Reading: Calculate 0%, 50%, and 100% Calibration Points for ΔP transmitter
Inst Tools > Blog > Practical Questions > Calculate 0%, 50%, and 100% Calibration Points for ΔP transmitter
Calculate 0%, 50%, and 100% calibration points for the ΔP transmitter to measure liquid level in the vessel for wet leg and dry leg.
Last updated: November 14, 2020 11:02 am
Practical Questions
3 Comments
2 Min Read
Calculate the 0%, 50%, and 100% calibration points for the ΔP transmitter to measure liquid level in this vessel, given a range of 0 to 30 feet and a specific gravity of 0.85.
Dry LegWet Leg
Note that the “low” side of the transmitter connects to the top of the vessel to compensate for vapor pressure inside the vessel. This tube (or leg) is called a “dry leg” because there is no liquid inside of it:
Dry Leg
Dry Leg
Now suppose the vessel is heated, and the liquid inside the vessel emits condensible vapors. These vapors will condense inside low-side tube leading to the ΔP transmitter which is cooler than the storage vessel, resulting in a “wet leg” instead of a “dry leg.”
In other words, the transmitter will now “see” a constant column of liquid (SG = 0.85) 30 feet high connected to its “low” process port:
Wet Leg
Wet Leg
Re-calculate the 0%, 50%, and 100% calibration points for the ΔP transmitter to measure liquid level in this vessel with a wet reference leg instead of a dry reference leg.
Answers:
  • DP Transmitter with 5 Way Manifold
  • Question on Analytical Controller
  • Loop Powered Pressure Transmitter
  • PLC Practice Questions
  • Questions on Chemical Reactor P & ID
Credits: Tony R. Kuphaldt
Programmable Logic Controller (PLC) Questions and Answers – 8
Three-valve Manifold on Remote Seal DP Transmitter
Solenoid Valves Questions & Answers – 1
Air Pressure Inside the Tank
Programmable Logic Controller (PLC) Questions and Answers – 3
Problem on Tachogenerator
3 Comments
  • mubin says:
    November 16, 2020 at 6:18 am
    why u put the answer use 50mA?
    • shah says:
      November 16, 2020 at 9:44 am
      As per the image, I think it is assumed 10 to 50 mA as output current range of DP transmitter.
  • chin weng fong says:
    November 22, 2020 at 5:59 pm
    how to install calibration range and full range and check distance
How a Bourdon Tube Pressure Gauge might be Adjusted for Linearity?
Programmable Logic Controller (PLC) Questions and Answers – 7
Displacer Level Transmitter Question & Answer
Differential Pressure Measurement across Baghouse
Practical Process Control System Questions & Answers – 6
Differential Capacitance Pressure Sensor Circuit
Displacer Level Transmitter 5-point Calibration
Oil and Air Pressure Actuated Lifts Questions
Strain Gauge Bridge Circuit
Something is Wrong with Strain Gauge Bridge Circuit
pH Monitoring System Triggers an Alarm
Heat Exchanger Differential Pressure Transmitter
Smart DP transmitter Formula
DP Transmitter Error Calculations
simple motor start-stop circuit
Liquid Level Switch Control Logic
reactor vessel
surface-mounted water pump
Surface-mounted Water Pump
simulate a thermocouple
Calculate the appropriate millivoltage values of a Thermocouple
Alarms to Annunciator
Basics of Alarms and Trips
Self Balancing Bridges Objective Questions
Bridge Circuits Objective Questions
PLC Latching circuit Animation
What is Seal-in Circuit ?
Circuit Control Devices Multiple Choice Questions
Circuit Control Devices Multiple Choice Questions & Answers
Substation Safety Clearances
Induction Motors Faults and Protection
Calculate Temperature of Four Wire RTD
Calculate the Temperature of 4 Wire RTD
Hydrostatic interface level measurement Formula
Hydrostatic Interface Level Measurement