working Principle

Distributed Control System Architecture for Profibus Field Instruments

H1 FF Physical layer

how-to-avoid-bad-grounds

How to Avoid Bad Grounds ?

State Variable Analysis and Design

State Models for Linear Continuous Time Systems

Nonlinear Control Systems

Constructing Phase-Trajectories

Menu

  • About
  • Privacy Policy
  • Copyright

Quick Links

  • Learn PLC
  • Helping Hand
  • Part Time Job

YouTube Subscribe

Follow US
All rights reserved. Reproduction in whole or in part without written permission is prohibited.
Welcome Back!

Sign in to your account

Username or Email Address
Password

Lost your password?