Inst ToolsInst ToolsInst Tools
  • Courses
  • Automation
    • PLC
    • Control System
    • Safety System
    • Communication
    • Fire & Gas System
  • Instrumentation
    • Design
    • Pressure
    • Temperature
    • Flow
    • Level
    • Vibration
    • Analyzer
    • Control Valve
    • Switch
    • Calibration
    • Erection & Commissioning
  • Interview
    • Instrumentation
    • Electrical
    • Electronics
    • Practical
  • Q&A
    • Instrumentation
    • Control System
    • Electrical
    • Electronics
    • Analog Electronics
    • Digital Electronics
    • Power Electronics
    • Microprocessor
  • Request
Search
  • Books
  • Software
  • Projects
  • Process
  • Tools
  • Basics
  • Formula
  • Power Plant
  • Root Cause Analysis
  • Electrical Basics
  • Animation
  • Standards
  • 4-20 mA Course
  • Siemens PLC Course
Reading: Calculate LRV and URV for 4-20 mA Loop-powered DP Transmitter
Share
Notification Show More
Font ResizerAa
Inst ToolsInst Tools
Font ResizerAa
  • Courses
  • Design
  • PLC
  • Interview
  • Control System
Search
  • Courses
  • Automation
    • PLC
    • Control System
    • Safety System
    • Communication
    • Fire & Gas System
  • Instrumentation
    • Design
    • Pressure
    • Temperature
    • Flow
    • Level
    • Vibration
    • Analyzer
    • Control Valve
    • Switch
    • Calibration
    • Erection & Commissioning
  • Interview
    • Instrumentation
    • Electrical
    • Electronics
    • Practical
  • Q&A
    • Instrumentation
    • Control System
    • Electrical
    • Electronics
    • Analog Electronics
    • Digital Electronics
    • Power Electronics
    • Microprocessor
  • Request
Follow US
All rights reserved. Reproduction in whole or in part without written permission is prohibited.
Inst Tools > Blog > Practical Questions > Calculate LRV and URV for 4-20 mA Loop-powered DP Transmitter

Calculate LRV and URV for 4-20 mA Loop-powered DP Transmitter

Calculate the proper LRV and URV pressures for the 4-20 mA loop-powered DP transmitter in this level measurement scenario.

Last updated: December 1, 2020 6:47 pm
Editorial Staff
Practical Questions
No Comments
Share
2 Min Read
SHARE

Calculate the proper LRV and URV pressures for the 4-20 mA loop-powered DP transmitter in this level measurement scenario:

Calculate LRV and URV

Calculate LRV and URV for 4-20 mA Loop-powered DP Transmitter

  • LRV = inches water column
  • URV = inches water column

Then, calculate the transmitter’s output given the following process levels (assuming perfect transmitter calibration):

Output = mA with the kerosene level 4 feet up from the bottom of the tank (4 feet “fillage”)

Output = mA with the kerosene level 6 feet down from the top of the tank (6 feet “ullage”)

Answer:

Note: a weight density (γ) of 51.2 lb/ft3 is assumed for kerosene.

LRV = 56.62 ”WC = 2.046 PSI

URV = 164.9 ”WC = 5.959 PSI

Output = 5.455 mA with the kerosene level 4 feet up from the bottom of the tank (4 feet “fillage”)

Output = 12.73 mA with the kerosene level 6 feet down from the top of the tank (6 feet “ullage”)

More Questions

1. Suppose the DP transmitter with the remote seal failed and had to be replaced. Unfortunately, you don’t have another DP transmitter with a remote seal in stock to replace it. Could you use a DP transmitter without a remote seal for this application? If so, would its calibration have to be different from the remote-seal transmitter?

2. Explain why this installation does not require a compensating leg.

Share your answers with us through the below comments section.

Read Next:

  • Pressure Gauge Dial
  • Level Gauge Design
  • Diaphragm Pressure Sensor
  • Pneumatic Relay Questions
  • Instrument Calibration Question

Credits: Tony R. Kuphaldt

Don't Miss Our Updates
Be the first to get exclusive content straight to your email.
We promise not to spam you. You can unsubscribe at any time.
Invalid email address
You've successfully subscribed !

Continue Reading

Level Measuring Instruments Velocities of Propagation
Programmable Logic Controller (PLC) Questions and Answers – 7
Programmable Logic Controller (PLC) Questions and Answers – 2
Transmitter Calibration Range of a Vessel Level
Process Control High Level Alarm Fault Analysis
DP Transmitter Problem
Share This Article
Facebook Whatsapp Whatsapp LinkedIn Copy Link
Share
Leave a Comment

Leave a Reply Cancel reply

Your email address will not be published. Required fields are marked *

Stay Connected

128.3kFollowersLike
69.1kFollowersFollow
210kSubscribersSubscribe
38kFollowersFollow

Categories

Explore More

Why Strain Gauge Resistance Changes as it Stretches and Shrinks?
Solenoid Valves Practical Problems
Steam Eductor Question
Question on Remote Seal with Capillary Tubing Transmitter
A Question on Steam Drum Water Level Measurement
Galileo Thermometer
Practical Process Control System Questions & Answers – 2
Simulate Different Values for Pressure Instrument Under Test

Keep Learning

Identify Problem with Oily Water Filter Instrumentation

Identify Problem with Oily Water Filter Instrumentation

Practical Control Systems Questions & Answers

Practical Process Control System Questions & Answers – 1

Diagnosing the Electric Motor Circuit

Diagnosing Electric Motor Circuit

Electronic Pressure Sensor with Bourdon Tube and LVDT

Electronic Pressure Sensor with Bourdon Tube and LVDT

Tank uses 3 Pressure Transmitters to Measure Level & Density

Tank uses 3 Pressure Transmitters to Measure Level & Density

pressure transmitter calibration setup

Why Pressure Vessel Connected to Tubing System?

Instrument Switch Status

Define Normal Status of a Process Switch ?

How Much Pressure indicated by Micromanometer

How Much Pressure Indicated by Micromanometer?

Learn More

How Buoyant Force instruments Works

How Buoyant Force instruments Works ?

Control Valves Classification

Classification of Control Valves

Electric Motor Winding Temperature Sensors

Electric Motor Winding Temperature Sensors

Hybrid Level Transmitter Principle

Hybrid Level Measurement Principle, Selection, Installation, Limitations and Calibration

Instrument Turndown Ratio

Instrument Turndown Ratio

Electron Gun of CRT

Electron Gun of Cathode Ray Tube

Siemens PLC Simulator and Plant Simulation Software

How to use Simulator in Siemens PLC?

PLC Motor Logic

Interconnection between PLC, MCC, LCP & Pumps – Video

Menu

  • About
  • Privacy Policy
  • Copyright

Quick Links

  • Learn PLC
  • Helping Hand
  • Part Time Job

YouTube Subscribe

Follow US
All rights reserved. Reproduction in whole or in part without written permission is prohibited.
Welcome Back!

Sign in to your account

Username or Email Address
Password

Lost your password?